Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Hi
We are looking to install ASHP for our Edwardian detached home. Had a few heat surveys which tend to recommend a 12kW ASHP. However, rule of thumb from Dr Modesta and our annual 22MWh gas consumption indicates only 5kW heat loss. (Our home is well insulated, EPC = B). So my question is...What is the disadvantages of oversizing and would it be smart to compromise at say 8kW ASHP?
Thank you for any ideas and to Mars for this excellent resource.
Slowly built up 4kW peak PV, 19.5kWh battery system, BMW i3 got us Octopus Intelligent Go low price off-peak supply, thorough insulation to EPC B in detached 1905 home, underfloor heating 26m2 of total 160m2. Vaillant 7kW pump, Unistor 300L cylinder. All working well and saving £1,500 / year versus gas central heating.
Rules of thumb are generally pretty rubbish for heat pump sizing and your gas usage patterns may or may not be a good indication.
Common theme seems to be you need 12kW. But the average house in the UK actually only needs sub 6kW.
I would ask to see the heat loss calculation and review it and pass comments back. Number of air changes per hour can be just daft for example, taking no notice of fabric improvements also. Do you have evidence of fabric improvements - without they may have just ignored etc.
General disadvantage of oversizing
Heat pump cycling
Large heat pumps need very high flow rates, so end up with big pipes, or a buffer (not good for efficiency), bigger radiators than needed etc. So everything gets bigger than needed, you also get a bigger bill than needed, to pay for all that bigger stuff.
The correct size is max heat loss plus an allowance for DHW heating. So if your heat loss was 5kW, or 120kWh a day being able to deliver 120kWh in say 22 hrs. So 5.5kW being able to be delivered at your outside design temperature.
In addition to the above oversizing means you are likely to be running the compressor at an inefficient point on it's modulation curve for much of the time, reducing COP.
My personal view, which differs a bit from @johnmo, is that gas readings, properly interpreted, can (but won't always) provide the only solid upper bound on heat loss available, so are well worth factoring in in addition to surveys, possibly only as a sense check but possibly as the prime source (depending on circumstances such as how the house is currently heated)
However I agree rules of thumb aren't sufficient, you need a bit more. Do you have smart meter readings, they can tell you a lot more. What's your pattern of heating and how old is your boiler, that can help interpret the has readings more intelligently.
I would also do what @johnmo suggests regarding the surveys.
Once you have that data put it all together to get the best data available.
Feel free to ask for more advice/post some of your data.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@johnmo thanks @johnmo that is great info - I will be discussing this with our best prospect installer.
I just needed some ideas to make it a discussion instead of a lecture!
So far I have just too much conflicting information:
1. Dr Modesta of the National Physics Lab in Teddington recommends using annual gas consumption (20MW) required to heat the house divided by Heating Degree Days at the local weather station - gives our heat loss 5kW
2. The "B" EPC estimates 18.5MWh to heat the house and water and the two surveyors are broadly the same.
3. Surveyors have estimated 10kW heat loss. But in the surveys, the ACHs seem unreasonably high (3 in bathrooms, loo & utility, 2 in kitchen, hall & landing, 1.5 in living & dining rooms and 1.0 in the bedrooms). I would expect the average ACH for our well draught-proofed house, especially in winter when we are careful with opening doors etc, to be under 1 and not the approx. 2 that is being used to exaggerate the ASHP sizing.
So what is right - the real world historical heating MW data and a world leading scientist or a detailed fabric heat loss estimation multiplied by MCS nonsensical ACHs?
Is there a heat geek approach to ACH that might sort this out?
many thanks
Slowly built up 4kW peak PV, 19.5kWh battery system, BMW i3 got us Octopus Intelligent Go low price off-peak supply, thorough insulation to EPC B in detached 1905 home, underfloor heating 26m2 of total 160m2. Vaillant 7kW pump, Unistor 300L cylinder. All working well and saving £1,500 / year versus gas central heating.
@jamespa thanks @jamespa. I really appreciate your thoughts on this.
Especially the benefits of not oversizing!
Our boiler is a condensing Worcester almost 10 years old and it does fine. We do have gas meter readings per month but not anything smarter. Annual consumption is a steady 22MWh.
