Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Help with heat pump sizing
I’m looking to install a heat pump but confused on how to size it and what units work best.
My calculated heat loss is 14kw (8kw fabric and 6kw ventilation based on 0.7 air changes). It’s an Edwardian house that we are refurbishing and extending and will end up around 380sqm. Design temp is -3 based on being in London.
I’ve been looking at mixture of units but I am confused by the heating output figures. Do I look at A7W35? Surely that doesn’t work at design temps of -3 where defrost is likely to bite? Also it seems as though A7W35 doesn’t match the quoted kw rating of the unit. I assume I’m looking at the wrong thing?
The units I’m considering/recommended by installers:
Steibel Eltron WCL AC25 has A7W35 of~8kw
Vailant arotherm 12kw has A7W35 of~8kw
Samsung EHS 16kw has A7W35 16
Grant Arona 15.5kw A7W35 16.6kw
Would appreciate a bit of help - thanks!
Posted by: @aminI’m looking to install a heat pump but confused on how to size it and what units work best.
My calculated heat loss is 14kw (8kw fabric and 6kw ventilation based on 0.7 air changes). It’s an Edwardian house that we are refurbishing and extending and will end up around 380sqm. Design temp is -3 based on being in London.
I’ve been looking at mixture of units but I am confused by the heating output figures. Do I look at A7W35? Surely that doesn’t work at design temps of -3 where defrost is likely to bite? Also it seems as though A7W35 doesn’t match the quoted kw rating of the unit. I assume I’m looking at the wrong thing?
The units I’m considering/recommended by installers:
Steibel Eltron WCL AC25 has A7W35 of~8kw
Vailant arotherm 12kw has A7W35 of~8kw
Samsung EHS 16kw has A7W35 16
Grant Arona 15.5kw A7W35 16.6kwWould appreciate a bit of help - thanks!
Unfortunately you will almost certainly need to go a layer deeper and look at the detailed specs (which are not always easy to find) to work out what the heat pump will do at your design flow temp and design air temp. Some of your figures are odd though eg Vaillant Arotherm 12kw has A7W35 of~8kw is incorrect see attached (but beware that Vaillant are allegedly not good at accounting for defrost so you may have to derate a bit around OAT0, particularly in the parts of London where its damp.
Sorry but there is no short circuit to this other than relying on the installer. Personally in your situation I would do the latter to give you cover, but check their workings
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
For the Vailant I’ve been looking at the values from pg49 of the operation manual attached and the page here
This seems different to the table in the doc you shared so I assume each is measuring something different?
I’m okay to rely on an installer but I also want to be able to verify and making sure I get something up to the task.
I dont think materially relative to this (I assume 'nominal' means the output at which they measure all the other various parameters)
But I agree its different to the page here, although the latter does also say 12.2kW at A-7W35. Not sure what the figures for A7/W35 or A2W35 are meant to signify, its the first time I had seen this table (Vaillant do keep changing exactly what they publish!). I cant see how they could possibly be max outputs because thats not how the thermodynamics works. Maybe they are trying to give representative figures for COP. A 12kW heat pump sized for -2C wont be running at anything like 12kW when its 7C, roughly half is about right but it sure is confusing. That however wouldnt explain the numbers at +2. Perhaps they are coming clean about the effects of deftost.
If you find out perhaps you could post here the answer, Im tempted to ask Vaillant myself!
PS I was tempted and I have. There is also a planning guide here
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 649 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 33 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 8 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 9 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 12 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 13 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 14 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 15 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 17 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 17 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 23 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago