[Solved] Low shower pressure after ASHP retrofit
Posted by: @jacs@derek-m not sure on the cylinder pressure but the flow drops massively when I open multiple taps, almost to a stop.
When you say that the flow drops massively, I assume this is at the shower head. It would appear that you have some form of restriction that is limiting the flow from or to the hot water cylinder, such that opening more taps will mean that this limited flow is being shared over more 'openings'. Because the shower head is higher than the taps it is more likely that this will lose flow first.
Try turning the shower 'cold' and open some cold taps. If the flow through the shower head remains constant then the problem is not with the shower, but is some form of restriction in the 'hot' pipework.
I would suggest that you check the pipework from the shower head back to the hot water cylinder for partially closed valves or thinner pipework. Also check the pipework from the mains supply to the hot water cylinder.
If, as Johnmo suggests, the problem is due to a pressure imbalance at the shower unit, you should ask your installer to fit a pressure reducing valve on the cold water feed to the shower unit. It should then be possible to set both the hot and cold feed to 3 bar.
@johnmo Hi, please can you confirm what balance flow is?
I turned the shower to cold and opened the cold taps and the shower flow didn't change.
Most mixers uses a balanced flow i.e. the flow pressure from hot and cold is the same. This is how it is normally achieved via the combined valve at the UVC
If you don't have this setup, you really need a check valve on the hot outlet of the cylinder to prevent reverse flow.
The alternative to the balanced flow connection on the combi valve is a prv at the cold water entry to the house set at 3bar or less. Mine is after stop cock, and strainer, then prv then to the rest of the house.
Your cold water test shows it's not a cold issue. So all that is left is the hot water supply. Testing hot on its own isn't really possible because there may always be a mix of cold going into the hot side of the mixer.
Problem resolved - there was a reducing valve under the bathtub restricting flow.
@jacs brilliant. Thanks for letting us know, and glad you’ve resolved it.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Our newly fitted shower system was regularly running to cold if paused. The excellent plumber fitting the ashp solved it by fitting a pressure control valve on the inlet cold feed.
Different symptoms but same root cause the mixer shower needed balanced pressure feeds. Why the original plumber didn’t fit one is a good question.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
-
Yes, the "zoning with ASHP" topic again...
2 months ago
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
5 months ago
-
Has anyone seen this problem before? Huge anticycling times
8 months ago
-
My British Gas – Heat Force ASHP Installation: A Frustrating Experience
9 months ago
-
Advice needed on inefficient Samsung ASHP installation
10 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 90 Online
- 3,393 Members
Latest Posts
-
RE: Ecodan consuming 100kwh per day in new build!!!
This particular example is one of the worst I have seen...
By JamesPa , 56 minutes ago
-
RE: Cleaning up after gas meter removed
i had the gas pipe terminated out side the house in the...
By AgentGeorge , 1 hour ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@toodles I have noticed that on some.days it takes a wh...
By ChandyKris , 11 hours ago
-
-
RE: Fan running in hot weather ...why?
I wonder if it has some kind of pressure transducer to ...
By ASHP-BOBBA , 15 hours ago
-
RE: Cooling with Samsung Gen6 and Flow error
@iaack The system isnt running long enough for any cond...
By EcoBaker , 21 hours ago
-
@heacol thanks for confirming we can only hope NAPIT ag...
By Bart , 23 hours ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@editor If it is of any interest, we had the BUS grant,...
By Toodles , 2 days ago
-
Sorry to hear that @bruce. Sadly I’ve heard from multip...
By Mars , 2 days ago
-
RE: Crystal Ball Time: Communal or even Area Energy Storage?
I am invested in a couple of listed energy storage fund...
By Old_Scientist , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
That would be my biggest commitment -time to gain great...
By SUNandAIR , 3 days ago
-
RE: Who has a V2G EV installation
As has been discussed on other threads, trying to justi...
By Majordennisbloodnok , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Thanks @mikeh. Then I will also go back to non smart ta...
By ChandyKris , 4 days ago
-
RE: Location of hot water isolation valve on cylinder
@transparent Thank you so much and very helpful. Earlie...
By rossowheels , 5 days ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 6 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 6 days ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 7 days ago