Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Battle of the charging technologies
As I commented on another thread (posted by @editor), we're looking into V2X; we're certainly interested in getting an electric car and V2X makes sense if it can effectively allow us to increase our solar PV storage capacity at the same time.
However, I'm aware now that CHAdeMo charging is essential to V2X being the only bidirectional charging technology readily available, but that it's losing out significantly to CCS in terms of installed public charging infrastructure. Has anyone any ideas:
- if there are any hints that CHAdeMo popularity may rise again or
- if there are an other bidirectional charging technologies that might be able to take CHAdeMo's place?
Any thoughts much appreciated.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Any of the VW ID range of 77kw or above is compatible after a software upgrade. No other change will be needed to the car according to VW. A compatible charger will be needed. Not sure what is the latest on timing in the UK.Â
Hi
Here is a little something for all the battery lovers to salivate over. 😎Â
Â
I'm horrible with cars, and even worse with EVs. Does Tesla have its own proprietary charging standard and is their tech bidirectional?Â
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @editorI'm horrible with cars, and even worse with EVs. Does Tesla have its own proprietary charging standard and is their tech bidirectional?Â
They haven't been supportive of v2g, but not to say they won't in the future. So not bidirectional currently.Â
They have their own chargers but also cables for some other chargers
https://www.tesla.com/en_GB/support/charging-connectors
Posted by: @jeffAny of the VW ID range of 77kw or above is compatible after a software upgrade. No other change will be needed to the car according to VW. A compatible charger will be needed. Not sure what is the latest on timing in the UK.Â
Thanks, @jeff. So does this mean the CCS connection in and of itself is capable of bidirectionality, and that it's only the car and charger that need to be told how to behave? I'm struggling somewhat with understanding the detail of where the CHAdeMo and CCS standards begin and the supporting hardware ends, and therefore what V2X compatibility really entails.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokPosted by: @jeffAny of the VW ID range of 77kw or above is compatible after a software upgrade. No other change will be needed to the car according to VW. A compatible charger will be needed. Not sure what is the latest on timing in the UK.Â
Thanks, @jeff. So does this mean the CCS connection in and of itself is capable of bidirectionality, and that it's only the car and charger that need to be told how to behave? I'm struggling somewhat with understanding the detail of where the CHAdeMo and CCS standards begin and the supporting hardware ends, and therefore what V2X compatibility really entails.
A good question.Â
I can't say i have read up much on the actual standards. There are standards around bi directional charging. For ccs for example, this might be a useful starter to read.Â
https://www.emobility-engineering.com/vehicle-to-grid-charging
ISO 15118 is the CCS V2G standards.Â
It is not clear to me if CHAdeMo has a long term future, but i am no expert.Â
In the case of VW, they say you will need a special "DC BiDi wallbox" charger. Not clear who will be supplying the wallbox or how much it will be, but i bet it won't be cheap. I would hope the charger isn't tied to only VW but don't know.Â
There will be an over the air software upgrade to the actual car (assuming the software hasn't already been upgraded in recently delivered models).
At least buying a VW ID you would know there is an upgrade path to V2G if that is important. Of course it assumes they don't change their minds, the charger isn't prohibitively expensive and their are reasonable electricity tariffs on the market.Â
I don't know if there are any trials going on at the moment with VW, i have only seen the Nissan Leaf trials which have had mixed reviews with V2G. There are some V2H Nissan Leaf trails following on.Â
I don't think there are any public V2G or V2H tarrifs or setups in the UK yet, only trials.Â
I think @Transparent has a VW ID, i expect he is a lot more knowledgeable.
It is early days, but i would hope the market moves quickly over the next few years.Â
Thanks, @jeff. A good deal to add to the reading-up I've already done, and that's a good thing.
It's also timely since we are looking seriously at the ID3 or its reclothed Cupra equivalent, so it's great to know that the VW stable is at least thinking of complying with the bigger picture. No guarantees, but better than no commitment at all.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Thanks @Jeff and yes I do have a VW ID3. But earlier you wrote:
Posted by: @jeffAny of the VW ID range of 77kw or above is compatible after a software upgrade.
My ID3 predates that capability. Perhaps I need to trade-up because I like the idea of V2G - if it's implemented correctly.
When I investigated VW's strategy at the end of 2021 it was clear that they were developing their own software system to control distributed storage. Ie theirs is a rival to the generic grid-connected storage control architectures being developed by Kaluza (OVO) and Octopus.
I think that approach is fundamentally flawed. Any house needs to have all its smart grid-connected devices controlled by a single universal control algorithm. Without that you can have electric storage radiators or storage batteries being switched on in response to a signal from a Time-of-Use tariff contract. Yet simultaneously, VW could then tell your ID3/ID4 to 'export to the grid'.
Consequently instead of earning grid-support income via VW's scheme, you're simply moving stored energy between devices which you already own.
Save energy... recycle electrons!
Posted by: @transparentThanks @Jeff and yes I do have a VW ID3. But earlier you wrote:
Posted by: @jeffAny of the VW ID range of 77kw or above is compatible after a software upgrade.
My ID3 predates that capability. Perhaps I need to trade-up because I like the idea of V2G - if it's implemented correctly.
When I investigated VW's strategy at the end of 2021 it was clear that they were developing their own software system to control distributed storage. Ie theirs is a rival to the generic grid-connected storage control architectures being developed by Kaluza (OVO) and Octopus.
I think that approach is fundamentally flawed. Any house needs to have all its smart grid-connected devices controlled by a single universal control algorithm. Without that you can have electric storage radiators or storage batteries being switched on in response to a signal from a Time-of-Use tariff contract. Yet simultaneously, VW could then tell your ID3/ID4 to 'export to the grid'.
Consequently instead of earning grid-support income via VW's scheme, you're simply moving stored energy between devices which you already own.
Yep, getting everything to work in harmony is a big challenge i agree.Â
As well as ISO 15118 for the bi direction ccs charging, I see VW are going to implement EEBUS
Have you come across EEBUS? How does this fit in with things like Kaluza?
We have a V2G wallbox, for our leaf, on a trial with Ovo.  So far as I’m aware, there are just a few small scale trial V2G to date similar to ours, using external AC to DC chargers, which are generally expensive (£5k +), and so a barrier to mass adoption.  Also, the cable carrying DC battery forces extra safety measures to be in place (locked connectors), which gives high static loss.
What would make a huge difference to adoption would be an update to the J1772 (granny cable) spec. Â That spec at present allows an external EVSE to turn on and off the car charger, and set the current the car charger may draw. Â I expect it could also have a reverse power mode - clearly to work this requires the car charger to be bidirectional. Â The EVSE is often called a charger, but it has no power conversion inside, it is actually a control box; using this plug, AC mains connects via a contactor directly to the car. Â Unlike a uk mains plug, the J1772 has no exposed pins on plug or socket, so power could be transferred either way.
Tesla are I think considering this - newer cars from them have bidirectional hardware built in, they choose not to use it (yet?). They have a proprietory plug, very similar to J1772.
Thanks for those insights @robl Before I read the above about your participation in the OVO/Kaluza V2G Trial, I'd just posted an overview of it in response to the related points you made in the topic on Sharing Battery Costs. Have a read of that there if you want.
Save energy... recycle electrons!
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 307 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
What material was the pipe made from?Was it a metal or ...
By Transparent , 37 seconds ago
-
RE: Vaillant arotherm plus heat pump frost protection
The thing labelled flow sensor is the heat exchanger, t...
By JamesPa , 24 minutes ago
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
Difficult to comment further without being there. If...
By JamesPa , 1 hour ago
-
@andrewj A ‘DIY’ job suggests you may clean up quite we...
By Toodles , 4 hours ago
-
RE: Our 10 year old Grant heat pump failed
Back in the 70’s and through the eighties, one of my re...
By Toodles , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
@indevolt-uk Keen to know more about the pricing and wh...
By ChandyKris , 7 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 20 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 24 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 1 day ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 1 day ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 1 day ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 1 day ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 1 day ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago