Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
How accurate was your heat loss survey?
I'm strongly investigating getting a heat pump.
We had a heat loss survey 2 years ago, and it said we needed an 8kW HP machine. I set my central heating boiler limited to 8kW, and it's been fine.
We didn't have the installation because of the complexity of planning, but with the upcoming changes we are revisiting the design. On a refresh of the quote, we now need a 10kW HP according to the design, no changes to building fabric. The main difference being one room which has increased heat loss by over 300 Watts (apparently).
So this has led me to run my own calculations, using the free Stelrad app, and according to that the original quote was "correct".
But now I have started to dive deeper into the topic, both with theory and real data.
My first approach was to calculate what my current power of my radiators are. The hardest to heat room, is the largest, has 3 external walls, a window and patio doors, is the index circuit and is the main living space so needs the highest temperature. I run my boiler at 55C flow, and it's a DT11 boiler, so the rads should be at 49.5C. Based on the current radiators I have, with the Stelrad conversion factor, that's 300Watts output less than the lower heat loss survey. And yes we had cold weather on the 10th Jan this year which was at the OT for the design of -2.4C. So the new design heat loss for the room is 2.2kW, the original was 1.9kW, but my actual radiators at my actual flow and return should only be capable of 1.6kW.
Which brings me to the data for that actual day, I have a weather station that measures both external and internal temperature, so I can be sure my room was heated to the correct temperature at -2.4C. My Octopus smart meter readings show 102kWh for a 17 hour heating period, which equals 5.4kW of heating power, assuming 90% boiler efficiency. And to confirm the same, each 30 minute period used 3kWh of gas.
This all suggests that the installers calculations are over the top, but what do I know, I'm just a dummy with a spreadsheet and too much time on my hands.
So can I ask the community, how accurate were your heat loss surveys, did you have more than one, did you do your own, was there a spread between theory and practice, and was your system ultimately over or under sized?
Thanks 👍
@scalextrix I think what you are describing is exactly why I am so sceptical of room by room assessments and more supportive of previous use estimates.
In my case I knew my previous bungalow was fine with a 5kW heat pump and estimated that the new one would be too with some radiator changes. I also did some experiments with running my gas boiler at a lower temperature.
Guess what. I was right. I don't think it's rocket science to get a ballpark figure, run some tests and if unsure add on a small amount for safety.
On several occasions I have looked at a house and estimated it's rough heat loss in minutes with a much greater degree of accuracy than many of the experts with their heat loss assessments who frequently over egg it.
Worst case scenario is add some more insulation if you are widely wrong.
I await a torrent of abuse over my comments 😁
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- Mine was rubbish. Very poor EPC assessment driving massive over assumption on heat loss and a resulting system much bigger than I need (cascade). Ours is a large old but very well insulated, double glazed property with UFH throughout downstairs. Room by room is a bit pointless as so many of the rooms touch each other - resulting in a higher spec. I even told them of our actual heating usage in each of the last 5 years - which for cop of 3 would mean a 10kw system (not 17kw which is what was installed)
so far this year since feb1 ( when the installation wrinkles were sorted) the whole sytem has been OFF for 25% of the time, and very rarely do both pumps operate.(I’ve seen it happen once)
@bontwoody thanks, do you have any tips for a real world data approach.
It does feel a little risky basing my estimate on a single day, unfortunately I had to travel quite a bit over winter so don't have a lot of good data to run with.
@carpenterstation sounds like what I'm afraid of, hopefully you can get it sorted.
Thanks for your feedback.
My heat loss survey came back at 7.4kW
We keep our house a little cooler than design temp, at around 19-20C, and 18C overnight. On the coldest day last winter, we generated 95kWh of heat, divided by 24h gives ~4kW, substantially below the heat loss survey calculation. I attribute the difference to the high air changes per hour value MCS used at the time, and that we do not heat to 21C.
Our situation was further exacerbated by the fact that the installers used Samsung who offer 8kW and 12 kW models, and the 8kW model cannot deliver 7.4kW output at design temp (-2C), so they insisted on installing the 12kW model. The upshot is we ran it at bare minimum all winter, and in the shoulder months of autumn and spring, we just run for a few hours and turn off like a conventional boiler as it's putting out too much heat for the property (we certainly turn off for 8-10h overnight)
That said, it has still performed really well and our COP figures are in line with Samsung's published data but continuous running is not possible for much of the year.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
The usual problems are not including known insulation improvements or the defaults for air leakage.
If you have an actual air loss measurement it can be used by a potential installer (3 used it, one didn’t) instead of defaults. Cost ~£300 might be saved on the heat pump unit alone if a smaller one proves suitable.
20% or even 50% over-sized is not a crucial issue. Problems occur when units are 2-3x oversized
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
@scalextrix When do you intend taking the plunge? Do you have next winter to work with to get some good data?
If you have the house area and a feel for the insulation level you can get a rough estimate using the heat geek basic guide.
Https://www.heatgeek.com/how-to-size-my-heat-pump-or-boiler-heat-loss-cheat-sheet/
Its very rare for a heat pump to be undersized compared to the opposite situation so I would start on the assumption that 7kW is a reasonable starting point.
Also try and find a house similar to yours using heatpumpmonitor.org or visitaheatpump. You can then ask how their system is performing.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@judith where it does start to make a differnce is installation cost and noise. Thanks for your reply.
Posted by: @old_scientistMy heat loss survey came back at 7.4kW
We keep our house a little cooler than design temp, at around 19-20C, and 18C overnight. On the coldest day last winter, we generated 95kWh of heat, divided by 24h gives ~4kW, substantially below the heat loss survey calculation. I attribute the difference to the high air changes per hour value MCS used at the time, and that we do not heat to 21C.
Our situation was further exacerbated by the fact that the installers used Samsung who offer 8kW and 12 kW models, and the 8kW model cannot deliver 7.4kW output at design temp (-2C), so they insisted on installing the 12kW model. The upshot is we ran it at bare minimum all winter, and in the shoulder months of autumn and spring, we just run for a few hours and turn off like a conventional boiler as it's putting out too much heat for the property (we certainly turn off for 8-10h overnight)
That said, it has still performed really well and our COP figures are in line with Samsung's published data but continuous running is not possible for much of the year.
Thanks, so yeah yours is quite oversized, we are the opposite, we need to keep the huse warmer than the standard.
For me: Two full surveys (each taking 3hrs, one of which cost me £300) got to 16kW. Correcting for obvious errors in the surveys got to 10.5kW. Measured loss based on gas consumption 7kW. Found Two installer prepared to take this into consideration.
Installed '7kW' Vaillant (actually specced at 8.5 kW at design conditions). More or less perfect, perhaps 0.5-1kW over. Really pleased with the installation.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@scalextrix for our house 1950s detached the air leakage proportion was30% of the supposed total, using the default values. In fact with the measurements it was 2%, so that alone would have given an over estimate.
Noise and insulation go together on heat loss on windows because seals and droughts are often poor on single glazing. Double glazing solves both issues together on windows but not elsewhere. Single glazing transmits external noise inside.
Your bills are the best estimate of what heat pump size you will need. Do you know your annual consumption. This rule of thumb works well for most people https://protonsforbreakfast.wordpress.com/2022/04/05/what-size-heat-pump-do-i-need-a-rule-of-thumb/
Different surveyors have different hang-ups. We had a range from 8 to 12kW and the reason for the upper value for that surveyor was we couldn’t prove the old retrofit cavity wall insulation still worked. Doh! It kept us warm didn’t count for that company. Our usage said 7-8kW according to the method used.
If you want the house hotter say so, they can go up but not down.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
- 26 Forums
- 2,722 Topics
- 63.8 K Posts
- 1,832 Online
- 7,124 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Electricity price predictions
@jamespa Smart move by Burnham, although minor it ticks...
By Papahuhu , 58 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
To clarify that statement a little, a plug-in battery t...
By Old_Scientist , 1 hour ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor Thank you for the detailed response. I’ll repor...
By sttpd1917 , 2 hours ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 2 hours ago
-
RE: Samsung heat pump - data cable issue
@Steveimpey, having skimmed through the manuals and the...
By Mars , 2 hours ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 hours ago
-
Heat of vaporization of water is 2.25 MJ/kg (0.625 kWh/...
By bobflux , 18 hours ago
-
RE: Air to air bus grant installer anywhere
society and politics require things to be made more com...
By Batpred , 2 days ago
-
RE: Existing Solar Panel installation - structural roof calculation check
What will also happen is that they see that there is so...
By EtchedPixels , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
It's a great looking piece of kit and the 5kw is very q...
By avenir , 3 days ago
-
RE: Vaillant Arotherm Pro vs new Plus
So with the dedicated Hager CU, flipping the big red bu...
By Batpred , 5 days ago
-
Well I usually do it by feel, which is a slight problem...
By Transparent , 5 days ago
-
@jeff I am well aware of the riskiness of such investme...
By Toodles , 5 days ago
-
Fully understood and entirely reasonable! On the home ...
By JamesPa , 5 days ago