Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant system tweaking.
Good Afternoon All,
As we are now entering into the cooler part of the year, I have started to investigate the settings on our heating further.
We have the following.
ASHP - VWL 75/6 A 230V S2. Sensocomfort VRC 720F downstairs, Sensocomfort VRC 92f upstairs. VR71 with gateway and VWZ AI VWL MB2 controller for the heat pump. Outside sensors also there for weather comp
Downstairs is Zone 1 - UFH with 4 zones. All controllers feeding into a microcenter EZC-12-4. Heat curve 0.7
Upstairs is Zone 2 - Rads. Heatcurve 1.2
It all appears to be working. Both upstairs and downstairs are in manual mode. Upstairs is temp controlled from the VRC92F, down stairs is being controlled by the individual room sensors, the VRC 720F is still there but doesn't directly control the heating downstairs.
Adaptive heat curve is ? Activated. Is this the best setup for what we have?
With the downstairs still set to heating rather than fixed temp, where does the system take its internal temp reading from, the VRC720F???
Basically, are we running the system as efficiently as we can? I know we are technically in the settling in period, and adjustments are ongoing, but does it look like we are doing everything correctly?
Thanks for all your assistance and knowledge, this site is brilliant.
Many thanks
Drew
assuming everything is vaillant, (you have used obscure nomenclature) the the rads should be compensated not fixed.
I suspect you are in installer configuration?
I can’t remember what the options are, but the zone needs to be assigned and activated obviously.
weather compensation with indooor modulation is optimum.. I would not select extended room control with a heat pump though
The only way to use heat gerenators optimally is with weather compensation, and constant running pumps..
turn the vaillant controls up and down, and but don’t turn off
Professional installer
Hi Alec,
Thanks for the reply. Sorry, everything is Vaillant apart from the UFH central unit, and the room stats down stairs.
Slowly getting there. Thanks everyone.
Drew
Posted by: @drew-paGood Afternoon All,
As we are now entering into the cooler part of the year, I have started to investigate the settings on our heating further.
We have the following.
ASHP - VWL 75/6 A 230V S2. Sensocomfort VRC 720F downstairs, Sensocomfort VRC 92f upstairs. VR71 with gateway and VWZ AI VWL MB2 controller for the heat pump. Outside sensors also there for weather comp
Downstairs is Zone 1 - UFH with 4 zones. All controllers feeding into a microcenter EZC-12-4. Heat curve 0.7
Upstairs is Zone 2 - Rads. Heatcurve 1.2
It all appears to be working. Both upstairs and downstairs are in manual mode. Upstairs is temp controlled from the VRC92F, down stairs is being controlled by the individual room sensors, the VRC 720F is still there but doesn't directly control the heating downstairs.
Adaptive heat curve is ? Activated. Is this the best setup for what we have?
With the downstairs still set to heating rather than fixed temp, where does the system take its internal temp reading from, the VRC720F???
Basically, are we running the system as efficiently as we can? I know we are technically in the settling in period, and adjustments are ongoing, but does it look like we are doing everything correctly?
Thanks for all your assistance and knowledge, this site is brilliant.
Many thanks
Drew
Hi, I've got a Vaillant so interested in responses to this.
One question I have is - can you have different heatcurves for different Zones? Wouldn't that confuse the ASHP or have I got that wrong (still learning). I've got two zones - but advice I've seen elsewhere is to just treat the house as one big zone.
This video may help you too
Andy
Hi Andy,
I know my controller shows two different curves. As I mention above we have UFH downstairs and Rads upstairs. Couldn't tell you how it adjusts to the situation where both zones are running though.
@andygo the heat pump or boiler works to the highest temperature..I have a vaillant install with 8 different curves!
A vaillant controlled electronic mixing valve lowers the temperature of the lower zones..
Professional installer
Hello again all,
So our system had been running for a few weeks as described above. The other morning I heard the unit running for a very long time. Out of curiosity I got up and checked the controller. I found the heat curve had adjusted itself for the rads upstairs to 0.5 from 1.2. Is this typical? I would have expected it to stay at above 1.0 all the time.
had anyone seen this before?
many thanks,
Drew
yes perfectly correct.. you really need to concentrate on the room temperature not what the pump does, you will find it disconcerting!
trchnicall the floating curve just reflects the characteristics of the building!
Professional installer
-
Heat pump done right first time? Installation in Kent.
3 weeks ago
-
How to Zone with a Single Room with UFH
7 months ago
-
UFH and ASHPs
11 months ago
-
Vaillant arotherm plus heat pump frost protection
1 year ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
1 year ago
- 26 Forums
- 2,586 Topics
- 60.2 K Posts
- 169 Online
- 6,908 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Anyone concerned about GivEnergy?
Keep trying with your installer since he’s at least awa...
By Judith , 4 hours ago
-
RE: Plug and play solar. Thoughts?
what little I know on the subject is (and all subject t...
By Judith , 5 hours ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 6 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Hi James Going through the bold bits: 1.) As far as...
By WesleyP1874 , 6 hours ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 6 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Unfortunately Mr Smith may need to adjust his expectat...
By JamesPa , 10 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 11 hours ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 13 hours ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 15 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 18 hours ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 18 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 1 day ago
-
RE: Forum updates, announcements & issues
A quick heads-up. We’ll be carrying out a major forum...
By Mars , 2 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 2 days ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
I read this thread from the beginning to its end.And th...
By LeJamaisContent , 2 days ago
-
RE: Water law settings... A year on
Yes it does Apart from the abbreviations! We're in ...
By Profzarkov , 2 days ago
-
My Immersun power diverter problems now they have ceased trading
I have had an Immersun unit for 15 years that happily w...
By pjcwood , 3 days ago
-
RE: To re-pipe or not to re-pipe? Moving from oil boiler to air source heat pump.
Hello @Penval unfortunately, now the winter is gone and...
By LeJamaisContent , 4 days ago
-
RE: Grant Aerona R32 – Summer, Winter mode & Setbacks
What are you envisaging doing throughout the day? Pers...
By JamesPa , 4 days ago
-
@batpred ok My energy delivered in kWh was a...
By JamesPa , 4 days ago
-
-
RE: Global Energy Systems Thurso ASHP
Hello @outlawuk sorry, I forgot about this, important:i...
By LeJamaisContent , 4 days ago