Help with heat pump sizing
I’m looking to install a heat pump but confused on how to size it and what units work best.
My calculated heat loss is 14kw (8kw fabric and 6kw ventilation based on 0.7 air changes). It’s an Edwardian house that we are refurbishing and extending and will end up around 380sqm. Design temp is -3 based on being in London.
I’ve been looking at mixture of units but I am confused by the heating output figures. Do I look at A7W35? Surely that doesn’t work at design temps of -3 where defrost is likely to bite? Also it seems as though A7W35 doesn’t match the quoted kw rating of the unit. I assume I’m looking at the wrong thing?
The units I’m considering/recommended by installers:
Steibel Eltron WCL AC25 has A7W35 of~8kw
Vailant arotherm 12kw has A7W35 of~8kw
Samsung EHS 16kw has A7W35 16
Grant Arona 15.5kw A7W35 16.6kw
Would appreciate a bit of help - thanks!
Posted by: @aminI’m looking to install a heat pump but confused on how to size it and what units work best.
My calculated heat loss is 14kw (8kw fabric and 6kw ventilation based on 0.7 air changes). It’s an Edwardian house that we are refurbishing and extending and will end up around 380sqm. Design temp is -3 based on being in London.
I’ve been looking at mixture of units but I am confused by the heating output figures. Do I look at A7W35? Surely that doesn’t work at design temps of -3 where defrost is likely to bite? Also it seems as though A7W35 doesn’t match the quoted kw rating of the unit. I assume I’m looking at the wrong thing?
The units I’m considering/recommended by installers:
Steibel Eltron WCL AC25 has A7W35 of~8kw
Vailant arotherm 12kw has A7W35 of~8kw
Samsung EHS 16kw has A7W35 16
Grant Arona 15.5kw A7W35 16.6kwWould appreciate a bit of help - thanks!
Unfortunately you will almost certainly need to go a layer deeper and look at the detailed specs (which are not always easy to find) to work out what the heat pump will do at your design flow temp and design air temp. Some of your figures are odd though eg Vaillant Arotherm 12kw has A7W35 of~8kw is incorrect see attached (but beware that Vaillant are allegedly not good at accounting for defrost so you may have to derate a bit around OAT0, particularly in the parts of London where its damp.
Sorry but there is no short circuit to this other than relying on the installer. Personally in your situation I would do the latter to give you cover, but check their workings
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
For the Vailant I’ve been looking at the values from pg49 of the operation manual attached and the page here
This seems different to the table in the doc you shared so I assume each is measuring something different?
I’m okay to rely on an installer but I also want to be able to verify and making sure I get something up to the task.
I dont think materially relative to this (I assume 'nominal' means the output at which they measure all the other various parameters)
But I agree its different to the page here, although the latter does also say 12.2kW at A-7W35. Not sure what the figures for A7/W35 or A2W35 are meant to signify, its the first time I had seen this table (Vaillant do keep changing exactly what they publish!). I cant see how they could possibly be max outputs because thats not how the thermodynamics works. Maybe they are trying to give representative figures for COP. A 12kW heat pump sized for -2C wont be running at anything like 12kW when its 7C, roughly half is about right but it sure is confusing. That however wouldnt explain the numbers at +2. Perhaps they are coming clean about the effects of deftost.
If you find out perhaps you could post here the answer, Im tempted to ask Vaillant myself!
PS I was tempted and I have. There is also a planning guide here
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,426 Topics
- 55.1 K Posts
- 153 Online
- 6,104 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Is it normal to use power from the grid when running off the battery?
@batpred I may be asking you for more info in how you h...
By JohnnyB , 6 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
@johnnyb The noise of the Solis is nothing very sign...
By Batpred , 6 hours ago
-
RE: Is my Samsung gen6 outside air temp sensor missing a sheath/sleeve?
@papahuhu Yes, good information is often hard to find, ...
By Old_Scientist , 6 hours ago
-
RE: R290 and Foundation Air Bricks
Professional risk assessment (inc some common sense) ...
By ASHP-BOBBA , 7 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
@toodles ahhh no trouble yeah probably won't mess with ...
By Burtis , 7 hours ago
-
RE: Daikin Wireless Thermostat
@bash we have mostly south facing rooms which would ove...
By Judith , 8 hours ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
Some more examples of those that really should be benef...
By Jeff , 9 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
I've now had an interesting email from a Complaints Res...
By MairiA , 11 hours ago
-
RE: Reliable, easy to use home battery options
Correct. LiFePO₄ cells mustn't be charged if their te...
By Transparent , 11 hours ago
-
RE: Water outage in the the south-east
Indeed!Any contamination in the well water would be tra...
By Transparent , 13 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I hear some cases of apparent misconfiguration of inver...
By Batpred , 13 hours ago
-
Are split ASHPs with R290 refrigerant coming soon?
Question. Are there any (or likely to be in the near t...
By iotum , 15 hours ago
-
RE: Setback savings - fact or fiction?
Indeed. In many ways, a defrost is a setback, with the ...
By cathodeRay , 16 hours ago
-
RE: Heat pump not reaching flow temperature
The good news is that it leaves no excuse if it doesn't...
By JamesPa , 16 hours ago
-
RE: How to use my Hanchu battery storage for home without it feeding back into the grid?
@countryman-helmsley In that case is there a button ...
By IRMartini , 16 hours ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
Great. It’s not bad is it, though I agree it may repres...
By Davesoa , 18 hours ago
-
RE: Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
@f1p apologies, you are absolutely correct
By Patch321 , 18 hours ago
-
RE: Samsung E101 Error Message and my ASHP Efficiency
@johnnyb amazing that the our forum is serving its purp...
By Mars , 1 day ago
-
Best option for controller upgrade? - Grant Aerona
Fairly new heat pump owner - Grant Aerona 3 10kw - and ...
By Topher , 1 day ago
-
Just a brief update to keep things transparent. Secti...
By DREI , 2 days ago