Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant Arotherm monobloc error f.788 - ASHP is not working!
@william1066 so my system did the experiment for me today.
I currently have a commissioned ASHP, the flow side goes to a 50L volumiser, then there is temporary shortcut (i.e. a bypass) back into the return side. I temporarily created demand so the ASHP has warmed up the water in the circuit and volumiser. the routes from the ashp's f+r circuit into the house are currently capped - there is no load on the ashp. the house is still on the boiler.
the graph starts when I got modbus working yesterday evening. RWT goes below 25 right at the start but nothing comes on. When Outside temp goes below 4C, the system switches the circulation pump on. But not the compressor. the lukewarm water in the circuit must be enough to satisfy the warmth needs of the outdoor unit. After that, the pump is leaving "off" gaps of 60 minutes then running for about 6-8 mins each time. I'm not sure what the "off" trigger is at the end of the "on" period. It'll be interesting to see how cool it gets before it puts the compressor on.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbankI'm not sure what the "off" trigger is at the end of the "on" period.
Probably just "x" amount of time
Hi,Â
I have the same Error F788 did you finally fix it?Â
Coule you please tell me Howell did you do?Â
thanks for tour help
@bobshopsupreme did you ever get this matter sorted out?
Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.
@editor Hello. Yes and no! The original problem was indeed a dead water pump, killed by contamination in the circuit and possibly the power cut during freezing conditions (we do have anti-freeze valves). It took two months to get a replacement part.
We have then had another 2 years of fun with shutdowns caused by low flow due to under-dimensioned pipes, and then we still have a contamination issue which seems to be coming from the radiators. At the moment the flow rate gradually decreases over several weeks until the system cuts out with a low flow error, and then is fine again after cleaning the filters. They are trying to find the right product to protect the inside of the radiators because whatever inhibitor they have in there at the moment clearly isn't working.
@bobshopsupreme very interesting. Do you have a buffer tank or is it an open zone?
Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.
@editor We have a 200 litre buffer between the hydraulic station and the radiator and underfloor heating circuits. The flow rate problem was due to undersizing of the pipes between the outdoor unit and the hydraulic station. Those pipes have now been changed and it now meets the >2000l/hr nominal flow rate when the filters are clean.
-
Has anyone seen this problem before? Huge anticycling times
4 months ago
-
Heat pump done right first time? Installation in Kent.
5 months ago
-
Vaillant arotherm plus heat pump frost protection
7 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
2 years ago
-
ASHP Reliability Poll - Hall of Fame vs Hall of Shame?
2 years ago
Currently viewing this topic 1 guest.
- 27 Forums
- 2,828 Topics
- 67.3 K Posts
- 2,619 Online
- 7,249 Members