Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Flow rate issues?
When our 11.2KW Ecodan was serviced back in October the engineer remarked that the flow rate was a little on the low side, approx 20 litres/min. He didn't think it would cause any major issues, but just advised us to be aware of it.
Roll forward to the current cold snap, and we've a couple of issues, and I'm just wondering if they could be attributable to the low flow rate.
1. When running a water cycle (set to 45C) the flow temp rises to about 47C and stays there until the tank starts to get close to the target temperature and then seems to drop to about 45C. Sometimes the flow temp might creep up again to 46C, but generally it just sits at 45C still running the water heating cycle, presumably because the tank hasn't reached a high enough temperature for the controller to be satisfied. I now work around this by using the iBoost to give a quick 15 minute burst on the immersion heater when the tank temperature reaches about 40C. Probably ought to mention that we don't have an immersion connected to the controller. If I don't use the iBoost the water cycle will continue until it has reached the 60 minute heating time set by the controller, then go back to space heating for 30 minutes before starting the water cycle again. If left to its own devices it will just continue in this loop.
2. We have radiators upstairs and underfloor heating on the ground floor. Upstairs temperature is fine - sits at a fairly steady 19-20C, but ground floor rooms are a bit too low for our liking (17.5 - 18C). We are running weather compensation, set to 42C at -3C, 20C at 18C. With the outside temperature below 0C I am seeing a water temperature of about 30C at the UFH manifold, mixer valve is set to maximum (65C). UFH has its own circulating pump.
The main pump and the UFH pump are both set to their maximum speed.
Any thoughts before I call an engineer out to charge me £££££'s for diagnosing the problem?
Thanks
For a typical 5degK delta T between flow and return, to provide 11kW you ideally need 11/(5x4.2) = 0.524l/s or 31l/min. Suggest the flow needs to increase or check and adjust the deltaT setting on the Ecodan if possible. Generally, the lower you set the weather compensated maximum supply temperature, the higher the flow needs to be because the deltaT between flow and return decreases. That's just how the physics of heat loss works.
What flow temperature have you the hot water boost set to? Medium temperature ASHPs may struggle to reach 50degC flow temperature or higher at the moment due to the very cold weather and also periodically defrosting. The flow temperature goes up like a saw tooth blade. It keeps dropping back during each defrost cycle.
Posted by: @allyfishFor a typical 5degK delta T between flow and return, to provide 11kW you ideally need 11/(5x4.2) = 0.524l/s or 31l/min. Suggest the flow needs to increase or check and adjust the deltaT setting on the Ecodan if possible. Generally, the lower you set the weather compensated maximum supply temperature, the higher the flow needs to be because the deltaT between flow and return decreases. That's just how the physics of heat loss works.
What flow temperature have you the hot water boost set to? Medium temperature ASHPs may struggle to reach 50degC flow temperature or higher at the moment due to the very cold weather and also periodically defrosting. The flow temperature goes up like a saw tooth blade. It keeps dropping back during each defrost cycle.
I don't think the deltaT can be adjusted on the Ecodan - it's not something I can see in the controller manual.
The hot water flow temperature is, I assume, set by the controller on the basis of the desired tank temperature. Again, I can't see anything about setting it manually. It seems to reach about 2C above the desired temperature and then drop back down as the tank comes up.
We're currently defrosting about every 60 to 80 minutes, and it seems to take about 15 minutes from the start of a defrost before the flow temperature returns to what it was.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 285 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 2 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 16 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 16 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 19 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago