Samsung Gen6 Settings - Remove Zoning
Hi,
I have a Samsung Gen6/Joule ASHP currently set with 3no. thermostats (1 per floor) controlling 3 heating zones (all radiators). I'd like to move to a single zone (or possibly 2?) controlled by the ground floor thermostat ("Thermostat 1") and use the radiator trvs to control room temps on the upper floors. The purpose of this is to
a) Increase the water flow to try increase efficiency (based on my understanding from heat geek videos), and
b) allow the bathroom towel rads in the upper floors be heated even if the upper floor is 'warm enough' according to the floor thermostat.
Currently each zone is wired to a a separate thermostat and I can see where these are connected in (2 wires from each thermostat). What i cant see from the samsung literature is how to switch control of these zones to the ground floor unit. Could i just disconnect Thermostat 2 and 3 and use jumper cables from Thermostat 1 to get things working as intended or is there a way to 'programme' this from the Samsung Controller?
Any assistance is appreciated in advance, I am struggling to make sense of the samsung/joule set up information to achieve this.
So I've found the answer to my own question. The joule control board is only wired in to the "Zone 1" of the gen6 controller. So zone 2 of the Samsung controller is irrelevant and however Zone 1 is set up will apply to all thermostat controls on the system.
In my case I am now trialling heating on pure weather compensation but with the thermostats acting as a high temp limit switch. So I have the thermostats on each level to 1 Deg above where I would like the room temperature and I will try playing with the water law settings (and maybe radiators) to dial it in.
To confirm the joule unit operates as such I contacted Samsung and confirmed that only the B22 live cable is connected between the Samsung board and the joule PCB. If there was B24 connected between the two it would control zone 2 on the Samsung controller
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 315 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@stevettweed, did you get a quote from Aira?
By Mars , 5 minutes ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
@jamespa Apologies I did know that but I seem to have r...
By Sim0n0 , 38 minutes ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@majordennisbloodnok Thanks. Yes, no problem. Wher...
By Bash , 2 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Here's what mine typically looks like. Hence why I ...
By benson , 2 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas Hello Henri, I know that we have had an exchange ...
By DavidAlgarve , 2 hours ago
-
RE: MELcloud scheduling misbehaviour
@downfield my understanding is that you can have a maxi...
By Richard24738 , 4 hours ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
If it is combined with the BUS and they make it all goo...
By Batpred , 5 hours ago
-
RE: Electricity price predictions
Before I dive into the issue of a strategy which helps ...
By Transparent , 7 hours ago
-
RE: Advice on reading thermal images
@editor Thanks Mars, better price from the website and ...
By colinc , 10 hours ago
-
RE: Signenergy AI Mode - How long does it take to learn a usage pattern?
@editor apparently it helps optimise charging and disch...
By Grantmethestrength , 10 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
To be blunt, I wouldn't choose. If we were to move to...
By Majordennisbloodnok , 11 hours ago
-
RE: Diagnostic Data Needed for Repeatedly Failing Tesla Powerwall 3 System
Yes, some queries were raised on github recently: ...
By Batpred , 11 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@cold123456 Mitsubishi has failed to respond to my com...
By Ecoste , 12 hours ago
-
RE: Grant Aerona Short Cycling
@steam-powered I'm currently running 30@-7 23@15 so cur...
By damonc , 15 hours ago
-
RE: What a Bad Heat Pump Installation Looks Like
That's pretty impressively incompetent. In our develo...
By Steelbadger , 23 hours ago
-
RE: Marginal pricing and UK electricity costs
@judith I just realised he’s the guy with the ‘minimum ...
By Lucia , 24 hours ago
-
Midea ASHP Issues with Smart Home App losing connectivity with the Wall Unit
Hi, First Post - replaced out 16 year old gas boiler ...
By SteveT , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: @lucia Manufacturer: Daikin Model: E...
By Lucia , 1 day ago
-
RE: Heat Pump Training vs. Real-World Installation
@judith I looked at the control challenge of balancin...
By Lucia , 1 day ago