Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Zilmet 110 ultra pro 18 (type 19) expansion vessel - Horizontal installation
This has been installed horizontally on top of a kitchen cabinet which houses the hot water tank. At the time of install I challenged the plumber on the orientation and he said that these types can be horizontal and all is fine.
I have looked on the Zilmet website and their documentation states:
"Expansion vessels should always be installed in a vertical orientation with the water
connection at the bottom.
Our requirements are simply that the vessel be installed in a way that allows future access,
and ideally be in the coolest available part of the system to assist with longevity of the
membrane. At no time can a vertical vessel be mounted horizontally, or be mounted to a
wall or framework suspended by itʼs legs."
Now, the exact model number 1100001955 is not listed in the manual and they do have "vertical and Horizontal" models. But to me this one looks like it should be Vertical as it has a wall brace.
Anyone else have this installed or experience of these?
I have sent an email to the manufacturer to confirm, hopefully i get an official reply.
Posted by: @saf1973the exact model number 1100001955 is not listed in the manual and they do have "vertical and Horizontal" models. But to me this one looks like it should be Vertical as it has a wall brace.
Anyone else have this installed or experience of these?
Thanks for including a photo @saf1973
I have five expansion vessels of differing sizes and orientations.
But it has much to do with me having a well and no mains water supply! 😎
All of these are self-installed, and I've had to replace one due to a failed membrane.
Three are for potable (treated) water, and the others for expansion in heating circuits.
The good news is that I therefore have the experience you're looking for!
The quote from the Zilmet site "Expansion vessels should always be installed in a vertical orientation with the water connection at the bottom" needs context.
It is not always the case.
Domestic well-pumps are often supplied with a horizontal expansion vessel beneath them - for which Zilmet is one of the manufacturers!
Nor is a welded bracket an indication of the preferred orientation.
Different models of expansion vessel are required depending on the 'type of water' in the system they are connected to.
Potable water, suitable for drinking, is usually connected to a vessel painted blue if it is made with cast mild steel.
But it can be left unpainted if stainless steel is chosen.
If the fluid contains system inhibitor chemicals, such as that which runs through radiators, then the vessel manufacturer may recommend that the internal rubber diaphragm is evenly in contact with that fluid.
That would occur in a vertical orientation such as you describe.
Each vessel is different, which is why it's important to select the correct one for the application.
Over time (years) there will be 'leakage' of air across the membrane.
That which enters a heating circuit will be eradicated through the air-release valves.
But the slow migration of air (gas) molecules will reduce the pressure in the expansion vessel.
This pressure is restored by using a car foot-pump to add air through the schrader valve beneath the black cap at the opposite end to the water connection.
It's tricky to do that whilst squeezing yourself into a kitchen cupboard!
Moreover, to obtain the required pressure, it's usual to have a shut-off valve on the water connection.
Otherwise you're pushing the foot-pump against the entire water circuit!
In tight situations I have two shut-off valves on the flexible connection to the expansion vessel.
By shutting both, I can remove the entire vessel from the circuit, whether it has any pressurised water inside it or not.
I can then take it outside and re-pressurise it with ease.
In most cases a pressure vessel should be oscillating around the half-full position.
If it's completely full of water then the pre-pressurised air part of the vessel needs pumping up.
You can deduce this by placing the vessel on a set of bathroom weighing scales.
1 litre of water has a mass of 1Kg.
Does that help?
Save energy... recycle electrons!
@transparent thanks for the post!
Mine is connected to the combination valve which sipplies the cold feed to the DHW tank and balanced cold to the house, so from your post it would see that it does not matter it's orientation so much? Also, this is a white vessel so is it the wrong type?
I am thinking that if it is on its side any sediment would build up under the membrane and potentially rub against it with the friction eventually bursting it. If it is vertical the sediment would remain at the bottom of the vessel and not touch the membrane. Fortunately I do have a whole house filter so sediment should be minimal.
I had a similar unit in my previous property where I maintained it, i had to release the water pressure in the system to be able to pump up the diaphram. In one instance i replaced it as the diaphram had burst. It was wall mounted but i cannot remember if that was for Potable water or the heating system.
i've just found this good YT video that explains a lot and shows a vessel in horizonal orientation...
Posted by: @saf1973... from your post it would see that it does not matter it's orientation so much? Also, this is a white vessel so is it the wrong type?
I don't think you can deduce that much from what I've said!
Zilmet will specify the orientation for each design which they offer.
It depends on a number of factors, including the composition of the butyl-rubber membrane, and the type of lacquer which may have been applied to the internal walls.
There are more combinations of features than can possibly be described by the colour which is used to paint the outside.
It is no longer the case that all manufacturers use blue to identify suitability for potable water.
As that YT video demonstrates, the new vessel chosen by the presenter is coloured white, but he introduces it as suitable for potable water!
I too have had difficulty finding the Zilmet specification sheet for your particular vessel.
However Advanced Water's site does have a document you can download which allows you to calculate the pre-charge pressure and the required total capacity you need.
Save energy... recycle electrons!
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 1,002 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
Every manufacture has a guide and service list...
By ASHP-BOBBA , 21 minutes ago
-
RE: Summer usage. Why is my Vaillant Aerotherm using so much energy on "heating"?
I don’t know how the Aerotherm works so can’t comment o...
By AndrewJ , 38 minutes ago
-
Its good kit the Midea and significantly cheaper, you w...
By ASHP-BOBBA , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Have you tried cutting the grid feed to see what actual...
By JamesPa , 3 hours ago
-
Contractors pack for inta antifreeze valves are around ...
By ASHP-BOBBA , 3 hours ago
-
RE: Renewables & Heat Pumps in the News
Critics and naysayers will be negative whatever the gov...
By JamesPa , 3 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 13 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 14 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 16 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 17 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 18 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 21 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 1 day ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 2 days ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 3 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 3 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 5 days ago