Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @jamespaViessman pre-heat a specific defrost
Grant have much to same and can even be placed outside, next to the HP.
Yes when defrosting the heat has to come from some where and by changing to the 3 port buffer it will still come from the house loop and need to be replace. So it will still work the same as your open loop.
Its the anti-freeze cycle that just keeps water flowing through the heat pump for 12hrs when it's below 4c, that will draw heat from the house with no buffer. And as the CH pumps are off at this time it confines the water flow to just the buffer.
When the HP starts up and flow temp goes up it will not worry about what's in the 3 port buffer and if the flow is still greater from the HP, it will heat up the buffer and help reduce the defrost
Posted by: @heacolI don't believe the installation of a buffer tank, complies with the building regulations.
Nice one!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaJust thinking about this measuring the temperatures on all 4 ports
That's how we start, 4 temps on the 4 ports. It showed we had a imbalance of 5° across the top, which I wanted to reduce having looked at the various videos on the subject.
And YES it is hard adjusting everything, leaving it 24 hrs and rechecking. If I had installed flow meters both side it might have been quick.
Learnt a great deal about my system doing this and quite happy to spend £200 this summer to put 4 valves, 2 flow meters and bypass pipes in, so once again I can check various combinations to see which works for us.
PS I've also learned/worked out that it could be automated just on temp and having automatic adjusted flow meters, but that's starting to get beyond me so no longer looking at it
Posted by: @heacolI don't believe the installation of a buffer tank, complies with the building regulations.
Wow! 😮
I think this needs raising with Citizens' Advice.
They hold the remit for operating the Consumer Rights Act (2015).
I suspect they have a heat-pump specialist to advise the separate offices.
They must have centralised policies on which cases can go to arbitration.
I already know they have a representative who specialises in Smart Meters, for example.
@editor - the ball's just bounced into your side of court
Save energy... recycle electrons!
Posted by: @uk_pete_2000Its the anti-freeze cycle that just keeps water flowing through the heat pump for 12hrs when it's below 4c, that will draw heat from the house with no buffer. And as the CH pumps are off at this time it confines the water flow to just the buffer.
OK thats definitely a different problem.
The buffer will presumably cool down fairly quickly in relation to 12 hrs and at that point I imagine that the heat pump might switch itself on to heat, in order to protect itself. This being the case would it be any worse simply having a pressure operated bypass valve?
That said, when its 4C outside could you reasonably operate 24*7, or is your heat pump so oversized that this isnt possible/cost effective.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @transparentPosted by: @heacolI don't believe the installation of a buffer tank, complies with the building regulations.
Wow! 😮
I think this needs raising with Citizens' Advice.
They hold the remit for operating the Consumer Rights Act (2015).I suspect they have a heat-pump specialist to advise the separate offices.
They must have centralised policies on which cases can go to arbitration.
I already know they have a representative who specialises in Smart Meters, for example.@editor - the ball's just bounced into your side of court
Well this is an interesting line of thought and I wonder where MCS would sit (on the fence? as far away as possible?)
If manufacturer insists on a buffer tank I cant see a case based on building regs succeeding (the word 'reasonable' applies), but if they don't (or strictly didn't at the time of installation ) then there is a good argument. In that situation the case would be against the installer.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
The heat pump only turns on when we request heat. Never really tested what happens if we leave if off for 24hrs and its below 4°. I think even our house would have lost so much heat that it would take 24hrs to get back up.
Posted by: @jamespaThat said, when its 4C outside could you reasonably operate 24*7,
It's not that it can not work 24hrs, I did it for a couple of days at the start of Jan and it worked fine.
The problems are, we need minus figures to keep it working 24/7
It's the fact it will not go below 23° flow temp and still heat the house up when it's freezing outside.
At preset I just leave it at 27° flow temp. Then on a average day I run it 6hrs, much colder nights I run it for 8hrs a day and if we get very cold days/nights I'll run it 12hrs a day.
And YES it's oversize due to MCS calculations at the time. But it will cost too much to replace it, so I work with it.
Posted by: @uk_pete_2000The heat pump only turns on when we request heat. Never really tested what happens if we leave if off for 24hrs and its below 4°. I think even our house would have lost so much heat that it would take 24hrs to get back up.
Posted by: @jamespaThat said, when its 4C outside could you reasonably operate 24*7,
It's not that it can not work 24hrs, I did it for a couple of days at the start of Jan and it worked fine.
The problems are, we need minus figures to keep it working 24/7
It's the fact it will not go below 23° flow temp and still heat the house up when it's freezing outside.
At preset I just leave it at 27° flow temp. Then on a average day I run it 6hrs, much colder nights I run it for 8hrs a day and if we get very cold days/nights I'll run it 12hrs a day.
And YES it's oversize due to MCS calculations at the time. But it will cost too much to replace it, so I work with it.
All fair enough. I dont think I can really add much more beyond what I've already said. if somehow you need to accommodate it switching itself on at 4C, but not heating, then a byass or buffer is the only way. I would be concerned that, at - temperatures, the water would still cool below freezing if left off for 12 hours but recirculating through the unit (unless the HP also switches to heat, which I imagine it might), I guess that where anitfreeze valves or glycol come in.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@iraknic, as promised, the episode is out. Well worth watching IMO. Your case is around the 23 minute mark.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
In the coming weeks, I’ll be scheduling another session on buffer tanks, where viewers can submit videos and images for our panel to assess and provide advice.
If you’d like to take part, please send us a question about your system and submit high-resolution photos and videos via WeTransfer.com to editor@renewableheatinghub.co.uk.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@iraknic out of curiosity how did you check your delta T. Was it just purely from your control panel?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 597 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
@david999 ... just water, David, or do you add anything...
By colinc , 16 minutes ago
-
RE: Our 10 year old Grant heat pump failed
Since my last post on this topic we've reached a conclu...
By Mike Patrick , 54 minutes ago
-
Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
My installation is 4 years old. After about 18 months a...
By seoras , 3 hours ago
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 12 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 12 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 16 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 16 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 17 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 18 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 20 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 20 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago