Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
More Samsung weather compensation oddities (8kW Gen6)
Now that the unseasonably mild weather has passed (only 2 nights below 10C outside in the first half of November, now its just over 2C in the middle of the day) I have been able to start fine tuning my Water Law settings. I am seeing some unexpected behaviour and wonder if anyone else has seen anything similar or can offer any advice?
Everything was going well with the TW2 (Samsung's name for water temp leaving the pump) nicely tracking the Water Law Target and with 24hr running I was getting a good steady indoor temperature. Here is the steady state with a DHW cycle in the middle:
However, from Sunday afternoon the TW2 has mostly been tracking below the Water Law Target by around 2C, however, it is not consistent. The OAT has been between 4C and -2C so has reached the point where defrost cycles are occurring (they appear to be running normally and are clearing all the accumulated frost). Sometimes the TW2 will recover to the target level after a cycle, either to fall away again or stay at the target, but will only reach the lower level after a subsequent defrost. The indoor temperature is now lower than we want and this is making it very difficult to tune the settings.
The pump is not running at maximum and it is outputting around 2kW most of the time, except for the DHW cycles:
The compressor frequency is around 30% of maximum although it is varying a lot between 16Hz (where it normally sits when holding a steady TW2 on the target) and 21Hz - this is producing an annoying variation in the sound like someone continually revving a car in the drive.
Current WL settings are:
- 201* Outdoor temperature for Water Law: LOW 10C, HIGH -15C
- 202* Water out temperature for Water Law: Low Target 33C, High Target 37C
- 2041 Heating Water Law for Auto Mode: WL1-Floor
- 2091 External Thermostat Application #1 (Floor): Use(Signal ON/OFF) or WL Interlink OFF( Water Pump2)
The pump is a 8kW Samsung Gen 6 connected to a Joule Cyclone Smart Plumb (including buffer tank) feeding underfloor heating in a 100m2 new build bungalow. The UFH is running with all the zone valves open except for the bedrooms which have remained closed for all these tests.
All the data values are captured from the Samsung NASA communications link, so they are the actual values reported by the pump and controller.
Any thoughts or ideas would be greatly appreciated.
Thanks
Stuart
Posted by: @sjnThe pump is a 8kW Samsung Gen 6 connected to a Joule Cyclone Smart Plumb (including buffer tank
A few questions might help point us in the right direction:
Is the buffer tank plumbed 2 port or 4 port?
Is there a secondary pump on the emitter side of the buffer tank and how is it set up?
What is the indoor temperature?
I note that there is a peak in output just before 1600 each day, is that when your DHW heats up?
A 100 sq m new build shouldn't need anything like 8kW, more like 4kW, so that may be a factor. To my surprise my 7-8kW house (measured figure) has been running all day at 4kW and is toasty, not sure why (perhaps because the exterior of the fabric is only slowly cooling down??).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaA few questions might help point us in the right direction:
Is the buffer tank plumbed 2 port or 4 port?
It is a 4 port buffer.
Is there a secondary pump on the emitter side of the buffer tank and how is it set up?
Yes, there is a secondary pump on the UFH return to the buffer.
The initial install included yet another pump on the secondary at the UFH manifold as directed by the Joule design. This was always on when there was any call for heat, even if the secondary circuit valves were closed for a DHW cycle so it was disconnected from power at the last service. It is still freewheeling in the secondary circuit but the service people are here again on Monday to remove it totally.
What is the indoor temperature?
We were getting a nice 22C but it has dropped to just above 20C since this issue started.
I note that there is a peak in output just before 1600 each day, is that when your DHW heats up?
Yes. This gives us enough DHW for the full day.
A 100 sq m new build shouldn't need anything like 8kW, more like 4kW, so that may be a factor. To my surprise my 7-8kW house has been running all day at 4kW and is toasty, not sure why (perhaps because the exterior of the fabric is only slowly cooling down??).
Agreed. I think the system was over specified at 8kW. It certainly struggled in the shoulder months as it can not modulate below around 2kW which seems to be too much for when we are anything over OAT of 8C. It short cycles if I try a flow temperature of anything below 32C.
I was expecting everything to be fine when the heat demand increased but with it not holding the target temperature I don't think the UFH can emit enough energy.
OK. It does sound like its possibly the system not the heat pump, thats limiting the output, and since room temp has dropped then there quite possibly is a problem. The plot of compressor frequency makes me think its trying to heat up the FT but getting stopped by something
There are a few things to consider
Is the UFH able to emit enough heat? Hopefully it was designed to emit enough, but at what flow temperature? Do you know? Do you know what temperature the flow to the UFH is actually at? Unless the buffer tank is well set up (which statistically is very unlikely indeed) the flow to the UFH is likely to be ~5C below the flow from the heat pump (which BTW is costing you 10%).
