Hi,
I have a Samsung Gen6/Joule ASHP currently set with 3no. thermostats (1 per floor) controlling 3 heating zones (all radiators). I'd like to move to a single zone (or possibly 2?) controlled by the ground floor thermostat ("Thermostat 1") and use the radiator trvs to control room temps on the upper floors. The purpose of this is to
a) Increase the water flow to try increase efficiency (based on my understanding from heat geek videos), and
b) allow the bathroom towel rads in the upper floors be heated even if the upper floor is 'warm enough' according to the floor thermostat.
Currently each zone is wired to a a separate thermostat and I can see where these are connected in (2 wires from each thermostat). What i cant see from the samsung literature is how to switch control of these zones to the ground floor unit. Could i just disconnect Thermostat 2 and 3 and use jumper cables from Thermostat 1 to get things working as intended or is there a way to 'programme' this from the Samsung Controller?
Any assistance is appreciated in advance, I am struggling to make sense of the samsung/joule set up information to achieve this.
So I've found the answer to my own question. The joule control board is only wired in to the "Zone 1" of the gen6 controller. So zone 2 of the Samsung controller is irrelevant and however Zone 1 is set up will apply to all thermostat controls on the system.
In my case I am now trialling heating on pure weather compensation but with the thermostats acting as a high temp limit switch. So I have the thermostats on each level to 1 Deg above where I would like the room temperature and I will try playing with the water law settings (and maybe radiators) to dial it in.
To confirm the joule unit operates as such I contacted Samsung and confirmed that only the B22 live cable is connected between the Samsung board and the joule PCB. If there was B24 connected between the two it would control zone 2 on the Samsung controller
- 21 Forums
- 1,765 Topics
- 37.7 K Posts
- 33 Online
- 2,054 Members
Join Us!
Latest Posts
-
Just wondering what delta T folk use with their ASHP? ...
By TheBinMan , 7 hours ago
-
RE: Fitting emitters with output greater than room heat loss.
@jamespa Funny you said you have a Vaillant 7kw. Just t...
By bigvibes , 7 hours ago
-
Difficult positioning of air source heat pump
Hello, We are trying to get an heat pump installe...
By Rikiarn , 9 hours ago
-
RE: Battery...Full house back up
@broadsman - I'm unsure if those suggestions from @sae...
By Transparent , 10 hours ago
-
RE: Non standard houses with non standard owners
@jswhite If you design the system to suit the whole hou...
By ASHP-BOBBA , 12 hours ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Thanks, we're planning on a large normal radiator. Heat...
By RobinBennett , 12 hours ago
-
RE: Does turning down radiators preserve the heat in the water?
In my opinion, the water that doesn’t flow through the ...
By Toodles , 13 hours ago
-
RE: Samsung E911 intermittent issue
@netdonkey ok, So its sounds like the the Wilo is doing...
By ASHP-BOBBA , 17 hours ago
-
RE: Samsung ASHP scheduling help
@morh does that samsung device connect to the HP or the...
By cyrusir , 18 hours ago
-
RE: Samsung heat pump has arrived with damaged fins – do I accept it or send it back?
Damage is cosmetic is appears, but the result of poor h...
By AllyFish , 19 hours ago
-
RE: Smart meter installation – seamless or a potential nightmare?
The incomer cable probably only has a size-rating once ...
By Transparent , 19 hours ago
-
RE: How Many ASHPs Work Correctly From Commissioning Date ( The resolution page)
Oh yes, I see, interesting that one of the 1st posts wa...
By ASHP-BOBBA , 19 hours ago
-
RE: Which system is most efficient...
OK. Im not going to be able to answer the question, bu...
By JamesPa , 21 hours ago
-
Palo Alto / London – Dec. 5, 2024 – More than two dozen...
By Jeff , 22 hours ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@lokisam I am following this with interest as I also ha...
By Odynsfee , 1 day ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you give us an update on your tests?
By Mars , 1 day ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@editor Yes, it's their "Aira Generation 1" 8kW model: ...
By trungdong , 1 day ago
-
RE: Reducing heat pump vibrations through flat roof
@patrickvito Hi Patrick, thanks so much for taking the ...
By sten_super , 2 days ago
-
RE: Noise Issues with our Ecodan 8.5kW WM85VAA air source heat pump
@athlonoc Its unlikely the FTC is controlling a 3rd par...
By ASHP-BOBBA , 2 days ago
-
RE: Mitsubishi Ecodan Produced energy showing 'INVALID'
Hello! I tried your idea and disabled the cooling funct...
By sorin , 2 days ago
Latest Topics
-
By TheBinMan 7 hours ago
-
Difficult positioning of air source heat pump
By Rikiarn 9 hours ago
-
Does turning down radiators preserve the heat in the water?
By Tufty 15 hours ago
-
Non standard houses with non standard owners
By jswhite 18 hours ago
-
By Jeff 22 hours ago
-
Which system is most efficient...
By bigvibes 2 days ago
-
What should we do with our Aga?
By RobinBennett 2 days ago
-
Reducing heat pump vibrations through flat roof
By sten_super 3 days ago