Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Increase floor temps for UFH, Samsung Gen6
We have a new build, well Insulated. 160mm PIR floor, 150mm PIR roof, 125mm full fill walls. Meticulously checked by me throughout installation. Air tightness of 3, likely due to multiple sets of sliding doors.
We are on octopus cosy, and for the last 12 months average about £160 a month, inclusive of Elec cooking, daily dish washer, daily washing machine, twice weekly tumble dryer etc.we go through a lot of hot water. We get away with the cheap heating periods, albeit it for cold snaps we do need to extend the hours noticeably.
We have a Samsung gen6 12kw ASHP, powering two UFH manifolds (one with 13 zones, other 5 zones). No buffer tank. From what I can tell we don't short cycle?
However the bungalow does have an inefficient design... . Very very high ceilings, sprawling a bit, lots of glass. Children's rooms have small floor space, but then a Mezzanine in them to give them two stories under a 4.5m bungalow roof. It's cool, but means they are tricky to heat die to surface area if UFH vs volume of room.
Now everything works well, however during these sub zero the children's rooms struggle to heat behind 18 degrees due to the design.
I am keen to see if I can force increase the UFH temps. Especially as the pays are nicely cheap in my mind, and the cosy periods at 11p mean I want to hammer them vs extending the hours excessively into the 24p tariffs.
My Samsung water law settings are....
Outdoor temp for water law:
15 degrees ........3.0
Water out temp for WL1 Heat (WL1 floor)
36 degrees..... 43degrees high target
Water temp out for WL2 Heat (wl2-fcu)
36 degs....... 43 degrees
However even setting the offset to +5 degrees, after 4 hours of operation the outflow temp is still only 29 degrees, and the rooms are all a couple degrees colder then I would like.
Welcome any recommendations. I know I could run the ASHP for longer... But the 11p vs 24p tariff change means I am keen to loose efficiency to make more usage of it.
Thank you!
Posted by: @AnonymousHowever even setting the offset to +5 degrees, after 4 hours of operation the outflow temp is still only 29 degrees, and the rooms are all a couple degrees colder then I would like.
4 hours isn't very long, houses have a large heat capacity (ie energy stored in the fabric) and can therefore take a day or more to reach a steady temperature. Is it possible that you have hit the maximum output of the heat pump which, if it were the case, would explain what you are seeing? ASHPs are generally sized on the assumption that they are run full time; if you are only running part time you could quite easily be hitting max output even though 12kW is quite a large ASHP. What was the design loss at what OAT and for how many hours are you running?
If you have in fact reached the max output capacity then there is not much more you can do with the heat pump. At this point its either run it for longer (as intended) or deploy some supplementary heating. Remember its only this cold for a few days of the year so if you hammer your electricity bill for a few days its not so much in the grand scheme of things. You do have to think about any heating, but particularly ASHPs, over a season since load varies quite dramatically.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@andehh, do you have a way of monitoring the power being produced by the ASHP when the UFH is on or, failing that, can you check the Instantaneous Usage shown in the Energy information display?
With your Water Law settings and the +5C set point, the target output temperature should be 48C when the outside air temperature is 3C or lower. If the output temperature is only 29C then I would expect the ASHP to be running up to its 12kW maximum to achieve the target (with regular defrost cycles given the low outside temperature).
With my Samsun 8kW Gen 6 it is very obvious from the noise when it is running at maximum during the DHW cycle. How does your 12kW unit sound during heating and DHW operation?
The reason I am asking about the power output is that my 8kW unit is regularly failing to achieve the Water Law target temperature but it is running well below full power, see this topic.
Highest draw I've seen from it is about 5kw input via the instantaneous power menu , though I don't check it too often. From octopus half hourly it seems to only pull 2 to 2.4kw over a 30min window on average..... Ie 4am to 7am slot. DHW is the same.
I presume this is ok? 2.4kw x my Cop of 3.5 ish comes close to the 12kw which I imagine is the OUTPUT up to?
And yes.... It could be 29 degrees is as hot as it can get if the whole slab is relatively cool from a period of 3-5 hours of a heat off cycle I guess?
I have added an extra 2 hours a day onto the schedule and will monitor, maybe add a couple more each time until 'cold' winter passes and then I'll reduce it back to cosy periods for the shoulder months.
- 26 Forums
- 2,645 Topics
- 61.8 K Posts
- 384 Online
- 7,045 Members
Join Us!
Latest Posts
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
No, I agree entirely. There shouldn't be a need for an ...
By Majordennisbloodnok , 1 hour ago
-
RE: How many people are happy with their ASHP and do you believe them?
I agree, and not. Energy prices are a largely politica...
By JamesPa , 2 hours ago
-
RE: Solar Produced vs Home Consumed
All inverters will use solar power in preference to dra...
By JamesPa , 2 hours ago
-
Yes, you will need to notify them even if the inverter ...
By Old_Scientist , 2 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 15 hours ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
I do the same: cool my large buffer (3000L) to 10C, pum...
By upnorthandpersonal , 24 hours ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 1 day ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I reached out to MCS directly last week on this and her...
By Mars , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 2 days ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 3 days ago
-
I will soon be struggling. Admittedly it is the summer,...
By Batpred , 3 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Not known yet. I've asked a local Councillor to follo...
By Transparent , 4 days ago