Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant Arotherm monobloc error f.788 - ASHP is not working!
@william1066 so my system did the experiment for me today.
I currently have a commissioned ASHP, the flow side goes to a 50L volumiser, then there is temporary shortcut (i.e. a bypass) back into the return side. I temporarily created demand so the ASHP has warmed up the water in the circuit and volumiser. the routes from the ashp's f+r circuit into the house are currently capped - there is no load on the ashp. the house is still on the boiler.
the graph starts when I got modbus working yesterday evening. RWT goes below 25 right at the start but nothing comes on. When Outside temp goes below 4C, the system switches the circulation pump on. But not the compressor. the lukewarm water in the circuit must be enough to satisfy the warmth needs of the outdoor unit. After that, the pump is leaving "off" gaps of 60 minutes then running for about 6-8 mins each time. I'm not sure what the "off" trigger is at the end of the "on" period. It'll be interesting to see how cool it gets before it puts the compressor on.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbankI'm not sure what the "off" trigger is at the end of the "on" period.
Probably just "x" amount of time
Hi,
I have the same Error F788 did you finally fix it?
Coule you please tell me Howell did you do?
thanks for tour help
@bobshopsupreme did you ever get this matter sorted out?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor Hello. Yes and no! The original problem was indeed a dead water pump, killed by contamination in the circuit and possibly the power cut during freezing conditions (we do have anti-freeze valves). It took two months to get a replacement part.
We have then had another 2 years of fun with shutdowns caused by low flow due to under-dimensioned pipes, and then we still have a contamination issue which seems to be coming from the radiators. At the moment the flow rate gradually decreases over several weeks until the system cuts out with a low flow error, and then is fine again after cleaning the filters. They are trying to find the right product to protect the inside of the radiators because whatever inhibitor they have in there at the moment clearly isn't working.
@bobshopsupreme very interesting. Do you have a buffer tank or is it an open zone?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor We have a 200 litre buffer between the hydraulic station and the radiator and underfloor heating circuits. The flow rate problem was due to undersizing of the pipes between the outdoor unit and the hydraulic station. Those pipes have now been changed and it now meets the >2000l/hr nominal flow rate when the filters are clean.
-
Vaillant arotherm plus heat pump frost protection
1 month ago
-
Heat pump done right first time? Installation in Kent.
3 months ago
-
Has anyone seen this problem before? Huge anticycling times
7 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
2 years ago
-
ASHP Reliability Poll - Hall of Fame vs Hall of Shame?
2 years ago
- 26 Forums
- 2,668 Topics
- 62.4 K Posts
- 381 Online
- 7,076 Members
Join Us!
Directory
Degrees of Separation
Latest Posts
-
There is NO MCB in the main consumer unit for the heat ...
By trebor12345 , 4 minutes ago
-
There's usually a group of people on the beach at Dover...
By Transparent , 9 minutes ago
-
RE: Daikin ESPAltherma and Home Assistant installation
Although I haven't used PlatformIO before and so am som...
By Majordennisbloodnok , 22 minutes ago
-
RE: GivEnergy inverter tripping due to over-voltage?
Thanks Tim. As before, there's too little data to mak...
By Transparent , 3 hours ago
-
RE: Plug and play solar. Thoughts?
MCS are inevitably going to be opposed to this because ...
By JamesPa , 5 hours ago
-
RE: Say hello and introduce yourself
@singlespeed potentially the first Haier heat pump on t...
By Mars , 16 hours ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
@l8again It seems you did very well. With our HG h...
By Batpred , 21 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
Just wondering how you went in the end? A guaranteed 40...
By Batpred , 21 hours ago
-
RE: Cooling with air to water heat pumps
Its really a non starter unless designed that way to st...
By dgclimatecontrol , 1 day ago
-
RE: Vaillant Arotherm Pro vs new Plus
That makes sense. If the heat transfer into a cylinder ...
By Batpred , 1 day ago
-
RE: What is the Heat Geek Guarantee?
Thanks, we also heard about the thermal store, to be us...
By Batpred , 1 day ago
-
RE: Growatt battery disconnected
Morning folks! I can finally let you know that I have...
By Eliuccio , 1 day ago
-
Sadly we also have rodent damage to the hot water syste...
By AliRam , 2 days ago
-
RE: MCS 2.0 - Changes in January 2025
I so recognise that. My first employer, which I worked...
By JamesPa , 2 days ago
-
RE: Outdoor Battery Solutions?
For us, adding a 16kwh battery means a heatpump can red...
By Batpred , 2 days ago