Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Load Compensation and Weather Compensation
Posted by: @AnonymousPosted by: @jamespaAlmost but not quite a trv with remote sensor. A trv with or without a remote sensor operates principally, so far as I know, as an on off device (albeit that there is an element of analogue control).
No they are not on/off valves, they modulate flow. Exactly what you say you want, they do our the box. Modulate radiator flow based on room temperature. So as to keep room a a set temperature. Add weather compensation, they will continue to modulate flow as needed.
Simple description of a trv
https://www.traderadiators.com/blog/how-do-thermostatic-radiator-valves-work
Er - that description you posted says that the trv shuts off the flow when the room is at the set temperature, which is also what seems to happen in practice at least with my Drayton trvs.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @AnonymousPosted by: @jamespaAlmost but not quite a trv with remote sensor. A trv with or without a remote sensor operates principally, so far as I know, as an on off device (albeit that there is an element of analogue control).
No they are not on/off valves, they modulate flow. Exactly what you say you want, they do our the box. Modulate radiator flow based on room temperature. So as to keep room a a set temperature. Add weather compensation, they will continue to modulate flow as needed.
Simple description of a trv
https://www.traderadiators.com/blog/how-do-thermostatic-radiator-valves-work
Er - that description you posted says that the trv shuts off the flow when the room is at the set temperature, which is also what seems to happen in practice at least with my Drayton trvs.
Think I attached the wrong link
Posted by: @AnonymousThink I attached the wrong link
Still not quite. As I read this the body adjusts for fixed flow when on (based on an adjustment made by the installer according to a table that doesn't even include the dt5 condition with which heat pumps are commonly designed) and then the head works like any other head, turning the flow on or off. We want something that adjusts the flow rate very slowly to achieve the required room temperature, as if adjusting a lsv manually. It's really a commissioning device not a control device and once set it can stay set.
There is definitely a problem and thus an opportunity. I've lost count how many times I have explained on this forum how to adjust WC, and then how to adjust lsvs to achieve equal room temps (or the desired different room temps) - in short how to set up an open loop WC based system. Clearly therefore installers don't always do this which, given how long it takes (elapsed time not actual effort,), is unsurprising.
With a gas boiler installers simply whack up ft to max fit trvs and then let householders sort it out. It needs to be as simple for an ashp. There are two (somewhat interlinked) parts of this namely the WC curve set on the heat pump and the flow rates through each radiator. Balancing for deltaT (which installers may do) is a start, but doesn't finish the job because radiators are inevitably not correctly sized. Balancing for room temperature (as described also on the heat geek website) is what's needed, but takes time.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
The solution for individual room control but to maintain minimum flow on an ASHP circuit will be perfect when they produce a valve that only depletes the flow in a controlled manor relayed back to the central control unit to reduce the output of the emitter rather than shuts it off completely. This kind of control has been available for a very long time commercially but is expensive, I am aware some versions of this are starting to hit the domestic market but can be expensive.
The solution needs to be cheap for it ever to be considered on domestic designs as the cost of these retro fits are expensive already. It is worth noting that with many of the discussions around the functionality or set up and efficiencies of these systems there is nearly always a better way to design and commission them but it costs more and more.
Compared to other tech in the commercial industry. TRV's are cheap and were designed to work with boilers for homes as a cheap better form of control, lock shields are cheaper and have been around forever.
All other forms of hydronic local control are more expensive and are often overlooked as the £9,000 to £15,000 bill is already expensive enough and as a nation we are often driven or guided to cheapest quote and not best design.
It is also worth noting that it is likely that most customers will have the basic installation the 1st time round as it is so expensive, of the £11,000 installation cost £7,500 of this is the retro fit conversion to make the house and the system match up for an ASHP, the remaining £3,500 would be to straight swap the ASHP external unit, just like replacing a boiler but this cost is only possible once the home has been retrofitted.
Once the home is retrofitted, in the future there will be upgrades available when you swap out the systems or mid life as companies invent cost effective solutions to control, we are currently seeing a few software versions already, hardware will probably follow at some point as the market gets bigger.
Capacity control works well on just maintaining DT at the external unit if you have the correct mechanical control at the emitters. Combined with WC capacity control on DT gives a very smooth control curve. Manufacturers have been using this kind of curve since the end of fixed speed compressors in the 90's. These systems are still just AC units with a plate, this tech has been here a very long time but the new part is the water adaption side and control of the water the rest of the system will always work well and always has done on good brands (this is where the fit a buffer to protect the manufacturers kit came in) they knew the systems will work for a very long time if the water flow rate is good and never stops.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @ashp-bobbaThe solution for individual room control but to maintain minimum flow on an ASHP circuit will be perfect when they produce a valve that only depletes the flow in a controlled manor relayed back to the central control unit to reduce the output of the emitter rather than shuts it off completely. This kind of control has been available for a very long time commercially but is expensive, I am aware some versions of this are starting to hit the domestic market but can be expensive
I think that maybe what the adia thermal system does, but as you say it's quite expensive and only works with some ashps
Alternatively perhaps someone will come up with something that is relatively crude but 'good enough'. I do wonder about a completely passive thing, essentially a version of a trv decorators cap, which replaces a trv head and has two adjustments, one set by the installer having complete adjustment, and the second offering the householder limited additional control. Installer could then balance for deltat which gets close if the sizing is roughly right, householder could then tweak within limits if they need to. Plastic moulding turned out in millions, cheap. Might need two versions, one to put on the rads which are fully open and are not to be adjusted, another to put on the other rads. Still cheap. Not fully automated but perhaps has potential?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 1,004 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
Every manufacture has a guide and service list...
By ASHP-BOBBA , 20 minutes ago
-
RE: Summer usage. Why is my Vaillant Aerotherm using so much energy on "heating"?
I don’t know how the Aerotherm works so can’t comment o...
By AndrewJ , 36 minutes ago
-
Its good kit the Midea and significantly cheaper, you w...
By ASHP-BOBBA , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Have you tried cutting the grid feed to see what actual...
By JamesPa , 2 hours ago
-
Contractors pack for inta antifreeze valves are around ...
By ASHP-BOBBA , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
Critics and naysayers will be negative whatever the gov...
By JamesPa , 3 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 13 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 14 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 16 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 16 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 18 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 21 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 1 day ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 2 days ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 3 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 3 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 5 days ago