Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Heatpunk Floor plan issues
OK so about 110 sq m with cavity wall insulation a good level of loft insulation, double glazing but uninsulated floors. 'Feels' like 3-5kW or less. My house, 7kW, needed 3100 kWh to heat it month to date (thats to house not from grid), yours is 1274kWh, suggesting yours is 2.8kW.
So I think we know your house loss is ~3-5kW probably towards the low end of that range. So you are likely looking at say a 5kW heat pump (there arent many that are actually less and you probably want this for DHW) and 2kW or thereabouts per floor. You may well need a volumiser to keep system volume up to reduce short cycling.
As to emitters, given the geometry you could possibly consider a single A2A on the landing, if you leave the bedroom doors open, plus something in the bathroom. However it might be difficult to manage/unsatisfactory and, if it were my house I would want to speak to someone first who has actually tried this arrangement before departing from A2W. Its just possible you wont need heating upstairs at all if you dont mind it fairly cool, but you have said you need cooling upstairs so something has to go there. You could possibly run the experiment with no upstairs heating in your current setup, see how the rooms settle.
Downstairs I cant see A2A being a good fit, its just too segmented, although you might just possibly consider A2A in the 4 main rooms. But it lends itself to A2W. Conservatory a possible problem space depending on solar gain/insulation/shading.
I would say there is at least a reasonable chance that microbore would work. In principle you can get 750W through microbore at 0.9m/s and DT5 which may be enough for every room. It will depend on individual room calculations and plumbing geometry however and needs to be worked out properly.
Cooling - if you go A2A obvious, if A2W perhaps fancoils in living room and landing, although the microbore feeds may limit effect so if you could do a couple more that would be good. No guarantee this will work well enough and certainly it wont be full aircon, just some light relief. Is closing blinds/curtains on the south side an option?
Im sure others will have ideas. Id probably do the calcs, see if I can get away with microbore and if so just upgrade rads, if not think more carefully about A2A, but this is just a gut reaction not one borne out of any experience except my own house and a couple of community centres (in which I did A2A - but these were a small number of large spaces).
Hope that helps at least a bit.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks, I'm thinking the same, I cannot make A2A work unfortunately without open plan downstairs.
The microbore is either blocked or the system really unbalanced, some rads barely get warm.
I should get someone round to a proper look but now the warm homes low/no interest loans have been announced that makes me want to wait until the details are fleshed out on that. I can at least start looking into local heat geeks.
- 26 Forums
- 2,591 Topics
- 60.3 K Posts
- 293 Online
- 6,924 Members
Join Us!
Worth Watching
Latest Posts
-
RE: How much can an east/west solar solar system be oversized?
@colinc I'm lucky to have a roof where the only shade i...
By Falesh , 44 minutes ago
-
@transparent it’s insulation on top of insulation to mi...
By David999 , 46 minutes ago
-
RE: Rate the quality of your heat pump design and installation
@keithb I actually found a video on YouTube to set weat...
By Josejo , 48 minutes ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Glad the heating is changed. Monitor and tweak if nece...
By JamesPa , 5 hours ago
-
Without a detailed analysis of the hydrodynamics I woul...
By JamesPa , 5 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge no idea if they’ve made changes, but I got...
By AndrewJ , 14 hours ago
-
RE: Say hello and introduce yourself
@alva welcome to the forums and feel free to start a ne...
By Mars , 15 hours ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
So under part G or the G3 rules you have a responsibili...
By ASHP-BOBBA , 16 hours ago
-
RE: Electricity price predictions
Mention on the news about Octopus and one or two other ...
By Toodles , 20 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 2 days ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 2 days ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 2 days ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 2 days ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 3 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 3 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 3 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 3 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 3 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 4 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 4 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 4 days ago