Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Grant Aerona Setback
Posted by: @derek-mIn the right hand chart did you vary the Target LWT or was this done by the controller?
It's being varied by the controller's WC - see below where I've just shown the 'Target LWT' vs OAT (and compressor freq) for that same time period; the Target LWT just reflects the OAT. On the Grant, as you know, the WC curve is just a straight line.
For clarity, all values are coming directly from the Grant HP, apart from 'Target LWT' which I calculate based on the OAT and WC curve (line) as defined by the 4 control parameters. I'm confident the calculation is correct given the observed modulation of compressor frequency when LWT reaches the Target LWT. My long-term plan is to modulate the LWT based on IAT as well, but that's down the line - I have flow rates and zoning to work on first.
Grant Aerona 3 10kW
Posted by: @cathoderay@mikefl - a useful comparison, even if it is, I agree, a rather busy chart! There is a more marked spike, but there is also a notable dip after the spike, meaning we may want to consider the area under the curve, rather than moment by moment values. And, although it is a bigger spike, it isn't huge, eg the added area under the curve in the left hand chart caused by the spike isn't that large compared to the total area under the curve.
I was vaguely under the impression that modern compressors have a slow start up, ie they wind up slowly, rather than jamming straight away into top gear, precisely to limit start up current draw (and perhaps other things as well). That's why I think the 'start ups carry a heavy current penalty' thing may be a hang over from the older heat pumps, that no longer applies to newer ones.
I think that you will find that the 'soft' start for an electric induction motor is only over a period of seconds, to limit the current inrush.
The compressor will probably start unloaded, so running at full speed will only draw slightly higher current. The loading increases as the pressure within the system builds, making the compressor work harder.
Posted by: @mikeflMy long-term plan is to modulate the LWT based on IAT as well, but that's down the line
I'm already doing that, and most of the time it works, but I still have to iron out a bug, running my hourly auto-adaption script, which varies the LWT depending on the difference between the actual and desired IAT, terminates the DHW heating if it happens to be on when the script runs. I've just adjusted the code so that it will only run if the DHW is off, generally not a limit as the DHW, which is on a timer, usually only comes on between 1300 and 1400 daily.
Posted by: @derek-mI think that you will find that the 'soft' start for an electric induction motor is only over a period of seconds, to limit the current inrush.
The compressor will probably start unloaded, so running at full speed will only draw slightly higher current. The loading increases as the pressure within the system builds, making the compressor work harder.
I don't currently collect compressor frequency, but it appears to be available over modbus. I will add it, and we should then be able to see how amps and compressor frequency are related. That said, are we right to assume compressor frequency is a direct measure of how hard it is working?
Midea 14kW (for now...) ASHP heating both building and DHW
No and yes, compressor frequency denotes how fast the compressor is running. How hard it is working is dependent upon the pressure within the condenser.
Think of pumping up a bicycle tyre using a hand pump. When the pressure is low it is quite easy to operate the pump, but as the pressure builds, so does the amount of effort required to move the pump.
I have noticed with our A2A heat pump, when it first starts the compressor run quite fast, but the quantity of electrical energy being consumed is not too high. As the heat pump gets to the point of supplying thermal energy, the compressor slows, but the amps increase.
Obviously as the amount of thermal energy being produced increases, the compressor speed also needs to increase, since it is moving more refrigerant gas around the system.
It will be interesting to see how the compressor speed varies with thermal energy output.
Posted by: @derek-mIt will be interesting to see how the compressor speed varies with thermal energy output.
Here we go, data from the last few hours since I added compressor frequency to the data, as it happens a period of relative stability in OAT, though it has been breezy (wind chill and, in my case drafts):
I suppose it is pretty much as expected, high compressor frequency at start up, slows as it comes under load, with the small uptick in amps at startup? I haven't included the energy in/out bar chart because that is hourly data, minute by minute variations will be lost. In the above chart, given the flow rate remains constant, as does the specific heat of the fluid, the LWT/RWT delta t can act as a proxy for the thermal energy output.
Midea 14kW (for now...) ASHP heating both building and DHW
-
Thermostat for Ideal Logic Air with 3 zone support
9 months ago
-
Grant Aerona Setback
3 years ago
Currently viewing this topic 4 guests.
- 26 Forums
- 2,645 Topics
- 61.8 K Posts
- 381 Online
- 7,045 Members
Join Us!
Latest Posts
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
No, I agree entirely. There shouldn't be a need for an ...
By Majordennisbloodnok , 57 minutes ago
-
RE: How many people are happy with their ASHP and do you believe them?
I agree, and not. Energy prices are a largely politica...
By JamesPa , 2 hours ago
-
RE: Solar Produced vs Home Consumed
All inverters will use solar power in preference to dra...
By JamesPa , 2 hours ago
-
Yes, you will need to notify them even if the inverter ...
By Old_Scientist , 2 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 15 hours ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
I do the same: cool my large buffer (3000L) to 10C, pum...
By upnorthandpersonal , 23 hours ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 1 day ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I reached out to MCS directly last week on this and her...
By Mars , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 2 days ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 3 days ago
-
I will soon be struggling. Admittedly it is the summer,...
By Batpred , 3 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Not known yet. I've asked a local Councillor to follo...
By Transparent , 4 days ago