Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Minimum and Zero Disrupt Heat Pump Installations

38 Posts
9 Users
14 Reactions
1,418 Views
(@l8again)
Eminent Member Member
Joined: 4 months ago
Posts: 23
Topic starter  

@batpred Have a read of this if you haven’t read it already:

https://energy-stats.uk/heat-pump-cycling/

Heat Geeks told me that another factor to take into account is de-icing when it comes to heat pump size.

 

 



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4864
 

Posted by: @l8again

Heat Geeks told me that another factor to take into account is de-icing when it comes to heat pump size.

 

That's true.  Some heat pumps quote capacity including defrost, others don't, installers need to take this into account.

UK is more or less worst case because it's damp and we generally design for just below zero.  So defrost occurs very close to the point where demand is highest.  In colder countries where the design oat is lower, defrost occurs when the demand is quite a bit less than max so doesn't really matter in terms of pump selection.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
2
ReplyQuote
Batpred
(@batpred)
Prominent Member Member
Joined: 1 year ago
Posts: 874
 

Posted by: @l8again

@batpred Have a read of this if you haven’t read it already:

https://energy-stats.uk/heat-pump-cycling/

thanks, that was very useful reading. 

It seems grant pumps can modulate more than most.

I am still wondering whether a 5kw Vaillant would do, which would offset the slightly higher Vaillant cost, when considering the sensocomfort controls and a 7kw model. 

 


8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4864
 

Posted by: @batpred

I am still wondering whether a 5kw Vaillant would do, which would offset the slightly higher Vaillant cost, when considering the sensocomfort controls and a 7kw model. 

Based on what I remember of what you have said I think quite possibly yes. I took a similar risk with the 7kW and dont for a moment regret it.  If it had turned out wrong I would just have used some supplementary heating on the few days it matters (until the Gulf Stream collapses!). 

Do you by any chance have half hourly (or even daily) meter readings.  They would give a relatively high level of confidence than the crude calculation based on annual consumption.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Batpred
(@batpred)
Prominent Member Member
Joined: 1 year ago
Posts: 874
 

Posted by: @jamespa

Do you by any chance have half hourly (or even daily) meter readings.  They would give a relatively high level of confidence than the crude calculation based on annual consumption.

We are with Octopus Energy for gas as well so I can pull the 30 mins data. I am not sure how far back I can go, but I am attaching 2yrs. Curious about what it says.. The last year is with the current insulation..


This post was modified 3 weeks ago by Batpred

8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4864
 

Hopefully you can read this.  The various tabs in the xlsx show average power over 3, 6, 12, 24 hrs.  If you can get average temp or degree days for your location you can plot vs one of these which will give you more info.  The pictures are the plots from your data which appear in the spreadsheet.

The file 'Measured consumption - Copy' is my data for comparison.

 

image
image
image
image

This post was modified 3 weeks ago 4 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
1
ReplyQuote
Batpred
(@batpred)
Prominent Member Member
Joined: 1 year ago
Posts: 874
 

Posted by: @jamespa

Hopefully you can read this.  The various tabs in the xlsx show average power over 3, 6, 12, 24 hrs.  If you can get average temp or degree days for your location you can plot vs one of these which will give you more info.  The pictures are the plots from your data which appear in the spreadsheet.

Thanks, I think most of the 10kW peaks at the 3hr graph are since we have the boiler on setback overnight, which is followed by a surge in the early hours. We would not have such a low setback with an ASHP. But there are a few cold days where power used is above 7kW for more several 3 hour periods. 

From the below table of Vaillant heat pumps, if the external temperature is -3C, a 5kW boiler would deliver 6.8kw at a 35C flow. Tempting to get a simple 5kW, but perhaps we need a 7kW pump?

image

The first pre survey quote we can actually consider calculated a 7.1kW @ -2C and used a 45C Flow Temp at -2C 

 


8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4864
 

Posted by: @batpred

From the below table of Vaillant heat pumps, if the external temperature is -3C, a 5kW boiler would deliver 6.8kw at a 35C flow. Tempting to get a simple 5kW, but perhaps we need a 7kW pump?

You need to make an allowance for defrost, perhaps 10-20%.

That said I would also be tempted to go with the 5kW based on this data.  Before coming to a conclusion I would definitely plot 24 hr consumption vs degree days/average OAT and work out for myself what I would do on coldest days if it turns out to be undersized, and whether I am truly happy with that.  Otherwise I would go with 7kW which you anyway may not get a choice over because I think you might struggle to convince an installer.

The other things to consider before considering 5 and given its so marginal are

  • How old is your gas boiler and what temp do you run it at (affects efficiency), whats the current heating pattern, is the house adequately warm?
  • How can the measurements be reconciled with the survey, is it wrong fabric assumptions, ventilation loss or its impossible to reconcile?

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Batpred
(@batpred)
Prominent Member Member
Joined: 1 year ago
Posts: 874
 

@jamespa 

Thanks, that is a good point, the installers would be concerned about it. Plus there´s little for them to gain by taking the risk with 5kW. 

My main concern is whether a 7kW would cycle too much in warmer weather. But reading energy stats etc, it seems that the Vaillant algorithm manages to avoid it.

And of course, most importantly, it will be outlast the gulf-stream collapse.. 😀 

Of course that after 7 years, we should expect a growing argument about lifetime, etc... 


This post was modified 3 weeks ago by Batpred

8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4864
 

Posted by: @batpred

Thanks, that is a good point, the installers would be concerned about it. Plus there´s little for them to gain by taking the risk with 5kW. 

My main concern is whether a 7kW would cycle too much in warmer weather. But reading energy stats etc, it seems that the Vaillant algorithm manages to avoid it.

True (first sentence)

Thats the reason to consider the 5kW (second sentence).

See my previous email for suggestions/questions if you wished to take the analysis further.  At this stage its up to you (or your installer!)

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Batpred
(@batpred)
Prominent Member Member
Joined: 1 year ago
Posts: 874
 

Posted by: @jamespa

Posted by: @batpred

From the below table of Vaillant heat pumps, if the external temperature is -3C, a 5kW boiler would deliver 6.8kw at a 35C flow. Tempting to get a simple 5kW, but perhaps we need a 7kW pump?

You need to make an allowance for defrost, perhaps 10-20%.

That said I would also be tempted to go with the 5kW based on this data.  Before coming to a conclusion I would definitely plot 24 hr consumption vs degree days/average OAT and work out for myself what I would do on coldest days if it turns out to be undersized, and whether I am truly happy with that.  Otherwise I would go with 7kW which you anyway may not get a choice over because I think you might struggle to convince an installer.

So our heat loss survey came up at 5.1kW on the coldest -2C day. The installer surveyor is still recommending the 7kW Arotherm. I had a look at https://energy-stats.uk/heat-pump-cycling/, the lower modulating would is seen as 2.2 for the 5kW vs 3.2 for the 7kW. Anyway, the 5kW could help bring the outlay below the budget ceiling...

The Grant could be cheaper as it is imported from countries where standards are not as strict as in our region?


This post was modified 2 days ago by Batpred

8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
(@l8again)
Eminent Member Member
Joined: 4 months ago
Posts: 23
Topic starter  

@batpred As my installation survey was carried out under the HG assured warranty scheme, my installer didn’t get much say as to the size of the heat pump. What I can say is that with no radiator changes, the HG survey was looking at a 5kW Valliant with a SCOP of 3.7. I elected to go for some radiator changes based on running my boiler at 50C for past 2 years. These radiator changes increased the minimum SCOP to 4 based on a 7kW Valliant. My predicted heat loss is 5.9kW at -3C.

A month or so on my system has stabilised on a 0.2 heat curve with an internal temp of 19.7C. All radiators fully open in Weather Compensation mode manual with room temp mod ACTIVE. Yes, I do get HP cycling: 338 cycles with just over 200 hours of operation. Having the heat pump cutout temperature set at 14C seems to be working well. So far in May, the heat pump has consumed 50kWh of electricity to cover heating; hot water and cylinder disinfection. I don’t have heat pump monitoring but looking at a similar sized heat pump (SCOP4.5) in my location which does have live monitoring, my recorded performance is closely matching it - particularly in respect of flow temps; daily usage and costs.



   
ReplyQuote