Vaillant Arotherm monobloc error f.788 - ASHP is not working!
@william1066 so my system did the experiment for me today.
I currently have a commissioned ASHP, the flow side goes to a 50L volumiser, then there is temporary shortcut (i.e. a bypass) back into the return side. I temporarily created demand so the ASHP has warmed up the water in the circuit and volumiser. the routes from the ashp's f+r circuit into the house are currently capped - there is no load on the ashp. the house is still on the boiler.
the graph starts when I got modbus working yesterday evening. RWT goes below 25 right at the start but nothing comes on. When Outside temp goes below 4C, the system switches the circulation pump on. But not the compressor. the lukewarm water in the circuit must be enough to satisfy the warmth needs of the outdoor unit. After that, the pump is leaving "off" gaps of 60 minutes then running for about 6-8 mins each time. I'm not sure what the "off" trigger is at the end of the "on" period. It'll be interesting to see how cool it gets before it puts the compressor on.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbankI'm not sure what the "off" trigger is at the end of the "on" period.
Probably just "x" amount of time
Hi,
I have the same Error F788 did you finally fix it?
Coule you please tell me Howell did you do?
thanks for tour help
@bobshopsupreme did you ever get this matter sorted out?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Hello. Yes and no! The original problem was indeed a dead water pump, killed by contamination in the circuit and possibly the power cut during freezing conditions (we do have anti-freeze valves). It took two months to get a replacement part.
We have then had another 2 years of fun with shutdowns caused by low flow due to under-dimensioned pipes, and then we still have a contamination issue which seems to be coming from the radiators. At the moment the flow rate gradually decreases over several weeks until the system cuts out with a low flow error, and then is fine again after cleaning the filters. They are trying to find the right product to protect the inside of the radiators because whatever inhibitor they have in there at the moment clearly isn't working.
@bobshopsupreme very interesting. Do you have a buffer tank or is it an open zone?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor We have a 200 litre buffer between the hydraulic station and the radiator and underfloor heating circuits. The flow rate problem was due to undersizing of the pipes between the outdoor unit and the hydraulic station. Those pipes have now been changed and it now meets the >2000l/hr nominal flow rate when the filters are clean.
-
Vaillant arotherm plus heat pump frost protection
9 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
12 months ago
-
Has anyone seen this problem before? Huge anticycling times
12 months ago
-
ASHP Reliability Poll - Hall of Fame vs Hall of Shame?
1 year ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
1 year ago
- 26 Forums
- 2,271 Topics
- 50.8 K Posts
- 276 Online
- 5,933 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: My DIY Heat Pump installation
@temperature_gradient Building regs I had my initial...
By Polar bear , 4 hours ago
-
This is a plot from a Shelly EM monitoring the supply t...
By Ubert767 , 5 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Hi again all, Just to update on this... I've now ad...
By benson , 6 hours ago
-
RE: Request for feedback on where we're at with our quest to get an ASHP or ideas.
thanks, heatpunk looks great, being able to do the calc...
By giryan , 7 hours ago
-
RE: Is Your House Warmer Upstairs Than Downstairs?
Why arent you expecting them to make much difference. ...
By JamesPa , 7 hours ago
-
RE: Oil Boiler & Heat Pump Hybrid System
@paultheheating I wonder if you are being a bit pessimi...
By GrahamF , 7 hours ago
-
@toodles sounds good. I started with cosy but then plug...
By Eliuccio , 8 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It has been just over a year since we changed over to a...
By npru , 10 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
He showed me a photo of 5-10l/min. However a...
By Crimson , 11 hours ago
-
RE: Finding a Thermostatic Shower Valve That Works with Heat Pump Systems
@morgan I should just have written ‘Mea Culpa’ shouldn’...
By Toodles , 12 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
'We learn from history that we do not learn from histor...
By Lawrence Leask FInstR , 12 hours ago
-
Mitsubishi Ecodan FTC7 Legionella date set
I can set the number of days between Legionella cycles ...
By DRB01 , 17 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard Yes, I like the extra facilities that NetZe...
By Toodles , 18 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk downstairs rads are less prone to airlocks, you ...
By AgentGeorge , 19 hours ago
-
RE: My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
@editor thanks for highlighting my name. Yes I did get ...
By Chansug , 1 day ago
-
RE: balancing radiators with a mixture of different size pipework and a few undersize rads.
@editor Thanks for your input Mars. No I think the comm...
By baxtDave , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
We’re looking to expand our list of recommended list of...
By Mars , 1 day ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@transparent Along with the right workers, they can’t b...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I have just looked at my heat pump 'long interval' (27 ...
By cathodeRay , 2 days ago