Is the secondary pump running fast enough to take the heat away (can you measure the temperatures on any of the emitter side ports?).
Have you got any secondary controllers (thermostats, homely etc) limiting output on the emitter side. Also I think (but am not sure) you may have selected a value for 2091 which means that the WL controls the flow temp but the internal sensor in the controller will switch it off once it reaches set temp - can you confirm the value of 2091. What is the target room temp set to on the Samsung controller and where is the controller located?
These are possible explanations based on what you have said, although the oddity is that its not holding the target flow temperature, so maybe there is a genuine fault in the unit itself (presumably its still under warranty?)
Its very likely the case that you ideally want the buffer out, or replumbed as 2 port either in the return or the flow. Any idea why it was fitted?
If its not obvious and its still under warranty then I would probably get the installers/Samsung to have a look. The fact it isn't reaching target FT is a bit odd and I dont have an immediate explanation (others might).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa - thank you for your comments.
The plot of the compressor frequency is very interesting. Before I had the instrumentation sorted out I was always curious about the continual revving up and down sound as if the pump was "hunting" for a stable point so it was good to see it in the data. It made me think of badly tuned PID controllers that I have worked on in control systems in the past. I was pleased to see the stable state that the system achieved over the weekend with just the occasional change from around 16Hz.
The buffer and secondary pump set up does appear to be reasonable with around a 1C difference between the reported TW2 from the pump and UFH flow into the manifold (measured using a ds18b20 sensor strapped on the outside of the flow pipe). For example, early this morning:
In this next plot the dT between the UFH flow and return for the same period shows the difference between when the TW2 is at target and when it is low. My rough calculations are that this equates to the UFH emitting around 2kW at target and 1.4kW when low.
Unfortunately I do not have any detailed design data.
The 2091 setting on the Wired remote controller is "Use(Signal ON/OFF) or WL Interlink OFF( Water Pump2)" - I think that's the value 2 described in the manual.
The system is set to use an external thermostat. There are individual stats in each room which go to a wiring centre. When a thermostat calls for heat, the manifold valve for the room is opened and the external thermostat input to the Samsung controller is activated. Based on advice from this site, I have removed the manifold valve actuators for all but the bedrooms meaning that the UFH for the rest of the house is one open zone. I can then call for heat using one of the public room thermostats. The one I am using is set to 26C so is continually calling for heat. Sorry if that's all a bit complicated but I am in mid trial stage here.
Like you, I think that it would be better if the buffer was configured as a 2-port. My biggest problem is getting anyone around here to work on it. The visit on Monday is them just getting back to remove the redundant pump that was identified as an issue during the service way back in May.
The pump is still under warranty so that may be the way to go. It is good to have some ideas to talk to the service people about.
Many thanks again for your thoughts.
OK
I must admit Im a bit stumped.
Reducing it to its basics, the heat pump does not appear to be reaching the flow temperature you have told it to reach ,and there is no particular evidence from the return temperature that the 'system' is telling it not to. If it were consistently reaching it then cutting back when the return temp was rising, I would say its the feedback from 'the system', but that's not what I observe in your plots. If the Gen 6 had an 'adaptive' mode (where the system learns your house response) then I might say it was that, but I don't think it does. If you had Homely, I would say it was that, but you presumably don't. Basically I think your system has a controller which is supposed to achieve a FT and doesn't, but doesn't overshoot either and clearly isn't maxed out. Your 'poorly tuned PID controller...hunting' does indeed seem relevant.
I would be tempted to present it to the service people in these simple terms (leaving out any discussion of PID controllers, which they likely as not won't understand). Perhaps, if you have time, do some experiments where you somehow force the target FT to be different, in particular higher, and see if you observe the same behaviour.
One thing to check, although I would be surprised if its the issue based on what you say, I think that the Samsung has an easily accessible 'FT Offset' setting, I presume that is set to zero.
Others, familiar with Samsung, may have more insight
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thank you for your helpful comments. It has been very useful for me to write all this down and for someone else to sanity check it in case I had missed something obvious.
You are correct that I have no smart controller like a Homely and that the Gen 6 appears to be a straight, FT target control system. Yes, the FT Offset is set to zero.
I will try some more experiments over the next few days and discuss it with the service people coming on Monday. We can take it to Samsung support if they have no further thoughts.
Many thanks again
Stuart
Posted by: @sjnI will try some more experiments over the next few days and discuss it with the service people coming on Monday. We can take it to Samsung support if they have no further thoughts.
Sensible IMHO, varying the target FT might give a clue!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 394 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 7 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 8 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 8 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 11 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 17 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 17 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 1 day ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 1 day ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 2 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 2 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago