Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Kev-M's ASHP Performance
The next round is to try and use weather compensation and thermostats together. Here’s what happened.
The theory is that setting a compensation curve that would normally make the house a few degrees too warm and limiting it by on/off thermostats will reduce cycling while keeping the house at a steady temperature. The aim is to get something like the below 45 deg set flow but with lower flow temps. Although even this didn't prevent all cycling.
But what actually happens is the weather compensation and thermostats just end up getting in each other's way. The thermostat causes ons and offs but in between there is a lot of cycling. This is because the ASHP will stop heating when either the thermostat temp (21 deg in my case) or the weather comp flow temp is reached and won’t start until the thermostat calls for heat and the weather comp flow temp is low. So the thermostat calls for heat and the ASHP starts heating. But the target flow temp is reached before the thermostat set temp, so the ASHP stops, even though the thermostat is still calling for heat. The flow (and the house) cool down a bit then the ASHP kicks in again. And repeats this until the thermostat set temp is eventually reached, at which time the ASHP stops, whether or not its flow temp is reached. The house then cools from 21.5 deg or so to 20.5 deg or so, the thermostat calls for heat and does it all again.
The below graph illustrates the above. You can see the 5am start up, the steady state running, the gaps when the thermostats switch the ASHP off and the 3pm DHW peak. There are only four periods of ASHP heating but these all include as much cycling as letting the ASHP run constantly.
The obvious way to stop the cycling is to increase the flow temp so that it requires a high enough output/flow, a bit like the fixed flow above. To get this to work the compensation curve is going to have to be very flat, not a million miles from the fixed flow.
But does it matter? Cycling for me is about twice an hour or so and in these conditions my COP is good. This was a warmish day using weather compensation only. I’d rather get the cold weather performance right...
But I like tinkering so I have now bumped up the warm end of the curve so that it’s 42 @ -2 and 33 at 20 and the thermostats are controlling the room temp. I'll report back.
This is what happened. There is almost no cycling. The outside temp was 0-12C. Is it better/cheaper? The house temperature varies more, which isn't as good. I don't know if it's cheaper but I suspect there won't be much in it. Although there are periods when the ASHP is off, the flow temp is several degrees higher than it needs to be. It's interesting to see the COP is low at very low ASHP consumption. This is because the ASHP itself is slightly less efficient at very low outputs and also because with the way COP is measured in my set up, the consumed energy is everything; the pumps, FTC controller the immersion (if it's used) and these are running all the time the ASHP is.
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 2,689 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
I am amazed that there is not something out there to me...
By JamesPa , 1 hour ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 7 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 12 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 2 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 4 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 5 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago