MELcloud scheduling misbehaviour
I am aware that there are other threads discussing the shortcomings/confusion caused by the ability to set time schedules on both the Ecodan FTC wall box and the MELcloud app, but I think this warrants a separate thread.
I use MELcloud to set the following winter time schedule, viz:
0500 - 2200: 21C
2200 - 0500: 17C.
Pretty simple you would think. About 98% of the time it works fine. But seemingly at random it fails either to set back the temperatiure in the evening or to advance it in the early morning.
About 5 days ago we realised the house was too warm and it had stayed at 21C all night. This morning I woke at 0700 and realised the house was cold - still set at 17C.
Has anyone else seen this behaviour? For the avoidance of doubt, I never use the FTC wallbox to control the schedule, but I do wonder if a setting there is interfering with the MELcloud schedule in some way.
Mitsubishi Zubadan 14kW with Mixergy 210l DHW in 220m2 barn property. 24 solar panels = 9kWp with GivEnergy 5.0kW Hybrid inverter and 19kWh GivE batteries. Jaga Strada fan-assisted rads throughout. Landvac vacuum glazing/triple glazed windows.
I too use MELcloud exclusively to schedule temp changes and over night set back. Yes, very occasionally it misses a beat and the times that I have been able to pin it down were mini and intermittent internet connection drops. I put that down to the quality of the wet string that Openreach use to get what they laughingly call an internet service to the back of beyond. It is equally possible the failure may on occasion be the signal from Mitsubishi. It has never been too much of an issue to follow up.
@downfield my understanding is that you can have a maximum of 4 heating time slots on the FTC and that it does not rely on the internet to send the instructions to the Ecodan.
So, if your requirement is only 2 time slots, then using the FTC would avoid any risk of losing an instruction to internet failure.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
19 Jan 2026 - added Sigenstor 10 battery
@richard24738 Richard, last winter I was on weather compensation and without any set back other than on Tapo SRV's in some unused bedrooms. Over the summer I changed the buffer tank to volumiser, introduced a Mitsu wireless controller and changed to Adaptive control. I then introduced HavenWise and this is on 24 hrs.
So probably too many changes at one time and I am considering going back to basics. In this respect, could you please remind me if you can not only set a time, but a setback temperature on FTC? I only recall setting operating times and not temperatures in the set times
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
@davidalgarve Hi David. On my Ecodan I use Adaptive which allows up to 4 heating time slots to be specified on the FTC. For each time slot you enter the required room temperature. Set back is as simple as setting a time with your set back temperature
So in my case I currently have 3 settings 00:00 18c, 04:00 21c, 13:00 22c. Just to explain, the 22c at 13:00 is active until the next instruction at 00:00.
The timings are influenced by the Octopus Cosy "Cheap periods" and that we are home all day and like to be warm.
I have used 5 timings on Mel-Cloud in the past when playing around with the cheap cosy sessions but found it didn't make much difference and we did have an internet issue which meant that the pump didn't receive its instructions. FTC avoids internet issues.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
19 Jan 2026 - added Sigenstor 10 battery
@richard24738 Thank you very much for the info. I only had a short time on Adaptive before starting a trial with HavenWise so had not tried this.
I didn't recall, in previous years, having the ability to select temperature when I was using Weather Compensation (without the wireless controller).
As much as I would like to, I can't play around with it at the moment because I am having some difficulties with HavenWise control
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
@davidalgarve I don't think you have as much control with weather compensation. Definately not setting a room temperature as temp is from the curve but not sure about timing.
I did try Havenwise for a while and found it useful and the guys really helpful.
However, I wasn't ready to give up control at that point and had a bit of difficulty understanding the logic behind when it wanted to heat the hot water. It started in the afternoon (logically as its warmer) but my requirement was for early morning showers which meant that the water had about 17 hours to cool down with hand washing, etc.
The solution was to up the required water temperature which didn't sit right. It may have been more economical but didn't feel right and gave the risk that someone could draw the water during the afternoon or evening and we were left with cold morning showers. Of course things may now have changed with their algorithms.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
19 Jan 2026 - added Sigenstor 10 battery
Posted by: @richard24738@davidalgarve I don't think you have as much control with weather compensation. Definately not setting a room temperature as temp is from the curve but not sure about timing.
I did try Havenwise for a while and found it useful and the guys really helpful.
However, I wasn't ready to give up control at that point and had a bit of difficulty understanding the logic behind when it wanted to heat the hot water. It started in the afternoon (logically as its warmer) but my requirement was for early morning showers which meant that the water had about 17 hours to cool down with hand washing, etc.
The solution was to up the required water temperature which didn't sit right. It may have been more economical but didn't feel right and gave the risk that someone could draw the water during the afternoon or evening and we were left with cold morning showers. Of course things may now have changed with their algorithms.
Without disagreeing with anything you've said there, @richard24738, there is one thing I'd point out.
When I look back historically, our DHW accounts normally for between 1.5 and 4 kWh leccy (absolute max was 11.2 kWh) and an average of 3kWh. Given any energy efficiency savings will be based on minimising heat loss through the cylinder's insulation and given most cylinders are pretty efficient these days at retaining heat, even if my setup isn't optimally efficient, the potential saving is never going to be bank-breaking.
Our setup triggers a DHW heating cycle (up to 50 degC) whenever the hot water temperature drops by more than 8 degC. We have some prohibited times for DHW heating so that we can guarantee the water's reheated after the last shower of the evening (and so is hot enough for someone to have a shower in the morning), that no reheating happens during the expensive part of the morning or afternoon and that the DHW reheating doesn't interfere with the heat pump's recovery from a mild setback overnight to daytime room temperatures. Whilst it may not be absolutely the most efficient financially it definitely is the most effective for the household and the cost from any loss of efficiency is only a handful of pence.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@richard24738 We also want hot water for 7:00am showers and we have a cheaper tariff from midnight until 7:00am.
Havenwise choose to heat the water just after midnight rather than my previous choice of 5:00am.
Our tank is in an outside "pumproom", so how do you decide between my choice of minimising the time when losing heat from the cylinder and their choice of accepting the heat loss and operating the heat pump more efficiently at, possibly, higher ambient temperatures that might occur at midnight as opposed to those at 5:00 am?
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Posted by: @richard24738Definately not setting a room temperature as temp is from the curve but not sure about timing.
Just catching up with this thread as I am still having problems.
A question on the above comment, though: I thought that the WC curve defined the flow temp, which is independent of the room setting?
I use MELcloud to set a room temp of 21C for 18 hours and currently the WC curve shows a flow temp of 35C or so, return about 32C.
This works 95% of the time, but occasionally there is no step up in the a.m. or no set back at 2200.
Mitsubishi Zubadan 14kW with Mixergy 210l DHW in 220m2 barn property. 24 solar panels = 9kWp with GivEnergy 5.0kW Hybrid inverter and 19kWh GivE batteries. Jaga Strada fan-assisted rads throughout. Landvac vacuum glazing/triple glazed windows.
This issue continues - 3 days ago no heating on at 0500 and so on waking I had to increase the room temp on the MELcloud app to get the HP spinning.
So I contacted MEL support and got the following response:
You need to run the system in Auto Adaption mode for the target temps. set on schedule to be achieved.
Please call our homeowner helpline on 0161 866 6064 to help with this.
I find this difficult to understand, so went back with
I tried auto adaption a while ago and it reduced the COP. Can you explain a bit more why the WC setting won’t follow the time schedule? It doesn’t seem to make sense and works 90% of the time. Why does it suddenly fail?
This got the same unhelpful response:
Auto adaption mode is the only heating mode programmed to hit target temperature set on the schedule.
Please call our homeowner helpline on 0161 866 6064 to help with making sure your system is set-up correctly.
Is this correct? If so, what's the point of the WC option?
And why does it work fine most of the time?
