Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
That's all good news @eliuccio
... and extra thanks for posting here the photo of the trips with blue levers on the side of the Growatt ARK Battery Control Unit.
I'm pleased to note that the Cahill engineer has taken the trouble to actually explain a number of points,
rather than just switching the battery back on. 😀
His observation that the battery system is "isolated" matches what I had expected.
The word isolated can mean two different things in this situation.
What he (and I) mean here is that the battery 52v cabling is 'floating' and not tied to earth or anything else.
That's how it should be...
... and that's why my own batteries don't have the connections covered.
I can't get an electric shock by touching them, and nor can you.
I can think of two possible reasons why the battery trips went off.
The one which is most relevant is that there might've been a lightning strike nearby (within a couple of miles).
Sometimes trips pick up the passing spike and switch off.
No harm done.
Good news with having the RCBO changed for a bi-directional one.
That provides confidence that the safety protection will actually work if it needs to!
Whatever UKPN say about the Service Fuse upgrade from 60A, please let us know.
If they insist on a move to 3-phase, please don't be daunted.
We can help to explain what's involved both during and after that upgrade.
It would mean you'd have your Smart Meter changed too.
That's fine.
I'm a Smart Meter specialist and I can answer whatever you'd like to know.
An upgrade to 3-phase under these circumstances shouldn't require you to pay anything.
You will, however, be asked to divide the household circuits across more than one phase.
We have photos of your consumer units here, and I already have an idea how to achieve what's required at minimal cost for the electrician's time.
Let's wait and see what UKPN say first.
Save energy... recycle electrons!
@transparent there is big difference in LV vs HV for DC circuits compared AC.
A 9v PP3 battery will kill you if you are daft enough to put your tongue on it.
There are cases where children have swallowed button cells and not survived, they are 3.3V
Posted by: @agentgeorge...
There are cases where children have swallowed button cells and not survived
...
The same has been claimed of my sister-in-law's cooking, although in fairness that's more a case of salt and buttery.
OK, taxi's ordered.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@majordennisbloodnok Straight to the cells with you!
Toodles, heats his home with cold draughts and cooks food with magnets.
@agentgeorge if you'd like to start a new topic on the dangers of AC/DC electricity, please do so.
Tag me there and I'll contribute.
It is an important issue, and relevant for this forum.
But I don't think other readers will find it here on p.4 of a topic which is about a particular Home Battery Storage problem.
PS... and I do test PP3 batteries by touching them to my tongue! 😲
Save energy... recycle electrons!
@transparent Who needs a test meter?!😉
Toodles, heats his home with cold draughts and cooks food with magnets.
Need to put a warming on this thread incase anyone is following it… If it’s a discharged pp3 you'll get a tizzy tongue, don't try it with a fresh one.
It is all getting ticklish...
And phased with all of this. Anyone seeding for a any solar farm anywhere? 😀
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
@agentgeorge That’s a ittle too inscrotumable for me… Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles As we have had the topic issue resolved, we can edge off track a bit, and do a bit of testiculating; that’s wandering around a solar farm, waving ones hands in the air and talking bollox
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 330 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge I'll give it a go with my Apple Watch late...
By HarrisonC , 56 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 4 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 16 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 18 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 18 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 21 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 3 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago