Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
A Salus auto balance UFH valve, could be a simple bolt on to replace a trv. Just open the lock shield fully. Not sure what dT your radiator works at? The Salus above 30 Deg holds a 7 Deg dT and below 30 degs a 4dT. They use a clip on temperature probe on the supply and return piping, but also require a power supply.
The original ones had a couple of hours self commission period, new one fit in place, zero commission period.
Posted by: @AnonymousA Salus auto balance UFH valve, could be a simple bolt on to replace a trv. Just open the lock shield fully. Not sure what dT your radiator works at? The Salus above 30 Deg holds a 7 Deg dT and below 30 degs a 4dT. They use a clip on temperature probe on the supply and return piping, but also require a power supply.
As I understand it these balance for fixed dT
That's not what's needed unless emitters are perfectly sized (which they inevitably aren't). What's needed is to balance for room temperature (but slowly, like an lsv being manually tuned,) thus taking out inevitable variations in sizing.
I agree that the right device would allow lsvs to be fully open.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
That's not what's needed unless emitters are perfectly sized (which they inevitably aren't). What's needed is to balance for room temperature
So a thermostat is what you are describing, that modulates flow instead of shutting it off? So a trv with remote sensor?
Posted by: @Anonymous
Posted by: @jamespaThat's not what's needed unless emitters are perfectly sized (which they inevitably aren't). What's needed is to balance for room temperature
So a thermostat is what you are describing, that modulates flow instead of shutting it off? So a trv with remote sensor?
That is kind of what I was thinking.
Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w + 13x 480w Solar Panels
Sigenergy 10kW Inverter
16kW Sigenstor battery
These have been about for a few decades. Simple. Sure you could get a wireless version. Just look around. Do a basic radiator balance, let them fine tune.
But you really need them, cash rich, time poor maybe, a couple of fine tunes, over a few evenings, no you don't need them. If your radiator sizing is reasonable shouldn't be much to do apart from hydraulic balance. Just follow heat geek instructions on their website.
Posted by: @Anonymous
Posted by: @jamespaThat's not what's needed unless emitters are perfectly sized (which they inevitably aren't). What's needed is to balance for room temperature
So a thermostat is what you are describing, that modulates flow instead of shutting it off? So a trv with remote sensor?
Almost but not quite a trv with remote sensor. A trv with or without a remote sensor operates principally, so far as I know, as an on off device (albeit that there is an element of analogue control). That's not what we want, we want a device that adjusts the flow on a longer timescale (hours) so that it's just the right flow to achieve the desired room temperature. WC still applies.
It's literally the same as adjusting the lsv manually, something you do slowly over hours or days until it's right, then leave forever.
I completely agree that householders could in principle do this manually, but doubt that many can/will hence the need for a fit and forget solution. Don't forget we need to assume that a)householders have no interest in heating and b) that a high proportion are incapable of (or unwilling to) following simple instructions.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
It's literally the same as adjusting the lsv manually, something you do slowly over hours or days until it's right, then leave forever.
Is that really the case? Won’t the rate of heat loss in the room change as it cools/warms outside and thus what it is balanced for today at 1c isn’t the same as tomorrow when it’s -3c? The flow temperature would have increased but is the radiator still properly balanced in the changed scenario?
Posted by: @andrewj
It's literally the same as adjusting the lsv manually, something you do slowly over hours or days until it's right, then leave forever.
Is that really the case? Won’t the rate of heat loss in the room change as it cools/warms outside and thus what it is balanced for today at 1c isn’t the same as tomorrow when it’s -3c? The flow temperature would have increased but is the radiator still properly balanced in the changed scenario?
Yes it really is the case to a good (good enough) approximation. Once emitters are balanced open loop WC with all emitters permanently on works pretty well, and all this is is open loop WC with an automated balancing instead of manual balancing.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @andrewj
It's literally the same as adjusting the lsv manually, something you do slowly over hours or days until it's right, then leave forever.
Is that really the case? Won’t the rate of heat loss in the room change as it cools/warms outside and thus what it is balanced for today at 1c isn’t the same as tomorrow when it’s -3c? The flow temperature would have increased but is the radiator still properly balanced in the changed scenario?
Yes it really is the case to a good (good enough) approximation. Once emitters are balanced open loop WC with all emitters permanently on works pretty well, and all this is is open loop WC with an automated balancing instead of manual balancing.
That's good to know - and in which case, adding anything fancy to the system to "automate" it sounds like (a) an unnecessary complication; and (b) likely to not work very well and/or just become aggravating (in my somewhat jaded and world-weary opinion)
Posted by: @andrewjPosted by: @jamespaPosted by: @andrewj
It's literally the same as adjusting the lsv manually, something you do slowly over hours or days until it's right, then leave forever.
Is that really the case? Won’t the rate of heat loss in the room change as it cools/warms outside and thus what it is balanced for today at 1c isn’t the same as tomorrow when it’s -3c? The flow temperature would have increased but is the radiator still properly balanced in the changed scenario?
Yes it really is the case to a good (good enough) approximation. Once emitters are balanced open loop WC with all emitters permanently on works pretty well, and all this is is open loop WC with an automated balancing instead of manual balancing.
That's good to know - and in which case, adding anything fancy to the system to "automate" it sounds like (a) an unnecessary complication; and (b) likely to not work very well and/or just become aggravating (in my somewhat jaded and world-weary opinion)
In principle I agree. However how else can you correctly adjust the lsvs? Installer won't spend the hours that it takes to do it (they may adjust for DT but won't in most cases adjust for room temperature) and most homeowners not capable/not willing. The alternative (as I fear the default) is fitting trvs which are a bad option.
It's a real problem that needs a solution that works for the average householder, not just the ones on this forum!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaAlmost but not quite a trv with remote sensor. A trv with or without a remote sensor operates principally, so far as I know, as an on off device (albeit that there is an element of analogue control).
No they are not on/off valves, they modulate flow. Exactly what you say you want, they do our the box. Modulate radiator flow based on room temperature. So as to keep room a a set temperature. Add weather compensation, they will continue to modulate flow as needed.
Simple description of a trv
https://www.traderadiators.com/blog/how-do-thermostatic-radiator-valves-work
But the disadvantage of trv modulation or any self balancing devise is variation in flow rate at the heat pump. You ideally need as much flow as possible, to give smallest dT to get maximum radiator output, for minimum flow temp, to get best CoP.
Hence the reason everyone is saying minimise their usage.
Auto balance anything, is just a band aid on a fully open system. They really have no place. People should either self install or get a professional install, the professional install should balance they system, if they don't call them back, you have paid good money for an install.
- 26 Forums
- 2,582 Topics
- 60.1 K Posts
- 382 Online
- 6,896 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
Shocking.
By Majordennisbloodnok , 18 minutes ago
-
RE: Anyone concerned about GivEnergy?
@jostar Given the circumstances I think most folk wo...
By KevH , 43 minutes ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
Interesting. I am on OG Variable and the night time ...
By JamesPa , 1 hour ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
@wesleyp1874 OK so the installation was paid for by ...
By JamesPa , 1 hour ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 2 hours ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
RECC are abysmal. I was hoping it’d be HIES.
By Mars , 2 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
I read this thread from the beginning to its end.And th...
By LeJamaisContent , 3 hours ago
-
And one should not underestimate the enhanced flavour p...
By Toodles , 6 hours ago
-
RE: Water law settings... A year on
Yes it does Apart from the abbreviations! We're in ...
By Profzarkov , 7 hours ago
-
Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Occasionally, during a Set Back period the com...
By Unsure , 13 hours ago
-
Very thought provoking Mars, and it just goes to reinfo...
By Toodles , 14 hours ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Yes it's a shame the manufacturers make this vital info...
By bobflux , 17 hours ago
-
RE: Plug and play solar. Thoughts?
News that the German VDE is widening the plug in solar ...
By Batpred , 1 day ago
-
My Immersun power diverter problems now they have ceased trading
I have had an Immersun unit for 15 years that happily w...
By pjcwood , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Quite often it’s the ones that have to figh...
By Papahuhu , 1 day ago
-
RE: To re-pipe or not to re-pipe? Moving from oil boiler to air source heat pump.
Hello @Penval unfortunately, now the winter is gone and...
By LeJamaisContent , 1 day ago
-
RE: Grant Aerona R32 – Summer, Winter mode & Setbacks
What are you envisaging doing throughout the day? Pers...
By JamesPa , 1 day ago
-
@batpred ok My energy delivered in kWh was a...
By JamesPa , 1 day ago
-
-
RE: Global Energy Systems Thurso ASHP
Hello @outlawuk sorry, I forgot about this, important:i...
By LeJamaisContent , 2 days ago
-
RE: Debugging my legionella immersion heater
@prunus Hmm 57 vs 65 does seem a way off, bu...
By JamesPa , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
@batpred I assume you plugin the battery on a wall sock...
By ChandyKris , 2 days ago
-
RE: Grant ASHP keeps switching on every hour
Frankly I have no idea how a room thermostat is ever go...
By JamesPa , 3 days ago