Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Debugging my legionella immersion heater
My legionella cycle has never worked, and I'm trying to work out why
I have a Grant Aerona3 13kW and I've wired it so the ASHP controls the legionella cycle (disconnecting the spurious Grant timer box they install). The way this works is the ASHP runs up the hot water to the maximum temperature it can manage, then hands over to the immersion heater for the last few degrees to get it to 60C. On the standard setup it has 2 hours to do that - there's a service manual parameter to extend it to 3 hours, which I've done. After 3 hours the water is only at 50C and the ASHP flashes 'LC' meaning legionella cycle failed. Next week comes around and it does legionella again and the same happens... every week.
To cut a long story short of pondering various control system things (eg what if the pump is running during the immersion cycle, won't that be using the DHW coil to cool the cylinder?), I turned off the ASHP completely and just manually powered the immersion (it goes via a contactor which I can enable independently). I have a power meter on it so I can see the current. And this is what I see:
It seems the hot water temperature is plateauing at 52C. I confirmed this with two thermometers in the drawn water. I could also see that the current had dropped away, ie the immersion had cut out even though the contactor was still enabled. I took off the back of the immersion (Thermowatt 340160900000 aka 3401609) and I saw this:
A bit hard to see but the dial was about 90% of the way anticlockwise towards the + symbol. I turned it anticlockwise all the way:
then restarted the immersion and I got:
so 57C is the max it will go. According to some calculations, 3kW (confirmed on the meter) into a 200 litre cylinder should cause a rise of 12.9degC per hour, or roughly a degree per 5 minutes. The immersion is at the bottom of the cylinder as you'd expect and the pocket with the thermistor that the ASHP is reading is halfway up (the immersion is not being externally controlled here, just using its own thermostat). The hot water is being drawn off the top of the cylinder.
I can't find any manual for this immersion, but the only downloadable manuals on the Thermowatt website say the factory set should be 65C or 75C for various models. That's also what the label seems to imply:
It seems to be really struggling to heat the water. I think this points to a faulty thermostat on the immersion, but before I go draining everything down to change it did I perhaps miss something?
Also to add, on the original Grant wiring there was a separate tank stat which is in the pocket at the top of the cylinder. I have disconnected this and am just relying on the thermostat inside the immersion heater. Was that a mistake?
Posted by: @prunusAlso to add, on the original Grant wiring there was a separate tank stat which is in the pocket at the top of the cylinder. I have disconnected this and am just relying on the thermostat inside the immersion heater. Was that a mistake?
Not sure which sensor you are referring to.
When the heat pump heats the DHW (ie normal DHW heating not the legionella cycle) it relies on the tank sensor (NOT the one associated with the immersion) to tell it what the temperature of the water is. This is normally in a pocket about half way down and must not be removed.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Here is the full setup (I really should tidy that wiring...):
Disconnected tank stat at the top pocket, thermistor going to the ASHP in the middle pocket, immersion in the bottom pocket. The buffer is below that out of shot.
Tank stat:
Grant's wiring for this is as if it was a classic gas boiler: boiler programmer -> tank stat -> immersion. There is additionally a single DIN timer and contactor for immersion boost. AIUI the tank stat is used for setting the normal ASHP target DHW temperature (eg 45 as it's currently showing) where the Grant wiring centre then shuts off hot water mode once the tank stat opens. I believe the boost timer overrides the tank stat and heats the hot water using only the thermostat in the immersion, to get it up to 60+C for legionella. Because this immersion timer has no temperature sensing the whole legionella cycle is done open-loop by immersion alone (ie it's just run for a fixed time, without preheating by ASHP and just hoping nobody ran a bath in the middle).
I have disconnected the whole Grant wiring centre and replaced it with controls from the ASHP, ie the ASHP does it's own legionella cycle and then it's own DHW boost output kicks in the immersion once it has achieved maximum temperature, according to the thermistor. That means the ASHP just powers the immersion until 60C is sensed. The thermostat on the immersion wants to be set higher (say 65) so it will reach 60C and be shut off by the ASHP before the immersion shuts itself off.
But perhaps I misunderstood something about this particular immersion? The instructions for those Thermowatts I can find are clear as mud.
Posted by: @prunusGrant's wiring for this...
like almost everything else in Grant's original wiring schemes, should be ignored - as you have
Posted by: @prunusI have disconnected the whole Grant wiring centre and replaced it with controls from the ASHP, ie the ASHP does it's own legionella cycle and then it's own DHW boost output kicks in the immersion once it has achieved maximum temperature, according to the thermistor. That means the ASHP just powers the immersion until 60C is sensed. The thermostat on the immersion wants to be set higher (say 65) so it will reach 60C and be shut off by the ASHP before the immersion shuts itself off.
