Thanks Craig, now lower the LWT setting to 30C and see what happens to how the system operates.
Right, finished timing. Now back to 8 mins on 20 seconds off again.
Flow temp 28.1 set to 30
Indoor 22.1Â
Outdoor 6.5
Room temp 19
Posted by: @craig1980Right, finished timing. Now back to 8 mins on 20 seconds off again.
Flow temp 28.1 set to 30
Indoor 22.1Â
Outdoor 6.5
Room temp 19
Hi Craig,
I'm afraid that I have run out of suggestions.
There appears to be something fundamentally wrong with your heat pump, and/or how the system has been installed. The only thing that I can see that appears to be incorrect is the Teva_out temperature reading of -50C, which could possibly be due to a faulty or disconnected temperature sensor.
I would suggest that you e-mail Samsung Technical Help and ask them why your system may be operating as it is doing.
In the meantime set your system back onto WC mode and adjust for the required indoor temperature.
Â
Okay, many thanks for all of your help. I'll update if I find anything from Samsung. Thanks again. Much appreciated.Â
Interestingly, when I put the settings back to WC I get error E121. Upon looking this up in the manual it saysÂ
"Short-or open- circuit error of the room temperature sensor of the zone 1 indoor unit (detected only when the room thermostat is used) Error source - Hydro unit.Â
Posted by: @hughfPosted by: @mike-hAm I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
It doesn't have a buffer, no...
Which set of instructions say that the samsung needs a buffer?
Â
@hughf Please see the topic about Samsung install and buffer tank
https://renewableheatinghub.co.uk/forums/postid/11342
Freedom Heat Pumps claims a buffer tank is required to be within the Samsung warranty, even though the manual implies otherwise and Joule make a pre-plumbed cylinder without a buffer tank.
Â
@mike-h Ah yes, good old freedom. I’d trust the instructions from midsummer wholesale personally. I know that GH was always getting 911 errors (low flow) on his early installs, so they probably mandated a buffer to deal with that issue, allowing the primary pump to run at full speed to charge the buffer.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 25 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
So now I have completed my heat loss calculations and I...
By pash44pump , 10 minutes ago
-
RE: Boiling Mad: Exposing Radiatorgate
Actually they do. My case is a prime example. Catalo...
By DREI , 8 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
Blunt answer? The 20-year-old gas system was f...
By DREI , 9 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
You can even go as low as 40c flow temp, if you want a ...
By DREI , 9 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 9 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
1040kw Even beat June and July. Great month.
By Andris , 11 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 11 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 14 hours ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 15 hours ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 21 hours ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 21 hours ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 1 day ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 1 day ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 2 days ago
-
What is the Heat Geek Guarantee?
We regularly hear from homeowners who are researching i...
By Mars , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk, interesting point. I’ve not focused much on Hea...
By Mars , 2 days ago
-
Intelligent Octopus Flux (IOF) Review
I promised @toodles that I would provide an update and ...
By Old_Scientist , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I am pleased to see the change. We definitely need t...
By Jeff , 3 days ago