Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Grant Aerona Setback
Posted by: @derek-mIn the right hand chart did you vary the Target LWT or was this done by the controller?
It's being varied by the controller's WC - see below where I've just shown the 'Target LWT' vs OAT (and compressor freq) for that same time period; the Target LWT just reflects the OAT. On the Grant, as you know, the WC curve is just a straight line.
For clarity, all values are coming directly from the Grant HP, apart from 'Target LWT' which I calculate based on the OAT and WC curve (line) as defined by the 4 control parameters. I'm confident the calculation is correct given the observed modulation of compressor frequency when LWT reaches the Target LWT. My long-term plan is to modulate the LWT based on IAT as well, but that's down the line - I have flow rates and zoning to work on first.
Grant Aerona 3 10kW
Posted by: @cathoderay@mikefl - a useful comparison, even if it is, I agree, a rather busy chart! There is a more marked spike, but there is also a notable dip after the spike, meaning we may want to consider the area under the curve, rather than moment by moment values. And, although it is a bigger spike, it isn't huge, eg the added area under the curve in the left hand chart caused by the spike isn't that large compared to the total area under the curve.
I was vaguely under the impression that modern compressors have a slow start up, ie they wind up slowly, rather than jamming straight away into top gear, precisely to limit start up current draw (and perhaps other things as well). That's why I think the 'start ups carry a heavy current penalty' thing may be a hang over from the older heat pumps, that no longer applies to newer ones.
I think that you will find that the 'soft' start for an electric induction motor is only over a period of seconds, to limit the current inrush.
The compressor will probably start unloaded, so running at full speed will only draw slightly higher current. The loading increases as the pressure within the system builds, making the compressor work harder.
Posted by: @mikeflMy long-term plan is to modulate the LWT based on IAT as well, but that's down the line
I'm already doing that, and most of the time it works, but I still have to iron out a bug, running my hourly auto-adaption script, which varies the LWT depending on the difference between the actual and desired IAT, terminates the DHW heating if it happens to be on when the script runs. I've just adjusted the code so that it will only run if the DHW is off, generally not a limit as the DHW, which is on a timer, usually only comes on between 1300 and 1400 daily.
Posted by: @derek-mI think that you will find that the 'soft' start for an electric induction motor is only over a period of seconds, to limit the current inrush.
The compressor will probably start unloaded, so running at full speed will only draw slightly higher current. The loading increases as the pressure within the system builds, making the compressor work harder.
I don't currently collect compressor frequency, but it appears to be available over modbus. I will add it, and we should then be able to see how amps and compressor frequency are related. That said, are we right to assume compressor frequency is a direct measure of how hard it is working?
Midea 14kW (for now...) ASHP heating both building and DHW
No and yes, compressor frequency denotes how fast the compressor is running. How hard it is working is dependent upon the pressure within the condenser.
Think of pumping up a bicycle tyre using a hand pump. When the pressure is low it is quite easy to operate the pump, but as the pressure builds, so does the amount of effort required to move the pump.
I have noticed with our A2A heat pump, when it first starts the compressor run quite fast, but the quantity of electrical energy being consumed is not too high. As the heat pump gets to the point of supplying thermal energy, the compressor slows, but the amps increase.
Obviously as the amount of thermal energy being produced increases, the compressor speed also needs to increase, since it is moving more refrigerant gas around the system.
It will be interesting to see how the compressor speed varies with thermal energy output.
Posted by: @derek-mIt will be interesting to see how the compressor speed varies with thermal energy output.
Here we go, data from the last few hours since I added compressor frequency to the data, as it happens a period of relative stability in OAT, though it has been breezy (wind chill and, in my case drafts):
I suppose it is pretty much as expected, high compressor frequency at start up, slows as it comes under load, with the small uptick in amps at startup? I haven't included the energy in/out bar chart because that is hourly data, minute by minute variations will be lost. In the above chart, given the flow rate remains constant, as does the specific heat of the fluid, the LWT/RWT delta t can act as a proxy for the thermal energy output.
Midea 14kW (for now...) ASHP heating both building and DHW
-
Thermostat for Ideal Logic Air with 3 zone support
9 months ago
-
Grant Aerona Setback
3 years ago
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 923 Online
- 6,993 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 7 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 8 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 11 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 12 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 13 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 14 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 16 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 16 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 22 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 23 hours ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago
-
@toodles That’s way better per kWp performance than our...
By Papahuhu , 6 days ago