Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Problems with Daikin 18 kW High Temp ASHP
Firstly, the description, it turns out that it is not an 18 kW heat pump at all, but more like 12 kW with a 6 kW so called ‘ backup heater’. So feel cheated by that to start with.
DHW, claims it can produce leaving water at up to 70 C, so DHW at say 60 should not be a problem, right? No, it cuts out at DHW 55. OK , not the end of the world and 55 is more than adequate but if you can set 60 ( you can set higher) it should be able to do it! No apparent reason for it to shut down. Disinfection cycle uses immersion ( ‘booster ‘ in Daikin speak) to get it up over 60.
Despite this, in general, it has been working well until the colder weather came along.
I now find that when ambient drops to 2 or 3 it starts to freeze up on the evaporator, and has to do a defrost cycle once an hour. This takes around 15 min, so it’s on for an hour , off for 15 min. It never reaches its set leaving water temp, so heating the house is suffering. And we haven’t had any really cold weather yet. I am sure it would be ok, it it could only last longer than an hour between defrost cycles. Are these things designed for our relatively humid winters as opposed to cold dry continental winters. Have I been sold a ‘pup’?
Has anyone else had experience of these units?
I can't comment on other aspects, but heat pumps do have to work harder at temperatures close to freezing with high relative humidity. This is reflected in Daikin's capacity graphs which show a drop in capacity at ambient temperatures from like 1-5C, then it increases below 0C before dropping off again as it gets really cold.
Defrost cycles could be worse if you have your flow temperature set to higher than it needs to be. Are you running it with weather compensation?
100% this heat pump is being used like a gas boiler. Turn down the flow temperatures and it'll stop icing up. It needs to be used in the heat pump sweet spot. My flow temperature yesterday was 32° - no defrost
Thanks, yes I am using weather compensation, it may be set a bit high at low temperatures as it never reaches the set value before being turned off by room thermostat controls ( when there isn’t the defrost issue). However it generally cuts out for defrost before it gets much above 50, and it needs to be at least that, so if I set it that low I would expect it to still need to defrost? It seems to be controlling on differential temp rather than leaving temp so I don’t think it would be working any less hard.
Where are you finding the capacity graphs?
@batalto It is being used in accordance with its instructions. Flow temp is a lot lower than it used to be with the gas boiler, but I doubt that 32 deg would get anywhere near heating the house. I have radiators, not UFH. It is set up for those. I will look at setting it lower than it is but I don’t think I have much scope to go lower than it is reaching before needing to defrost.
@bramshot I would just try knocking the weather compensation curve down a little bit. It'll cost less to run, probably have to defrost less, and if you're saying your flow temps never even reach what they're set up to run at, then your house can clearly handle lower temps than the heat pump is aiming for. You should wait 1-2 days after changing weather compensation settings before assessing if the changes have worked. The worst that's going to happen is you're a tiny bit too cold for a few hours, the best is lower bills, less stress on your heating system, and fewer annoying cycles.
On the capacity graphs, you can get them from this link https://daikintechnicaldatahub.eu/en-GB otherwise they'll be in the installer's manual, but I wouldn't worry about it too much.
@bramshot I've got rads. Honestly use some weather comp. You can go below 37° you'll be fine.
@oswiu I have reduced the temperatures, but I have already seen a defrost cycle as the ambient falls tonight. Even though the house can cope with the lower temperatures, surely it is at those lower temperatures that the frosting is occurring? It never gets to deliver the higher temperatures that were set. I don’t think reducing the setpoint reduces the demand on the heat pump, it is the actual temp and delta T achieved that is determining how hard it is working. I will however persevere and keep reducing the temp as I think it is the way to go, just not sure if it ( the heating) will be effective when low enough to prevent frosting.
Thanks for the chart location data, though like most Daikin info it is not easy to understand especially when the axis labels are messed up. This info is NOT in the installation guides etc that I have seen. Mine is an EPRA18DAV3, which is not specifically mentioned in those listed.
@batalto my rads are not oversized, as it is a High temperaure heat pump and supposed to work with ‘ normal’ sized rads. Are yours the same? Also an oldish house so not as well insulated as a modern one. Although the rads were surprisingly effective at lower temperature when the weather was warmer I really doubt that anything below 50 to 52 will do as ambient falls to zero.
Posted by: @bramshot@oswiu I have reduced the temperatures, but I have already seen a defrost cycle as the ambient falls tonight. Even though the house can cope with the lower temperatures, surely it is at those lower temperatures that the frosting is occurring? It never gets to deliver the higher temperatures that were set. I don’t think reducing the setpoint reduces the demand on the heat pump, it is the actual temp and delta T achieved that is determining how hard it is working. I will however persevere and keep reducing the temp as I think it is the way to go, just not sure if it ( the heating) will be effective when low enough to prevent frosting.
Thanks for the chart location data, though like most Daikin info it is not easy to understand especially when the axis labels are messed up. This info is NOT in the installation guides etc that I have seen. Mine is an EPRA18DAV3, which is not specifically mentioned in those listed.
You will probably still get frosting occurring on the Evaporator, but at less frequency as the LWT is lowered. This will happen in particular when there is low ambient temperatures, but above zero, and high humidity.
Remember that the refrigerant gas could be at -40C inside the Evaporator, so any moisture touching the outer metal is likely to freeze.
Are you controlling your system using weather compensation?
@bramshot my rads are all normal double type rads. Honestly I'd give lower flow temps a go. The worst case is you turn it back up. Low and long is the aim
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 532 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
I brought my old R407C water to water heat pump to the ...
By bobflux , 13 minutes ago
-
Its good kit the Midea and significantly cheaper, you w...
By ASHP-BOBBA , 49 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
Have you tried cutting the grid feed to see what actual...
By JamesPa , 52 minutes ago
-
Contractors pack for inta antifreeze valves are around ...
By ASHP-BOBBA , 52 minutes ago
-
RE: Renewables & Heat Pumps in the News
Critics and naysayers will be negative whatever the gov...
By JamesPa , 56 minutes ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 11 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 13 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 14 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 15 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 17 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 20 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 23 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 3 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 5 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 5 days ago