Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Low temperature heating - does it feel like heat is more evenly distributed?
@toodles Yes I have noticed a more even heat distribution since installing my heat pump (12Kw Samsung Gen6). I have a particular problematic room (also identified on the heat loss survey) which is heated using a vertical radiator. With the heat pump heating characteristics of low temperature and longer run times per cycle, this vertical radiator performs better, giving off more heat and the room does not get so cold. It now settles at approx 1 deg cooler than the remainder of the house, however with the oil boiler it was 3+ deg cooler.
As I have been fine tuning my system this Winter, I have now acquired a deep understanding of my smart thermostats behaviour (Honeywell T6R+HW). When the thermostat learns its controling the heat pump, the thermostat demands heat in each cycle ( 3 cycles per hour, 1 cycle is max 20mins) for approximately 13 minutes. When the thermostat learns the oil boiler is running (I have a bivalent system), the heat demand per cycle is reduced to about 5 - 6 minutes.
I am not a thermodynamics expert but I think because of the longer run times of the heatpump the heat output of the rads gets more chance to circulate the room before cooling. With the short 5 - 6 minute blast from the oil boiler, I am thinking the rad output cools down before it has chance to circulate the room properly?
With my vertical radiator mentioned above, due to the oil boiler not running long enough, the rad does not get chance to heat properly and hence the room is a lot cooler.
As far as heating rates, I have found the thermostat heats at approx 0.5 degree per hour regardless of heat source. The advantage I am finding with the heatpump is the lower longer heat output does not give you the chance to feel any sudden temperature cooling like the high short bursts of the oil (or gas) boiler and the rads are warmer longer so the heat distribution is better?
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
Posted by: @technogeek@toodles Yes I have noticed a more even heat distribution since installing my heat pump (12Kw Samsung Gen6). I have a particular problematic room (also identified on the heat loss survey) which is heated using a vertical radiator. With the heat pump heating characteristics of low temperature and longer run times per cycle, this vertical radiator performs better, giving off more heat and the room does not get so cold. It now settles at approx 1 deg cooler than the remainder of the house, however with the oil boiler it was 3+ deg cooler.
As I have been fine tuning my system this Winter, I have now acquired a deep understanding of my smart thermostats behaviour (Honeywell T6R+HW). When the thermostat learns its controling the heat pump, the thermostat demands heat in each cycle ( 3 cycles per hour, 1 cycle is max 20mins) for approximately 13 minutes. When the thermostat learns the oil boiler is running (I have a bivalent system), the heat demand per cycle is reduced to about 5 - 6 minutes.
I am not a thermodynamics expert but I think because of the longer run times of the heatpump the heat output of the rads gets more chance to circulate the room before cooling. With the short 5 - 6 minute blast from the oil boiler, I am thinking the rad output cools down before it has chance to circulate the room properly?
With my vertical radiator mentioned above, due to the oil boiler not running long enough, the rad does not get chance to heat properly and hence the room is a lot cooler.
As far as heating rates, I have found the thermostat heats at approx 0.5 degree per hour regardless of heat source. The advantage I am finding with the heatpump is the lower longer heat output does not give you the chance to feel any sudden temperature cooling like the high short bursts of the oil (or gas) boiler and the rads are warmer longer so the heat distribution is better?
It makes sense that longer heating at a lower degree will give time for the air to circulate more which would lead to heat percolating through more of the room. The only thing that worries me is that your system is turning on and off as often as 20 mins; I have a dumb Honeywell and the installers left it set with 5 cyclers per hour, so for the first 2 or 3 weeks it was turning on for 6 min off for 6 mins, wasting large amounts of energy. Once I worked it out I turned it to 1 cycle per hour and it comes on for half an hour, much more efficiently and also easier on the system. I have adjusted the weather control to try and lengthen the on period. Again, it was set quite high, something like 34 at 15C and45 at +2, I have it at 31 or 32 at +15 and 42 or so at -2.
Radiators surely also make a difference, the installers got 2 things right, one of which was upgrading the radiators to larger double fine high output ones, meaning there is more air circulating out the top of them. I have been trying to get everyone else in the house to stop using radiators for drying things on, because that interrupts the air flow, but they refuse to listen to technical stuff.
(The other thing they got right was doing a simple clear install without a buffer tank, the thing they got wrong was the dumb control system is a problem)
Posted by: @guthrieThe only thing that worries me is that your system is turning on and off as often as 20 mins; I have a dumb Honeywell and the installers left it set with 5 cyclers per hour, so for the first 2 or 3 weeks it was turning on for 6 min off for 6 mins, wasting large amounts of energy. Once I worked it out I turned it to 1 cycle per hour and it comes on for half an hour, much more efficiently and also easier on the system. I have adjusted the weather control to try and lengthen the on period. Again, it was set quite high, something like 34 at 15C and45 at +2, I have it at 31 or 32 at +15 and 42 or so at -2.
