Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Guidance with installing a new heating system
cement and sand mix, 7cm (5 for pipes + 2 on top), tiles all overPosted by: @hamilton
So 5m3 of mortar. With density 1.6-2 and thermal capacity 800-1000 J.kg/°C if the slab heats by 1°C that means 1.7-2.7 kWh is stored.
So you can store a bit of heat in the slab during the cheap kWh hours, but probably not enough to keep the house warm for the rest of the day.
Slab reaction time should be a few hours, so if you have large south facing windows letting in plenty of sun you may find it useful to use a thermostat to stop the heat pump when the sun heats the house enough. Otherwise it'll keep heating the slab and a few hours later when that heat gets released it gets too hot.
Now I see you have exterior insulation: if the walls are heavy masonry (stone/brick/concrete not hollow blocks) and not insulated on the inside, this adds a huge amount of thermal mass, quite effective at smoothing temperature variations. In this case you can probably exploit the cheap kWh hours more to store heat in the masonry, also store free heat from the sun.
PE-RT Type 1Posted by: @hamilton
This doesn't say whether it has EVOH oxygen barrier or not.
9 circuits, at 10cm centre to centre, planned layout image attached to this message.Posted by: @hamilton
10 cm, you're going for ultra low temperature then! Good for optimizing heat pump COP, but there are a few gotchas.
For example, if you run 25°C flow and ambient temperature is 20°C then you can't have 5°C deltaT between flow and return, more like 3°C, which means for the same power you need higher flow.
If the pipes are long, at low flow temperature, and low flow rate, you can get into a situation where most of the heat has left the pipe way before reaching the end, which gives uneven heating. A way to fix that: in rooms with 2 loops, just run the 2 loops together, ie route two pipes side by side, but reverse the flow direction of one pipe, a bit like a countercurrent heat exchanger. This gives more uniform floor temperature.
100m ID 13mm PEX pipe gives Kv ~ 0.43 m3/h (that's the flow for a pressure drop of 1 bar). With manifold/flowmeter losses you get about 3 l/min in this circuit for a circulator-friendly 2.8mH2O (0.28 bar) pressure. With 9 circuits that gives 27 l/min (1.6 m3/h) which is absolutely fine for your future heat pump, it gives 9.5kW at deltaT 5 which means it'll have enough flow to run at a much lower deltaT on a 5kW heat pump.
Note I'm assuming it's balanced for the same flow in all circuits, which means the shorter ones need to have the balancing valve throttled on the manifold. Otherwise all the flow goes to the shorter circuits and the longer ones don't heat.
I'd turn the 2x 105m circuits into 3x 70m circuits, making them closer in length to the others. That should make balancing much easier and less fiddly.
With good insulation, I think one pipe every 10cm is a bit overkill: I have one 20mm PEX pipe every 15cm and flow temperature is something like 25°C lol.
- 27 Forums
- 2,816 Topics
- 66.7 K Posts
- 2,781 Online
- 7,230 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Should I change my cylinder when changing from a gas boiler to a heat pump.
I have 178 L Gledhill unvented cylinder which was fitte...
By David , 5 hours ago
-
RE: Plug and play solar. Thoughts?
Impressions so far from the one I've installed are that...
By EtchedPixels , 6 hours ago
-
-
@batpred The Daikin temperature probe protrudes from th...
By Toodles , 10 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@editor And as an occasional contributor, may I say wel...
By Toodles , 12 hours ago
-
RE: Should Households Who Can Afford It Pay More for Energy to Help Those Who Can't?
They don't have to try. Our entire system is d...
By EtchedPixels , 12 hours ago
-
RE: Why don't people choose heat pumps?
Fair enough. I guess I was thinking of pipes that run ...
By JamesPa , 12 hours ago
-
RE: How Can I Prove Coal Was My Main Heating Source Without Receipts?
Got excepted for the grant now so thanks for the replie...
By Chilli304 , 16 hours ago
-
Daikin Altherma 3 R F+W, room thermostat control, weath...
By JanHarley , 17 hours ago
-
RE: Buffer tank on a 2 x 14kw Ecodan system
Pretty much as I had guessed in my crude scaling from m...
By JamesPa , 20 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Well you have a vibration generator running at some fre...
By bobflux , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@downfield Thats a decent rate, I’m shocked they hadn...
By Papahuhu , 2 days ago
-
RE: Adventures in heat loss calculations
@toodles thanks! So as suspected, around a doubling of ...
By SusannaSaunders , 2 days ago
-
Six books in three years and I think I’ve now covered j...
By Mars , 3 days ago