Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Battery Storage Wiring Gauge Question
I'm looking to get an Seplos Mason 280/LF304 battery bundle (15kwh) and I want to place it in a little outhouse attached to the side of the main house - mainly for fire prevention reasons but it's also damned heavy! The Solis inverter is in the loft...
What is the maximum length of cable I can run between the two please? I'll obviously get the correct gauge but can't get my head around what that gauge needs to be.
Posted by: @puffWhat is the maximum length of cable I can run between the two please?
As long as you like, you have to watch overall voltage drop on the DC side less than the AC. (Assume you are running in DC). I am running PV cables 40m in DC no issue, in AC it would have been quite costly and I may have had voltage drop issues.
Posted by: @puffI'm looking to get an Seplos Mason 280/LF304 battery bundle (15kwh) and I want to place it in a little outhouse attached to the side of the main house - mainly for fire prevention reasons but it's also damned heavy! The Solis inverter is in the loft...
What is the maximum length of cable I can run between the two please? I'll obviously get the correct gauge but can't get my head around what that gauge needs to be.
As far as the gauge or thickness of the cable is concerned, this will depend upon the maximum quantity of power to be moved and the voltage.
If you wish to supply 3kW of power at 240 Volts AC, then the maximum current would be 3000/240 = 12.5 Amps.
To move the same 3kW at 50 Volts DC would require a current flow of 3000/50 = 60 Amps.
If you look at the current carrying capacity of different sized cable you should find the one that would meet the task.
Posted by: @derek-mAs far as the gauge or thickness of the cable is concerned, this will depend upon the maximum quantity of power to be moved and the voltage.
If you wish to supply 3kW of power at 240 Volts AC, then the maximum current would be 3000/240 = 12.5 Amps.
To move the same 3kW at 50 Volts DC would require a current flow of 3000/50 = 60 Amps.
If you look at the current carrying capacity of different sized cable you should find the one that would meet the task.
It's a Solis 3.6kw hybrid inverter, so has a nominal 5kw max output at 48/50 vDC, which from the above would imply 100 Amps/thereabouts.
I need about 8m of length so a 1AWG or 0 AWG to be on the safe side?
25mm² cable would give 2.56% (1.23 volts) drop based on 48V, 100A and 8m.
35mm² 1.87% (0.896 volts) drop
Doesn't look like you need (50mm²)
Posted by: @puff1AWG or 0 AWG to be on the safe side?
Check your manual for max volt drop.
- 27 Forums
- 2,772 Topics
- 65.3 K Posts
- 1,702 Online
- 7,174 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
The positive reviews keep coming in for Britain's Heat ...
By Mars , 2 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
I have one of these fitted which also allows you to reg...
By Old_Scientist , 5 hours ago
-
RE: Recommendations in Ely (Cambs) area for Full setup checks on Nibe HP setup for House.
If they can't don't give up. Heat pumps are, in reali...
By JamesPa , 1 day ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
@ian-s I wouldn't be too concerned about the design ...
By Rob of York , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes that's what would happen by turning down the lsv to...
By JamesPa , 1 day ago
-
RE: Grant R290 DHW Cycle Interuption
It looks like some sort of short pre-run. The question...
By JamesPa , 1 day ago
-
RE: Cascade System or larger single unit
@renewables345 I would say if it a new build it’s no mo...
By Aventus Eco , 1 day ago
-
RE: Why are ASHP installs so expensive?
Posted by: @batpred There´s another aspect that coul...
By Rob of York , 2 days ago
-
RE: Say hello and introduce yourself
@gz00, welcome to the forums. There’s a huge amount of ...
By Mars , 2 days ago
-
RE: Home energy storage & battery register
1 fox ess lv5200 batteries, plus 2 more waiting to be i...
By Jimcub , 2 days ago
-
RE: Heat Pump deployment statistics: June 2026
@l8again Unfortunately the government is, I suspect,...
By JamesPa , 2 days ago
-
My feed of random industrial auctions turned up this au...
By Prunus , 2 days ago
-
We’ve just passed 20 million forum views! 🎉
It's official. The Renewable Heating Hub forums have of...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@batpred When the raw material input has increased in c...
By Papahuhu , 5 days ago