Commencing on an ASHP Installation Process

37 Posts
5 Users
7 Reactions
952 Views
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2470
 

Posted by: @sheriff-fatman

Posted by: @jamespa

What value of air changes per hour is assumed?

It varies by room, but the conservatory is assumed at 2 per hour, as is the kitchen, hallway and landing.

Living room and upstairs office are assumed at 1.5, bedrooms at 1, and bathroom/toilets at 3.

Two calculations both use similar figures, with the exception that one of them assumes 2 for the ensuite and downstairs toilet, rather than 3, so I assume they have some sort of common reference point to estimate this.

One of the calculations excludes the conservatory, so I only have one calculation showing a figure for this.  Within my replicated spreadsheet I can manipulate the figure and each additional digit adds about 400W to the conservatory ventilation heat loss.

 

I think those are pretty much the standard figures that used to be quoted in mis3005-d (which now instead references a BS EN standard that I have yet to read)

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Page 4 / 4
Share:

Join Us!

Trusted Installers

Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.

✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available

👉 Find your installer now!

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security