Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Guidance with installing a new heating system
cement and sand mix, 7cm (5 for pipes + 2 on top), tiles all overPosted by: @hamilton
So 5m3 of mortar. With density 1.6-2 and thermal capacity 800-1000 J.kg/°C if the slab heats by 1°C that means 1.7-2.7 kWh is stored.
So you can store a bit of heat in the slab during the cheap kWh hours, but probably not enough to keep the house warm for the rest of the day.
Slab reaction time should be a few hours, so if you have large south facing windows letting in plenty of sun you may find it useful to use a thermostat to stop the heat pump when the sun heats the house enough. Otherwise it'll keep heating the slab and a few hours later when that heat gets released it gets too hot.
Now I see you have exterior insulation: if the walls are heavy masonry (stone/brick/concrete not hollow blocks) and not insulated on the inside, this adds a huge amount of thermal mass, quite effective at smoothing temperature variations. In this case you can probably exploit the cheap kWh hours more to store heat in the masonry, also store free heat from the sun.
PE-RT Type 1Posted by: @hamilton
This doesn't say whether it has EVOH oxygen barrier or not.
9 circuits, at 10cm centre to centre, planned layout image attached to this message.Posted by: @hamilton
10 cm, you're going for ultra low temperature then! Good for optimizing heat pump COP, but there are a few gotchas.
For example, if you run 25°C flow and ambient temperature is 20°C then you can't have 5°C deltaT between flow and return, more like 3°C, which means for the same power you need higher flow.
If the pipes are long, at low flow temperature, and low flow rate, you can get into a situation where most of the heat has left the pipe way before reaching the end, which gives uneven heating. A way to fix that: in rooms with 2 loops, just run the 2 loops together, ie route two pipes side by side, but reverse the flow direction of one pipe, a bit like a countercurrent heat exchanger. This gives more uniform floor temperature.
100m ID 13mm PEX pipe gives Kv ~ 0.43 m3/h (that's the flow for a pressure drop of 1 bar). With manifold/flowmeter losses you get about 3 l/min in this circuit for a circulator-friendly 2.8mH2O (0.28 bar) pressure. With 9 circuits that gives 27 l/min (1.6 m3/h) which is absolutely fine for your future heat pump, it gives 9.5kW at deltaT 5 which means it'll have enough flow to run at a much lower deltaT on a 5kW heat pump.
Note I'm assuming it's balanced for the same flow in all circuits, which means the shorter ones need to have the balancing valve throttled on the manifold. Otherwise all the flow goes to the shorter circuits and the longer ones don't heat.
I'd turn the 2x 105m circuits into 3x 70m circuits, making them closer in length to the others. That should make balancing much easier and less fiddly.
With good insulation, I think one pipe every 10cm is a bit overkill: I have one 20mm PEX pipe every 15cm and flow temperature is something like 25°C lol.
- 27 Forums
- 2,783 Topics
- 65.6 K Posts
- 1,183 Online
- 7,187 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: How should the Boiler Upgrade Scheme be reformed?
Yes, their gas typically costs twice ours and electrici...
By Batpred , 1 hour ago
-
Over the years, due to the non barrier PEX underfloor h...
By bobflux , 2 hours ago
-
RE: Getting closer to a finished Haier system
All the 45° elbows required for getting the primaries i...
By Singlespeed , 3 hours ago
-
RE: Tesla Powerwall (2) Calibration Cycles
@papahuhu Likewise, the main ‘extra’ relates to TOU tar...
By Toodles , 9 hours ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
That sounds like a better approach (being able to see a...
By cathodeRay , 1 day ago
-
RE: DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
Thanks for the reference @jamespa I can't see any te...
By Transparent , 1 day ago
-
RE: battery storage without solar
Indeed, current on the grid input = current used for ch...
By bobflux , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu @papahuhu A lot of tears and sweat went into ...
By Andris , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We have the same problem, 12 mature trees clip the morn...
By Papahuhu , 2 days ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I had a battery and inverter installed a while ago, my ...
By Batpred , 2 days ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@ltron2 The EPC on our house is A-92, however that i...
By Rob of York , 2 days ago
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
The layout is confusing - much better like this: We b...
By downfield , 4 days ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
My experience, backed up by opinions from various frien...
By Majordennisbloodnok , 4 days ago
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
I had a meeting today with a company based out of Swede...
By Mars , 4 days ago
-
RE: Review your electricity provider
We were with Octopus in our old house and it was fault...
By ian33a , 4 days ago
Members Online
No online members at the moment