Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Performance in the current cold snap…
Posted by: @derek-mPosted by: @hughf@derek-m single heat pump, just run on weather comp, no stats, no setback.
The Carel platform that my heat pump is built on allows full tuning of the PID settings, along with full control of the compressor ramp speeds. It’s close to maintaining setpoint, but I’ve still got some work to do. I’d like to deal with the initial overshoot next, I think I’ve got the oscillation damped quite well.
When it’s around freezing outside, it runs happily for a long period of time, it’s dealing with the overshoot when it’s cycling that’s the next area of tuning that needs my attention.
I suspect that it will not be possible to accurately control the LWT during milder weather conditions, simply due to the fact that the heat pump will be starting to operate outside its control envelope. i.e. it cannot turn-down any further.
As far as controlling IAT is concerned this should not be a major issue, though it could take some time to optimise for maximum efficiency.
Out of interest what are your PID settings?
It is my suspicion too, that in milder weather, we are simply oversized. I didn't take into consideration the possibility that the ACH value used in the heat loss spreadsheet (and by heating engineer) could be considerably higher than we actually achieve.
The fact that it was tracking the requested setpoint to within 0.1 degree during the last 2 weeks of freezing weather leads me to think my PID settings aren't a million miles off.
At the moment they are: P = 5 deg. C, I = 50 secs, D = 0 secs.
The controller also allows me to open up the overshoot window, which gives headroom for compressor rampdown - currently set to 5 degrees. I can't remember the rampdown settings though, it's specified in Hz/sec inside the Power+ inverter settings.
To comment on the original question in the thread title - I was away for a lot of the 2 week freeze, but the residents reported stable internal temperatures (21-22) 24/7 and there were no issues with defrosting, even with our limited system volume.
Whole house electric consumption was running around 50kWh/day - all electric house now.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 2,493 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
@cathoderay I started to record oil usage per month on ...
By ian33a , 53 minutes ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 4 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 9 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 1 day ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 3 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 4 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago