Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Warmflow ASHP costing a fortune to run and ignored by installer

78 Posts
8 Users
6 Reactions
21.4 K Views
(@myanthony)
Eminent Member Member
Joined: 3 years ago
Posts: 33
Topic starter  
951D89FF 9B36 41E5 BF45 F2F741329ADA
DDAE52EE 7F52 48CB 8EC0 1498E29FCC00
0A7543CA E290 44F7 85DC 02F25A0A71D1
69096DAB BA87 40B9 9FBE 23F06DF0B96F
C0749CE8 123B 4BBC 8CCB EE4FAE919337


   
ReplyQuote
(@hughf)
Honorable Member Member
Joined: 4 years ago
Posts: 489
 

£10 says there isn’t one 


Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 5 years ago
Posts: 4425
 

@myanthony

The pipe with the isolation valve with the blue handle, to what equipment does the pipe connect?



   
ReplyQuote



(@hughf)
Honorable Member Member
Joined: 4 years ago
Posts: 489
 
6230 F675E15F E514 410B 9AF6 43BF822DCD38

Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote
(@myanthony)
Eminent Member Member
Joined: 3 years ago
Posts: 33
Topic starter  

@derek-m I’m sure that’s for old biomass connection.



   
ReplyQuote
(@hughf)
Honorable Member Member
Joined: 4 years ago
Posts: 489
 

Can you send more detailed photos of the outside of the cylinder? I'm suspecting that it might be a thermal store...


Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote



(@derek-m)
Illustrious Member Member
Joined: 5 years ago
Posts: 4425
 

Posted by: @myanthony
image

There would appear to be two electrically operated valves, is that correct?

Does the flow pipe from the heat pump connect between these two valves?

 



   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 5 years ago
Posts: 4425
 

@myanthony

It would appear that Hugh wishes to help, so rather than have too many 'cooks', I will leave you in his capable hands.

Best of luck in resolving your problems.



   
ReplyQuote
(@hughf)
Honorable Member Member
Joined: 4 years ago
Posts: 489
 

Posted by: @derek-m

@myanthony

It would appear that Hugh wishes to help, so rather than have too many 'cooks', I will leave you in his capable hands.

Best of luck in resolving your problems.

Cheers Derek 🤣 Just what I needed...

 


Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote



(@derek-m)
Illustrious Member Member
Joined: 5 years ago
Posts: 4425
 

You are more than welcome.

I prefer to work through problems in a systematic and logical manner, particularly when the person seeking help is new to heat pumps. I suspect that having a number of forum members throwing different questions at them could actually be counterproductive.

 



   
ReplyQuote
(@hughf)
Honorable Member Member
Joined: 4 years ago
Posts: 489
 

It's going to be a difficult one to diagnose just off photos... I suspect that the ashp is batch charging the thermal store - that all needs re-plumbing if it ever stands a chance of working properly. Shame I'm basically the other end of the country.

 


Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 5 years ago
Posts: 4425
 

This is one of the problems, you are arriving at conclusions without establishing the full facts.

 



   
ReplyQuote