Mitsubishi Zubadan 14kW with Mixergy 210l DHW in 220m2 barn property. 24 solar panels = 9kWp with GivEnergy 5.0kW Hybrid inverter and 19kWh GivE batteries. Jaga Strada fan-assisted rads throughout. Landvac vacuum glazing/triple glazed windows.
@downfield I wonder if it is the MELCloud app that is the problem? It is not the greatest bit of software. I was using weather compensation all last year with the operating times set on the FTC 6 rather than the MELCloud app and it never failed. The responses you received were disappointing and suggested that they did not read your question.
Out of interest what CoP were you getting on Auto adopt? With Havenwise operating on Auto adopt, I am now getting average of 3.4 but appreciate your AAT’s are lower than mine
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
- 27 Forums
- 2,484 Topics
- 57.3 K Posts
- 461 Online
- 6,196 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Warranty Repairs- An Un Eddi fying experience!
@editor Did you have one of the really old ones with th...
By swwils , 2 hours ago
-
RE: Brine pump error message on Thermia 8kW ground source heat pump system
@schanna I’ve just DM’d you a potential company that’s ...
By Mars , 2 hours ago
-
RE: Tell us about your Solar (PV) setup
Actually not that far, however, the cost of my...
By upnorthandpersonal , 2 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@petch I’ve not come across anyone yet that’s used thes...
By Mars , 2 hours ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
Steady green means that the pump is running full speed....
By smsm1 , 3 hours ago
-
RE: Help…my NIBE heat pump has faulted again!
@jamespa I meant to say I attached the report from the ...
By Fiona , 4 hours ago
-
RE: Rate the quality of your heat pump design and installation
I don’t have the strength to post this tonight, but I’v...
By Mars , 4 hours ago
-
Vaillant app under reporting flow temperature
Our Vailllant 5kW heat pump is working well and the hou...
By Bengeo , 4 hours ago
-
@boycey, in your scenario if you use Melpump to change ...
By Majordennisbloodnok , 8 hours ago
-
RE: A Smarter Smart Controller from Homely?
Yep- already done that....nothing novel as such but som...
By benson , 8 hours ago
-
RE: Help needed to adjust weather compensation on Vaillant air source heat pump
I am in the fortunate position of having independent mo...
By MartinRobinson , 9 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@swwils Similar here, though it has been very mild. I...
By KevH , 11 hours ago
-
RE: Home energy storage & battery register
@toodles thankfully we have a range of tariffs to meet ...
By TechnoGeek , 13 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@editor thanks Mars! I'll contact them.
By kevinmc1970 , 14 hours ago
-
RE: Noisy Grant Aerona 3 13kW ASHP question
@heymikey thanks for the update and sorry to hear that ...
By Mars , 1 day ago
-
RE: Heat loss calculations and how they work in conjunction with heat pump sizing
@jamiejones85mespa your comments are spot on with my th...
By AgentGeorge , 1 day ago
-
RE: The good, the bad and the not that great – my heat pump installation
Must of knocked a load of crud through when they added ...
By Burtis , 1 day ago
-
@mkz, yes I have other installers... can you please sen...
By Mars , 2 days ago
-
I should add that our survey came up with a heat loss o...
By MartinRobinson , 2 days ago
-
RE: Optimising LG Therma V R32 using AI
@bontwoody oh dear! ... but as you say.. I suppose th...
By Tim441 , 2 days ago
-
RE: Volumiser required on Grant R290 air source heat pump?
@judith Indeed it's similar to the UK. It has to be an ...
By Patrick , 2 days ago
-
RE: Say hello and introduce yourself
Underfloor hydronic, powered by both the heat pump and ...
By upnorthandpersonal , 2 days ago
-
RE: PV export revenue and HMRC
That makes sense. They are companies that are on market...
By Batpred , 2 days ago
-
RE: R290 Heat Pump and Foundation Air Bricks
I have been having fun and games whilst getting surveys...
By petch , 2 days ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
@ashp-bobba brill thanks again!
By cmartinbwmba , 3 days ago