Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Guidance with installing a new heating system
cement and sand mix, 7cm (5 for pipes + 2 on top), tiles all overPosted by: @hamilton
So 5m3 of mortar. With density 1.6-2 and thermal capacity 800-1000 J.kg/°C if the slab heats by 1°C that means 1.7-2.7 kWh is stored.
So you can store a bit of heat in the slab during the cheap kWh hours, but probably not enough to keep the house warm for the rest of the day.
Slab reaction time should be a few hours, so if you have large south facing windows letting in plenty of sun you may find it useful to use a thermostat to stop the heat pump when the sun heats the house enough. Otherwise it'll keep heating the slab and a few hours later when that heat gets released it gets too hot.
Now I see you have exterior insulation: if the walls are heavy masonry (stone/brick/concrete not hollow blocks) and not insulated on the inside, this adds a huge amount of thermal mass, quite effective at smoothing temperature variations. In this case you can probably exploit the cheap kWh hours more to store heat in the masonry, also store free heat from the sun.
PE-RT Type 1Posted by: @hamilton
This doesn't say whether it has EVOH oxygen barrier or not.
9 circuits, at 10cm centre to centre, planned layout image attached to this message.Posted by: @hamilton
10 cm, you're going for ultra low temperature then! Good for optimizing heat pump COP, but there are a few gotchas.
For example, if you run 25°C flow and ambient temperature is 20°C then you can't have 5°C deltaT between flow and return, more like 3°C, which means for the same power you need higher flow.
If the pipes are long, at low flow temperature, and low flow rate, you can get into a situation where most of the heat has left the pipe way before reaching the end, which gives uneven heating. A way to fix that: in rooms with 2 loops, just run the 2 loops together, ie route two pipes side by side, but reverse the flow direction of one pipe, a bit like a countercurrent heat exchanger. This gives more uniform floor temperature.
100m ID 13mm PEX pipe gives Kv ~ 0.43 m3/h (that's the flow for a pressure drop of 1 bar). With manifold/flowmeter losses you get about 3 l/min in this circuit for a circulator-friendly 2.8mH2O (0.28 bar) pressure. With 9 circuits that gives 27 l/min (1.6 m3/h) which is absolutely fine for your future heat pump, it gives 9.5kW at deltaT 5 which means it'll have enough flow to run at a much lower deltaT on a 5kW heat pump.
Note I'm assuming it's balanced for the same flow in all circuits, which means the shorter ones need to have the balancing valve throttled on the manifold. Otherwise all the flow goes to the shorter circuits and the longer ones don't heat.
I'd turn the 2x 105m circuits into 3x 70m circuits, making them closer in length to the others. That should make balancing much easier and less fiddly.
With good insulation, I think one pipe every 10cm is a bit overkill: I have one 20mm PEX pipe every 15cm and flow temperature is something like 25°C lol.
- 27 Forums
- 2,821 Topics
- 67 K Posts
- 2,234 Online
- 7,241 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
-
RE: Heat Geek heat pump quote: is £8,500 for labour reasonable?
By that reckoning, the £8,500 labour quote starts looki...
By Majordennisbloodnok , 3 hours ago
-
RE: Plug and play solar. Thoughts?
That's sensible. If those guys can deliver it at nigh...
By Transparent , 6 hours ago
-
RE: How quickly would you want/expect heat recovery to take from setback?
@rob-of-york no trickle vents and the humidity is prett...
By AndrewJ , 7 hours ago
-
RE: Issues with Samsung heat pump – high running costs and house dropping to 11C overnight
The previous descriptions sound like my system when I i...
By Singlespeed , 9 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
I am interested to see this post. I experienced similar...
By archway , 11 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@editor ASHP installed 18 months ago, so just starting ...
By IanWilson , 1 day ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@editor Aira visited this morning for our 2 year servic...
By MikeH , 1 day ago
-
Britain’s Heat Pump Shitshow has made it to sunny Tener...
By Mars , 1 day ago
-
RE: LiFePO4 lithium battery fires and explosions
Absolutely. All batteries store energy, and if that ene...
By cathodeRay , 1 day ago
-
RE: Got two or three heat pump quotes that don’t agree? Post them here.
The worst case part is where the label really fools you...
By mk1234 , 2 days ago
-
RE: Why don't people choose heat pumps?
That, in a nutshell, is why I think we, in the UK shoul...
By JamesPa , 2 days ago
-
Tell us about your heating system
We’ve added a few new fields to member profiles so that...
By Mars , 3 days ago
-
RE: Grant Aerona3 13kw - Buffer Tank - Heating Journey
@toodles Thank you 🙂 I think I'm quiet lucky as the...
By HeyMikey , 3 days ago