Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Home Alone with Home Assistant (previously A Beginner's Guide to ASHP Monitoring)

143 Posts
16 Users
53 Reactions
32.1 K Views
Majordennisbloodnok
(@majordennisbloodnok)
Famed Member Moderator
Joined: 5 years ago
Posts: 1992
 

That's excellent news, @bontwoody.

So now it's worth a quick recap to ensure I understand correctly about what you can and cannot do within Home Assistant.

  • You can see the state of charge of your battery and actively tell it to charge from grid, discharge to grid or revert to being charged from solar.
  • You can see the current, previous and next Octopus unit prices for both import and export.
  • You can see what your EV and connected wall box are doing.
  • You can see the weather and solar forecast.
  • You can see the outside temperature, internal room temperature and generally what your heat pump is doing.

 

Is that correct?


105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs

"Semper in excretia; sumus solum profundum variat"


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1054
 

@majordennisbloodnok Not quite, I havent done anything with the EV and charger yet.

I got the script to work using the actions tab in the developer tools, I need to cement my understanding now on how to include that in an automation or yaml file. Still, its a positive move forward 🙂


House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
Majordennisbloodnok
(@majordennisbloodnok)
Famed Member Moderator
Joined: 5 years ago
Posts: 1992
 

Absolutely agree, @bontwoody. Well worth continuing with a bit of experimenting to get familiar with the control you now have.

That said, it's now also worth making a more detailed list of things you want to achieve. By "detailed", I also mean including enough explanation to deal with any gotchas you can see.

For instance, one gotcha with the EV charging is that it will be regarded by the inverter as load just the same as the fridge or heat pump. However, you don't want to be charging one battery (your car) from another battery (your Luna), so it's well worth putting in place an automation or two to deal with that. For me, that means one automation to say "if the EV is charging, set the home battery's minimum SOC to 90%" and another saying "if the EV is not charging, set the home battery's minimum SOC to 10%".

As a result, you can come up with a list of IFTTT (If this then that) statements that describe what you want to put in place. It helps a lot in knowing how to structure your automations. I can happily share what I have, although you'd have to remember I am on Octopus Agile so they might not be entirely suitable for you.


105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs

"Semper in excretia; sumus solum profundum variat"


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1054
 

@majordennisbloodnok Absolutely, I already know that I have an issue with EV charging outside of the IOG window that drains my home battery. FYI im a reasonable programer used to python and vb its just getting used to HA that takes a bit of time. 🙂


House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
Majordennisbloodnok
(@majordennisbloodnok)
Famed Member Moderator
Joined: 5 years ago
Posts: 1992
 

My apologies, @bontwoody. Completely misread your familiarity.

In that case, I suspect you've quite enough already to be able to fill in the gaps easily. Happy for you to shout if you need anything more, and in that case I won't go quite so basic in the explanation.


105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs

"Semper in excretia; sumus solum profundum variat"


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1054
 

@majordennisbloodnok No problem. I was glad of the help :-). Will just try and get my head around the syntax


House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1054
 

@majordennisbloodnok

Just an update, all going well and have managed to stop battery discharging into EV I think. Will know for sure next time I need to charge in the day 🙂 Thanks again.


House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
Majordennisbloodnok
(@majordennisbloodnok)
Famed Member Moderator
Joined: 5 years ago
Posts: 1992
 

Great news, @bontwoody.


105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs

"Semper in excretia; sumus solum profundum variat"


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1054
 

@majordennisbloodnok Ive been thinking, and Im wondering if I have been a bit too simplististic. My automation below, just detects when the EV is charging and sets the home battery to forcible charge if the SOC is less than 95%

 

image

I think this should work fine during night hours on IOG and if the battery is already charged, then it will have no effect, and if it isnt then it will charge the battery at cheap rate along with the EV. When the EV stops charging I have another automation that cancels the forced charge.

I then got to thinking, what would happen when IOG charges outside of the cheap rate window, presumably if the battery is below 95% then it will start charging along with the EV but still at cheap rate. So far so good.

But then I thought what will happen, if I plug the EV in during the day and it starts charging because I have surplus solar for example?, Now the battery could start charging when it isnt at cheap rate. But will it actually draw from the grid or just attempt to share the solar surplus?

Could this situation be prevented by changing the default mode of the Zappi so that it doesnt use excess solar? Or should I add another condition that detects when I am exporting solar? How do you handle it? Cheers in advance 🙂

 


This post was modified 2 weeks ago by bontwoody

House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
Majordennisbloodnok
(@majordennisbloodnok)
Famed Member Moderator
Joined: 5 years ago
Posts: 1992
 

@bontwoody, I think we may be missing a bit of info on your battery here. My Growatt inverter has a setting that it calls "Load First Battery Minimum SoC", and that specified the minimum state of charge the inverter should let the battery get to if it is in the mode for servicing load first. I'm sure there will be a similar kind of setting on your inverter even if I'm also sure it'll be called something else.

The way my automation works is that if my wall box changes status to "Charging", I set that minimum SoC to 90%. That doesn't mean the inverter will suddenly start charging the battery but it ensures that if the battery is at anything less than that the charge in the battery will not be used to charge the car. I also, of course, have another automation to say that if the wall box status changes from "charging" (i.e. the car isn't charging any more), I reset that minimum SoC back to 10%.

One of the features of the Zappi, as you know, is that it has an Eco+ setting, meaning it will never try pulling from the grid. If the inverter can supply 1.5kW or more, the car will charge using all available non-grid leccy, but if it drops below 1.5kW then charging will be paused. The reason I set the home battery's minimum to 90% is that on cloudier days it is possible for bouts of great solar to be interspersed with less than 1.5kW periods. By having that last 10% in the battery potentially available, it has the effect that my home battery will fill first in the morning, export to grid will then ramp up to more than 2kW, at which my car (if it's connected and not at its target charge level) will start charging. If the sun goes in, that Eco+ charging will still continue with some coming from solar and some topping up from battery until either the sun comes out again or the battery depletes to 90%. If the sun comes out again, the inverter will split charge between battery and zappi, so my buffer is regained. In effect, it stops the zappi stopping and starting when there's a bit of cloud.

Back to your situation, I can see in the documentation for your Huawei_solar integration that there are a number of configuration entities listed, but the names are foreshortened so not entirely readable. One of those, I suspect, will be the setting you want to play with.


105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs

"Semper in excretia; sumus solum profundum variat"


   
ReplyQuote
Majordennisbloodnok
(@majordennisbloodnok)
Famed Member Moderator
Joined: 5 years ago
Posts: 1992
 

I should also add that I have several automations for various scenarios, as listed in the screenshot below.

zappi automations

The big fly in the ointment for me, which doesn't affect you, is the idiotic and facile change by Volkswagen to their API to stop customers from being able to use the API for personal use. As a result, the VW Connect integration doesn't work and so my ability to see whether the car is at its target charge level or not is now non-existent. As a result, if we see negative pricing then we're setting the car to charge at a preset time (once again through HA using a date/time helper, but it's still more manual than it needs to be).


105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs

"Semper in excretia; sumus solum profundum variat"


   
ReplyQuote