Posted by: @ashp-bobba@old_scientist 35 DegC outdoor air temperature?
Yes, that's the default value, but can be set between 10C to 35C.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist I see, thats good, so set for a couple Deg above design and you have an over heat stop point. I am sure most manufacturers have something like this somewhere in the vast control settings.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
thanks both. Very useful.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Mitsubishi Ecodan just runs the same flow temp when it reaches the limit of the set curve.
I am not aware of any way of telling the heat pump not to run above a certain outside temp.
Mitsubishi Ecodan just runs the same flow temp when it reaches the limit of the set curve.
I am not aware of any way of telling the heat pump not to run above a certain outside temp.
On a podcast a few months ago, one of the panelists mentioned that most heat pumps (and possibly boilers with outdoor sensors) are designed to stop running when the CIBSE outdoor temperature threshold is reached. I don’t remember the exact number offhand, but I think it was a very specific 15.5C.
I haven’t come across specific documentation confirming whether Mitsubishi Ecodan follows this principle, but it might be worth checking the service menu or installation manual to see if there’s a parameter for a high outdoor temperature cut-off.
In our case, I’ve not seen this setting anywhere, but I’ll check again today. That’s the reason we just turn ours off manually to prevent heating if, for example, the temp drops to 14.5C for a period of time.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @garyMitsubishi Ecodan just runs the same flow temp when it reaches the limit of the set curve.
I am not aware of any way of telling the heat pump not to run above a certain outside temp.
See my post https://renewableheatinghub.co.uk/forums/postid/44973 - it's called summer mode and is in the service menu.
Posted by: @editor
Mitsubishi Ecodan just runs the same flow temp when it reaches the limit of the set curve.
I am not aware of any way of telling the heat pump not to run above a certain outside temp.
On a podcast a few months ago, one of the panelists mentioned that most heat pumps (and possibly boilers with outdoor sensors) are designed to stop running when the CIBSE outdoor temperature threshold is reached. I don’t remember the exact number offhand, but I think it was a very specific 15.5C.
I haven’t come across specific documentation confirming whether Mitsubishi Ecodan follows this principle, but it might be worth checking the service menu or installation manual to see if there’s a parameter for a high outdoor temperature cut-off.
In our case, I’ve not seen this setting anywhere, but I’ll check again today. That’s the reason we just turn ours off manually to prevent heating if, for example, the temp drops to 14.5C for a period of time.
My Vaillant definitely has a 'Max outside temp for heating' parameter.
What it doesn't have, unfortunately, is a 'Max solar irradiance for heating' parameter. For much of this week its been quite chilly outside. Solar gain has dominated during the day, but then in the evening the house starts cooling. So really I need to turn off the heating during the daytime, and put it back on evening and night. I could set up a timed program to do this I suppose!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa use expanded mode! It’s ideal for that, and I’ve just moved back to it.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
@judith Thanks, Ill give it a go.
Given the tight hysteresis do you turn up the target temperature a bit to ensure it switches back on early enough in the evening?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Vailant arotherm+ has a setting to turn off heating when OT is above the set point. 16°c by default
-
Warm weather and heat pumps.
3 months ago
-
Savings - using Weather Compensation & Time of Use Tariffs
5 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
6 months ago
-
LG Therma V. Software upgrades, AI (weather compensation), SCOP
1 year ago
-
LG Therma V R32 Monobloc. Setup advice inc flow temperature & weather compensation
2 years ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,123 Topics
- 46.7 K Posts
- 67 Online
- 4,531 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: ASHP heat output monitoring
As you say its poor either way. I have tried to find o...
By JamesPa , 2 hours ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 4 hours ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 4 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
The current FAQ says it's not compatible with existing ...
By Old_Scientist , 5 hours ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 7 hours ago
-
RE: 300 Liter Tank - Do I have to heat it all?
Cross references for @martingale Background discussi...
By Transparent , 21 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@terry1812 Oh Good! Pleased to help if I can! Regards, ...
By Toodles , 1 day ago
-
It's unclear to me how the Smart Control project work b...
By Transparent , 1 day ago
-
RE: Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
@pavel, this isn't about discrediting Chinese products....
By Mars , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We had an excellent four months (11/3 to 15/7) generati...
By JulianC , 4 days ago
-
RE: Is this just haze or something more?
I think the present somewhat cooler hazy days show the ...
By Judith , 4 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
All noted and accepted and as I say I am sorry that you...
By JamesPa , 4 days ago
-
I think it is very much me that is sitting outside the ...
By Grantmethestrength , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
Aggregators have been recognised for many years, and it...
By Transparent , 5 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Great news I edited my previous post (probably af...
By JamesPa , 5 days ago
-
RE: Double or Triple Glazed Windows?
@toodles Glad to hear things are progressing well for y...
By TRBob , 5 days ago
-
How to waste energy (and time) playing with AI.
A friend of mine who subscribes to an AI service was ex...
By Toodles , 6 days ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@topher you’re more than welcome to, yes. I’ll send you...
By Mars , 7 days ago