I have a balancing act with my system because it is a bivalent set up. Oil boilers like a duty cycle of 3 cycles per hour unlike gas which is 6 cycles per hour. Also each cycle run time can be varied by the thermostat between 4 and 20 mins depending on the heat demand of the house. In addition, my thermostat has a minimum setting of 3 cycles per hour.
All the HVAC websites I have found suggest the ideal duty cycle for a heat pump is 2 to 3 cycles per hour, each cycle duration being between 10 and 20 mins long. So this fits in nicely with the way my oil boiler likes to be controlled and keeps the run time of the heatpump to a minimum, so extending the compressor lifespan :-). The biggest loss of energy I know of is the startup surge current of the compressor but the compressor can cycle on and off during the heat pump run time, when it achieves its water flow temperature. I do not think there is much to be saved regards power when running a heat pump with a 50% duty cycle and running the heat pump for extended periods shortens the life of an expensive compressor :-), however I could be incorrect in my assessment 🙂
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
@technogeek That's a funny sort of system, I have not heard of, but if it works for you that is fine.
I find it odd the HVAC websites say 10 to 20 mins long is best, that's different from what I have read on here and elsewhere on heat pump focused places. As for compressor lifespan it is not something that people generally bring up, where did that concern come from? My understanding is that turning them on and off a lot isn't great, 5 times an hour is definitely bad, and running it for a while is good because everything gets up to temperature.
@guthrie my friend, I feel we need to conclude this conversation as I fear we are diverting from the original topic of this thread 🙂
I am happy to continue discussing this topic in a thread of your choosing but to conclude:
Posted by: @guthrieI find it odd the HVAC websites say 10 to 20 mins long is best, that's different from what I have read on here and elsewhere on heat pump focused places.
Regards suitable duty cycles I simply put the phrase "Heat Pump Duty Cycles" in google search engine and it came back with a number of results saying the same thing, "cycle 2 to 3 times an hour, each cycle 10 to 20 minutes long". This seems to fit with the abilities of my thermostat which has 3, 6, 9 or 12 cycles per hour. Currently set to 3 to satisfy both the heat pump and oil boiler.
Posted by: @guthrieMy understanding is that turning them on and off a lot isn't great, 5 times an hour is definitely bad,
Not sure why 5 times an hour is mentioned but for clarity my system is as follows:
1 Cycle = 20 minutes
Therefore, 60 mins (1hour) / 1 cycle (20 mins) = 3 cycles per hour.
My thermostat, during a single cycle, can demand heat from the pump for approximately 13 minutes of that 20 minute cycle, that is the pump is on for 13 minutes and off for 7 minutes.
With 3 cycles per hour this means the heat pump will have 3 starts per hour and a total run time of 3 x average 13 minutes = average 39 minutes per hour.
During cold weather this heat pump on period in a cycle can be extended by the thermostat to between 15 and 18 minutes making the off time only 2 minutes. Likewise, in very mild weather the cycle on period can be reduced down to approximately 6 to 8 minutes and an off time of 12 to 14 minutes.
The number of heat pump starts remains constant at 3 times per hour. I have noted during very mild weather the system can switch off the compressor during a cycle "on" period but mainly it varies the compressor speed to maintain the LWT when reached.
To be fair this is similar behaviour to your humble fridge freezer.
For your information, for an outside temperature range of +5 to +14 degrees C, I am getting an average COP of 4.33. This could be improved by replacing all my old 1970's /80's oversized single panel radiators with modern ones however I fear that would be a step too far with "She who must be obeyed"! lol
Also a bivalent system is simply a configuration that allows you to set an outside temperature threshold (in my case +5 degrees) and when the temperature is greater than the threshold, the heat pump operates or if the temperature is less than the threshold, the oil boiler operates.
Normally this type of system is used to help keep the building warm in very low outside temperatures when the heat pump can no longer efficiently supply the required heat. I am using it as a cost saver because the electric tariff I am on, I find the cost of heating the house below +5 deg outside temperature, significantly cheaper with oil sadly.
However over the next year the situation may change, oil may get more expensive and electricity (hopefully) cheaper in which case the temperature threshold will be moved down and the oil boiler used less and less.
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
@technogeek Yes, we are going far off topic, some drift is tolerated here so we should be fine. Your COP sounds good, but with the old radiators you will struggle to get lots of heat into the house, it is a pain having them replaced.
I am now wondering why I haven't read much about lifespan of the air pump systems, I may start a thread on that after more research.
The on and off 5 times an hour seems to be a widely agreed upon number of cycles per hour that would be bad for your heat pump, but I haven't seen exactly where that number came from, it might be that one of the long term members has an idea.
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 551 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
Your topic raises my interest for a couple of reasons. ...
By DavidB , 6 minutes ago
-
@batpred frost protection £632 ??? That is taking t...
By MartinRobinson , 28 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
@editor Interesting questions. If the answer to either ...
By ChandyKris , 39 minutes ago
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 8 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 9 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 10 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 11 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 13 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 14 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 16 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 18 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 22 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 3 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago