Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Kev-M's ASHP Performance
The next round is to try and use weather compensation and thermostats together. Here’s what happened.
The theory is that setting a compensation curve that would normally make the house a few degrees too warm and limiting it by on/off thermostats will reduce cycling while keeping the house at a steady temperature. The aim is to get something like the below 45 deg set flow but with lower flow temps. Although even this didn't prevent all cycling.
But what actually happens is the weather compensation and thermostats just end up getting in each other's way. The thermostat causes ons and offs but in between there is a lot of cycling. This is because the ASHP will stop heating when either the thermostat temp (21 deg in my case) or the weather comp flow temp is reached and won’t start until the thermostat calls for heat and the weather comp flow temp is low. So the thermostat calls for heat and the ASHP starts heating. But the target flow temp is reached before the thermostat set temp, so the ASHP stops, even though the thermostat is still calling for heat. The flow (and the house) cool down a bit then the ASHP kicks in again. And repeats this until the thermostat set temp is eventually reached, at which time the ASHP stops, whether or not its flow temp is reached. The house then cools from 21.5 deg or so to 20.5 deg or so, the thermostat calls for heat and does it all again.
The below graph illustrates the above. You can see the 5am start up, the steady state running, the gaps when the thermostats switch the ASHP off and the 3pm DHW peak. There are only four periods of ASHP heating but these all include as much cycling as letting the ASHP run constantly.
The obvious way to stop the cycling is to increase the flow temp so that it requires a high enough output/flow, a bit like the fixed flow above. To get this to work the compensation curve is going to have to be very flat, not a million miles from the fixed flow.
But does it matter? Cycling for me is about twice an hour or so and in these conditions my COP is good. This was a warmish day using weather compensation only. I’d rather get the cold weather performance right...
But I like tinkering so I have now bumped up the warm end of the curve so that it’s 42 @ -2 and 33 at 20 and the thermostats are controlling the room temp. I'll report back.
This is what happened. There is almost no cycling. The outside temp was 0-12C. Is it better/cheaper? The house temperature varies more, which isn't as good. I don't know if it's cheaper but I suspect there won't be much in it. Although there are periods when the ASHP is off, the flow temp is several degrees higher than it needs to be. It's interesting to see the COP is low at very low ASHP consumption. This is because the ASHP itself is slightly less efficient at very low outputs and also because with the way COP is measured in my set up, the consumed energy is everything; the pumps, FTC controller the immersion (if it's used) and these are running all the time the ASHP is.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 242 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 8 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 12 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 13 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 13 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 16 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 23 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 23 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago