Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Battery Storage Wiring Gauge Question
I'm looking to get an Seplos Mason 280/LF304 battery bundle (15kwh) and I want to place it in a little outhouse attached to the side of the main house - mainly for fire prevention reasons but it's also damned heavy! The Solis inverter is in the loft...
What is the maximum length of cable I can run between the two please? I'll obviously get the correct gauge but can't get my head around what that gauge needs to be.
Posted by: @puffWhat is the maximum length of cable I can run between the two please?
As long as you like, you have to watch overall voltage drop on the DC side less than the AC. (Assume you are running in DC). I am running PV cables 40m in DC no issue, in AC it would have been quite costly and I may have had voltage drop issues.
Posted by: @puffI'm looking to get an Seplos Mason 280/LF304 battery bundle (15kwh) and I want to place it in a little outhouse attached to the side of the main house - mainly for fire prevention reasons but it's also damned heavy! The Solis inverter is in the loft...
What is the maximum length of cable I can run between the two please? I'll obviously get the correct gauge but can't get my head around what that gauge needs to be.
As far as the gauge or thickness of the cable is concerned, this will depend upon the maximum quantity of power to be moved and the voltage.
If you wish to supply 3kW of power at 240 Volts AC, then the maximum current would be 3000/240 = 12.5 Amps.
To move the same 3kW at 50 Volts DC would require a current flow of 3000/50 = 60 Amps.
If you look at the current carrying capacity of different sized cable you should find the one that would meet the task.
Posted by: @derek-mAs far as the gauge or thickness of the cable is concerned, this will depend upon the maximum quantity of power to be moved and the voltage.
If you wish to supply 3kW of power at 240 Volts AC, then the maximum current would be 3000/240 = 12.5 Amps.
To move the same 3kW at 50 Volts DC would require a current flow of 3000/50 = 60 Amps.
If you look at the current carrying capacity of different sized cable you should find the one that would meet the task.
It's a Solis 3.6kw hybrid inverter, so has a nominal 5kw max output at 48/50 vDC, which from the above would imply 100 Amps/thereabouts.
I need about 8m of length so a 1AWG or 0 AWG to be on the safe side?
25mm² cable would give 2.56% (1.23 volts) drop based on 48V, 100A and 8m.
35mm² 1.87% (0.896 volts) drop
Doesn't look like you need (50mm²)
Posted by: @puff1AWG or 0 AWG to be on the safe side?
Check your manual for max volt drop.
- 27 Forums
- 2,741 Topics
- 64.3 K Posts
- 1,784 Online
- 7,144 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
@majordennisbloodnok - thanks so much. That has been...
By CalumM , 4 hours ago
-
We have large radiators as our emitters. Room temp is 2...
By Old_Scientist , 6 hours ago
-
RE: Electricity price predictions
2. As EV ownershp increases it'll certainly increase de...
By EtchedPixels , 6 hours ago
-
I meant to say I cannot register my kit at Energyplus… ...
By Batpred , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
@indevolt-tech When you say 'dedicated switched fused ...
By JamesPa , 11 hours ago
-
RE: PV and battery long payback - sense check query
So if it helps I was recently quoted about 8 grand for ...
By EtchedPixels , 1 day ago
-
RE: HomeTherma Is Live: A New Home-Energy Platform Built Around the Homeowner
Signed up!
By bobflux , 2 days ago
-
RE: Has anyone seen this problem before? Huge anticycling times
Oh dear. Glad it was replaced. I have been mighty imp...
By JamesPa , 3 days ago
-
RE: Can I start an argument about buffer tanks please? 🙂
Dont, just adjust the LSVs to get different temperature...
By JamesPa , 3 days ago
-
RE: Heat pump running costs – what has actually worked for you?
I installed the air source heat pump in January 2026, i...
By bobflux , 3 days ago
-
RE: Grant Aerona Air to Water R290 6.5 kW - Quiet Mark and Silent Running
Thats all interesting. DHW on my Vailant seems to respe...
By JamesPa , 4 days ago
Members Online
No online members at the moment