Another thing that bothers me is that if a well installed ASHP can deliver SCOP of 4, why cant a 5kW heat pump deliver 20kW?
Slowly built up 4kW peak PV, 19.5kWh battery system, BMW i3 got us Octopus Intelligent Go low price off-peak supply, thorough insulation to EPC B in detached 1905 home, underfloor heating 26m2 of total 160m2. Vaillant 7kW pump, Unistor 300L cylinder. All working well and saving £1,500 / year versus gas central heating.
Posted by: @matwinif a well installed ASHP can deliver SCOP of 4, why cant a 5kW heat pump deliver 20kW?
I love it !
That's an excellent question for the Welcome topic!
The maths works the other way around from what you suppose.
The kW figure for the heat-pump is its output.
Thus a 12kW heat-pump would draw 3kW of electricity if it was operating with a SCOP of 4.0
... but 4kW input if the SCOP was only 3.0.
Save energy... recycle electrons!
@transparent thanks. Fighting confusion one step at a time. Do you have a view on ACH exaggeration?
Slowly built up 4kW peak PV, 19.5kWh battery system, BMW i3 got us Octopus Intelligent Go low price off-peak supply, thorough insulation to EPC B in detached 1905 home, underfloor heating 26m2 of total 160m2. Vaillant 7kW pump, Unistor 300L cylinder. All working well and saving £1,500 / year versus gas central heating.
Hang on. Let me just have a look through my library of views....
It's Friday afternoon, and my more serious views have already been taken this week.
I could offer you a distant view of Bodmin Moor; that's an Agricultural Cornish Horizon.
Or, at the smaller end of the scale, I had a fleeting view of an Accelerated Collided Hadron... but it lasted barely a femtosecond.
Would you like to clarify which particular ACH you're interested in,
and just how exaggerated you think it shouldn't be?
Save energy... recycle electrons!
@matwin, welcome to the forums.
Expanding on transparent's reply, it's worth saying that a 5kW heat pump can deliver 5kW of heat... that’s its rated capacity. If its SCOP is 4, that just means that over the course of a heating season, it’s using about 1.25kW of electricity to produce that 5kW of heat. But it’s still only delivering 5kW. It can’t suddenly become a 20kW machine. Hope that helps.
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained
@editor thanks Mars. Your channel is making a big difference!
Slowly built up 4kW peak PV, 19.5kWh battery system, BMW i3 got us Octopus Intelligent Go low price off-peak supply, thorough insulation to EPC B in detached 1905 home, underfloor heating 26m2 of total 160m2. Vaillant 7kW pump, Unistor 300L cylinder. All working well and saving £1,500 / year versus gas central heating.
@matwin really pleased to hear that… thank you for your positive feedback.
Feel free to start a new, dedicated topic for your journey.
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained
Posted by: @matwin@transparent thanks. Fighting confusion one step at a time. Do you have a view on ACH exaggeration
I don't have much concrete evidence but
- The only way to explain the discrepancy between my calculated and actual heat loss is to assume ach =0.5 instead of 2-3
- Several of the better installers have gone on record as saying that they believe ach is overestimated and/or that when they have measured ach and it's never more than 1
- There is clearly an epidemic of loss overestimation generally.
One thing I don't yet understand is the basis of the figures. I believe that ach tests for building regs are done by pressuring the house and it's this figure that corresponds to the figures used for loss estimates.
However we don't generally pressurise houses, so the actual figure is due to natural infiltration or (usually but not always) very localised forced ventilation amounting to nothing like the assumed figure when averaged out over a whole house.
My strong suspicion, for which I have some very weak circumstantial evidence, is that MCS used the only figures that they could find (and attribute to another body thus avoiding liability) not anything that has a scientific basis for the purpose in question.
If you have consumption per month (particularly if it's for more than a year) you could try plotting that vs degree days or average temperature, which you can download from various websites. This may give you a bit more info, although unless you have several years of data probably not (but it will still increase confidence levels so very likely worth doing).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,724 Topics
- 63.8 K Posts
- 448 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Microgeneration Certification Scheme (MCS)
I’ve just spotted that Ian Rippin is leaving MCS as CEO...
By Mars , 10 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
Hi. I have 16 panel solar panels producing about 20k...
By peterackstraw , 4 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 5 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 19 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago