Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Heat Pump Pipe Sizing Question

3 Posts
2 Users
1 Reactions
17 Views
trebor12345
(@trebor12345)
Estimable Member Member
Joined: 2 years ago
Posts: 148
Topic starter   [#2987]

I watched Mars' video yesterday on his heat pump install "What Does a Sub-Par Heat Pump Installation Actually Look Like?"

 

Got me thinking about pipe sizing from, the outdoor unit to the cylinder inside, for my new 3.5kw vaillant arotherm being installed in a few weeks time. 

The proposal was for 32mm PEX/PE-RT/Multilayer Pipe, has oxygen barrier. The run is 10m in total length.

In this case 32mm (26 mm ID) might be too large, and 25mm (20 mm ID) might be a better size. 

Can I have your thoughts please?

 


This topic was modified 53 minutes ago by trebor12345
This topic was modified 52 minutes ago by Mars

Hitachi Yutaki SCombi Heat Pump
(Indoor Unit ) RWD-3.0RW1E-220S-K
(Outdoor Unit) RAS-3WHVRP1

2024 build bungalow, Southern england, 179 m2, 14w/m2
Underfloor heating all fully open
7KW heat pump
50 litre buffer tank (4 port)
3.6KW solar panels


   
👍
1
Quote
Topic Tags
Mars
 Mars
(@editor)
Illustrious Member Admin
Joined: 5 years ago
Posts: 4560
 

Great that you're thinking about this before the installation... let's run the numbers.

For a 3.5 kW unit, plug it into the formula. Aiming for an efficient delta T of 5C:

Required flow = 3.5 ÷ (5 × 0.0698) = 10 litres per minute

That's a very modest flow requirement. At 10 L/min, even 22mm pipework would probably handle it comfortably... so 25mm with a 20mm internal diameter is absolutely fine for a run of 10 metres. Pressure drop and flow velocity will both be well within sensible limits.

The 32mm proposal isn't wrong... it's just oversized for a unit of this output, and on a short 10 metre run the difference in heat loss is negligible either way.

To my understanding, where oversizing external pipework becomes a real consideration is on much longer runs with larger units, where the additional thermal mass of water sitting in wider pipe can actually slow system response. Not really a concern at 3.5 kW over 10 metres IMO, but would be interested to hear what others think.


Get a copy of The Ultimate Guide to Heat Pumps

Subscribe and follow our YouTube channel!


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
Joined: 5 years ago
Posts: 4560
 

Does anyone think it would be helpful to have this as a simple calculator on the site?