Very sensible!
Posted by: @prunusBut perhaps I misunderstood something about this particular immersion? The instructions for those Thermowatts I can find are clear as mud.
Do you know what the 'tank stat' did before you disconnected it?
Posted by: @prunusI have a Grant Aerona3 13kW and I've wired it so the ASHP controls the legionella cycle (disconnecting the spurious Grant timer box they install). The way this works is the ASHP runs up the hot water to the maximum temperature it can manage, then hands over to the immersion heater for the last few degrees to get it to 60C. On the standard setup it has 2 hours to do that - there's a service manual parameter to extend it to 3 hours, which I've done. After 3 hours the water is only at 50C and the ASHP flashes 'LC' meaning legionella cycle failed. Next week comes around and it does legionella again and the same happens... every week.
Does it actually ever enable the immersion. If not it may be that 'backup heater' has not been enabled in the installer menu, or if it has its parameters set up wrongly.
Alternatively it may be that the immersion simply doesn't go far enough down the tank so it heats the top third (above the Grant temperature sensor) then turns itself off before the the bit down to the Grant sensor gets heated. This may conceivably be worse than not running legionella at all! My Vaillant tank is like that, the immersion heater really only heats the top bit of the tank and the sensor barely notices it. In this case however its doesn't matter much because the Vaillant does the legionella cycle natively without invoking the immersion heater, and gets it to 69C.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I think we're talking at cross purposes here. The above test is with the ASHP completely turned off. The setup is mains -> power meter -> contactor -> immersion, and the contactor is turned on. ie the immersion is just constantly across the mains and yet it can only achieve 57C at its maximum setting. There is no thermostat in circuit beyond the thermostat integrated into the immersion.
The immersion is at the bottom of the cylinder but that should mean that the sensor in the middle of the cylinder and the water drawn off should be hotter than 57. In the draw-off after running the hot tap for a minute or two the highest I could get on my coffee and jam thermometers was about 55-56, which is probably within measurement error. (Hot side of kitchen mixer tap, not anything fancy like a thermostatic mixer)
So either the immersion is faulty or I misunderstood its settings. I can't think of anything else it could be, unless I misunderstood something about how this immersion operates?
(also to note that supposedly the safety cutout reset is a button on the immersion but seemingly that is pushed in on the pictures above, suggesting the cutout hasn't activated)
Posted by: @prunusI think we're talking at cross purposes here. The above test is with the ASHP completely turned off. The setup is mains -> power meter -> contactor -> immersion, and the contactor is turned on. ie the immersion is just constantly across the mains and yet it can only achieve 57C at its maximum setting. There is no thermostat in circuit beyond the thermostat integrated into the immersion.
The immersion is at the bottom of the cylinder but that should mean that the sensor in the middle of the cylinder and the water drawn off should be hotter than 57. In the draw-off after running the hot tap for a minute or two the highest I could get on my coffee and jam thermometers was about 55-56, which is probably within measurement error. (Hot side of kitchen mixer tap, not anything fancy like a thermostatic mixer)
So either the immersion is faulty or I misunderstood its settings. I can't think of anything else it could be, unless I misunderstood something about how this immersion operates?
(also to note that supposedly the safety cutout reset is a button on the immersion but seemingly that is pushed in on the pictures above, suggesting the cutout hasn't activated)
Ah. Ok with immersion at bottom then the whole cylinder should eventually heat. The hottest point will still be by the element, but you would expect everything above that to rise eventually to whatever the thermostat setting is on the immersion or perhaps a tiny bit below if the currents local to the immersion stat cause local hot spots.
Im wondering if there is actually a fault, or whether 57 is the temperature at which the immersion thermostat (possibly nominally set to 60) cuts out. Obviously at this point it would cease drawing power which you would detect. I cant see how it can continue to draw power without the tank continuing to heat, unless there is a heat sink! Otherwise it hat would be violating the laws of thermodynamics.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I suppose it could be that 57C is the maximum achievable temperature by the immersion heater, but I thought the point of the adjustment is you could set them higher than that? eg the manual for the 420011210800 "Thermowatt RT 1” ½ IP65 with RTS thermostat - Bipolar double safety disconnection" says:
The immersion heater is supplied with a RTS/RTS PLUS thermostat. Functional temperature is factory set to 75°C, with adjustable temperature. To maintain safety, any replacement thermostat must be of the same type. RECOMMENDATION: low water temperature is recommended to reduce limestone deposit (Not lower than 60°C).
and that has a picture that looks like the same as the back of mine. But nowhere, either on the product page or in the zipped PDF, does it state minimum/maximum thermostat temperatures.
As you say, if it's powered either the heat has to go somewhere or it's shut itself off - the power meter indicates it's shut itself off, which points to the internal thermostat. Moving the setting on the internal stat does seem to improve the shutoff temperature slightly. But could it be so out of calibration?
Posted by: @prunusI suppose it could be that 57C is the maximum achievable temperature by the immersion heater, but I thought the point of the adjustment is you could set them higher than that? eg the manual for the 420011210800 "Thermowatt RT 1” ½ IP65 with RTS thermostat - Bipolar double safety disconnection" says:
The immersion heater is supplied with a RTS/RTS PLUS thermostat. Functional temperature is factory set to 75°C, with adjustable temperature. To maintain safety, any replacement thermostat must be of the same type. RECOMMENDATION: low water temperature is recommended to reduce limestone deposit (Not lower than 60°C).and that has a picture that looks like the same as the back of mine. But nowhere, either on the product page or in the zipped PDF, does it state minimum/maximum thermostat temperatures.
As you say, if it's powered either the heat has to go somewhere or it's shut itself off - the power meter indicates it's shut itself off, which points to the internal thermostat. Moving the setting on the internal stat does seem to improve the shutoff temperature slightly. But could it be so out of calibration?
If the cut out is at 65 I would guess the max design temp is 60, so actual of 57 is plausible albeit at the margins. Bear in mind these are generally bimetallic strip thermostats so yes it could be that far out of calibration (if they even bother calibrating them, which frankly I doubt).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Well, if that's the right PDF the factory set is supposed to be 75 so in theory it should go up at least that far when cranked up to the max. A bit poor that it could be 18C off, especially where legionella might be a risk. I suppose I'll have to replace it with something better - any recommendations?
Edit: ah, does F.65/S.75 on the label mean 'max functional temp 65C, safety cutout temp 75C'? So it's not possible to set it above 65 +/- lots?
@prunus Hmm
57 vs 65 does seem a way off, but perhaps not impossible. Given the purpose, one might argue that its not fit for purpose!
I cant advise on immersion heaters TBH, my guess a fair proportion are made in the same factory in China then just branded differently. They arent expensive, but of course you will need to drain the tank.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,613 Topics
- 61 K Posts
- 2,906 Online
- 6,979 Members
Join Us!
Worth Watching
Latest Posts
-
@toodles I thought I’d enter the Temple Of Apollo to se...
By Papahuhu , 32 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
In view of No test needed. It does what I thought...
By JamesPa , 2 hours ago
-
RE: Electricity price predictions
I admit that the Cosy tariff encourages a bit of batter...
By KevH , 2 hours ago
-
RE: Anyone concerned about GivEnergy?
From the thisistsaffordshire web page it is indeed impo...
By KevH , 2 hours ago
-
We don't have time-stamps on those screenshots, nor do ...
By Transparent , 4 hours ago
-
It seems odd these companies don't design and ...
By ASHP-BOBBA , 17 hours ago
-
That's odd and concerning. Unless the pipework between ...
By JamesPa , 17 hours ago
-
RE: Ecoflow UK Support & Info Thread
As promised, the review is out:/p> See discount codes...
By Mars , 1 day ago
-
@cathoderay great, thank you.
By Painter26 , 1 day ago
-
RE: Microbore heat pump installs
When I wrote the piece I didn't have anything in mind, ...
By JamesPa , 1 day ago
-
RE: Water law settings... A year on
@jamespa I've adjusted a few parameters 201 is no...
By Profzarkov , 1 day ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@lejamaiscontent There’s a couple of things to add. We ...
By Judith , 1 day ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
That may well be correct. However we don't have enoug...
By Transparent , 2 days ago
-
RE: Rate the quality of your heat pump design and installation
@editor Thank you. I joined because I really liked your...
By claireisamazing , 3 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
@madsid I don't quite understand what extra you need...
By Bash , 3 days ago
-
@transparent thank you. Be Thursday before my mate giv...
By David999 , 3 days ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
@johnd our Peak system is no more. The installer cam...
By DaveC , 3 days ago
-
Hah! Well I guess we're all in the realm of conjectu...
By Transparent , 3 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Ah, not so useful then For sure, hopefully before ...
By JamesPa , 3 days ago
-
Thanks @editor I appreciate that things go wrong, bu...
By venkman , 3 days ago
-
RE: Home energy storage & battery register
AC coupled Pure Drive 10kW battery Solar PV Solis P...
By Little Lights , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: ispookie666 Manufacturer: Vaillant Mo...
By ispookie666 , 4 days ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I'm fairly new to the forum and have not voted. Back...
By ispookie666 , 4 days ago
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
@editor Thanks Mars. I look forward to the subsequent ...
By DavidB , 4 days ago