Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Fine tuning your ASHP performance
So you have had your ASHP installed and the installer has spent 2 minutes running you through the controls, which you promptly forget as soon as they leave the property.
A quick YouTube search refreshes your memory and you realise there are so many options for controlling your system. Internal thermostats, weather compensation curves, flow temps. But which one is the most efficient for your setup and how can you find that out.
I did start logging weekly performance data from the MMSP (Metering and Monitoring Service Package), changing room temperatures one week, flow temperatures the next but quickly realised that a simple comparison between weeks wasn't enough as outside temperatures were not the same.
I did have a quick look at compensation curves but was left unclear as to whether this was relevant to UK usage.
I currently only have 8 months of data. My MCS certificate stated a SCOP of 3.52. Not sure if that was the min, mean or max performance I should expect but it's currently bubbling around between 2.7 and 3.0. (October average outside temp is 13ºC, internal set to 22º with a flow temp of 50º)
So that is the subject of this topic. How can you systematically discover the optimal setup for your system?
Any suggestions welcome, and thanks.
Posted by: @markcSo you have had your ASHP installed and the installer has spent 2 minutes running you through the controls, which you promptly forget as soon as they leave the property.
A quick YouTube search refreshes your memory and you realise there are so many options for controlling your system. Internal thermostats, weather compensation curves, flow temps. But which one is the most efficient for your setup and how can you find that out.
I did start logging weekly performance data from the MMSP (Metering and Monitoring Service Package), changing room temperatures one week, flow temperatures the next but quickly realised that a simple comparison between weeks wasn't enough as outside temperatures were not the same.
I did have a quick look at compensation curves but was left unclear as to whether this was relevant to UK usage.
I currently only have 8 months of data. My MCS certificate stated a SCOP of 3.52. Not sure if that was the min, mean or max performance I should expect but it's currently bubbling around between 2.7 and 3.0. (October average outside temp is 13ºC, internal set to 22º with a flow temp of 50º)
So that is the subject of this topic. How can you systematically discover the optimal setup for your system?
Any suggestions welcome, and thanks.
If you find out,let me know!.
From my limited knowledge, weather compensation is a good thing. When it 13 degrees outside, my flow temps are high 30s (radiators) and it warms the house nicely. That's got to be better than 50 for a heat pump. I have only just got MMSP installed and it's not quite all working yet. Can you see the detailed data logs from yours? It's quite interesting to see how the energy consumption varies over time when the system starts up, etc.
I thought the MCS COP was the manufacturers standard rating (at a set flow temp, air temp, lab conditions), a bit like the mpg figures you see for cars. My real COP is similar to yours, maybe slightly higher.
Which heat pump/MMSP do you have?
Posted by: @kev-mPosted by: @markcSo you have had your ASHP installed and the installer has spent 2 minutes running you through the controls, which you promptly forget as soon as they leave the property.
A quick YouTube search refreshes your memory and you realise there are so many options for controlling your system. Internal thermostats, weather compensation curves, flow temps. But which one is the most efficient for your setup and how can you find that out.
I did start logging weekly performance data from the MMSP (Metering and Monitoring Service Package), changing room temperatures one week, flow temperatures the next but quickly realised that a simple comparison between weeks wasn't enough as outside temperatures were not the same.
I did have a quick look at compensation curves but was left unclear as to whether this was relevant to UK usage.
I currently only have 8 months of data. My MCS certificate stated a SCOP of 3.52. Not sure if that was the min, mean or max performance I should expect but it's currently bubbling around between 2.7 and 3.0. (October average outside temp is 13ºC, internal set to 22º with a flow temp of 50º)
So that is the subject of this topic. How can you systematically discover the optimal setup for your system?
Any suggestions welcome, and thanks.
If you find out,let me know!.
From my limited knowledge, weather compensation is a good thing. When it 13 degrees outside, my flow temps are high 30s (radiators) and it warms the house nicely. That's got to be better than 50 for a heat pump. I have only just got MMSP installed and it's not quite all working yet. Can you see the detailed data logs from yours? It's quite interesting to see how the energy consumption varies over time when the system starts up, etc.
I thought the MCS COP was the manufacturers standard rating (at a set flow temp, air temp, lab conditions), a bit like the mpg figures you see for cars. My real COP is similar to yours, maybe slightly higher.
Which heat pump/MMSP do you have?
Mitsubishi Ecodan 14Kw R32 with the MelCloud MMSP. I had 4 months of incorrect metering as they had been wired up incorrectly, registering energy output only, not consumption. So my first 4 months show a SCOP of 6500 🙂
Posted by: @markcPosted by: @kev-mPosted by: @markcSo you have had your ASHP installed and the installer has spent 2 minutes running you through the controls, which you promptly forget as soon as they leave the property.
A quick YouTube search refreshes your memory and you realise there are so many options for controlling your system. Internal thermostats, weather compensation curves, flow temps. But which one is the most efficient for your setup and how can you find that out.
I did start logging weekly performance data from the MMSP (Metering and Monitoring Service Package), changing room temperatures one week, flow temperatures the next but quickly realised that a simple comparison between weeks wasn't enough as outside temperatures were not the same.
I did have a quick look at compensation curves but was left unclear as to whether this was relevant to UK usage.
I currently only have 8 months of data. My MCS certificate stated a SCOP of 3.52. Not sure if that was the min, mean or max performance I should expect but it's currently bubbling around between 2.7 and 3.0. (October average outside temp is 13ºC, internal set to 22º with a flow temp of 50º)
So that is the subject of this topic. How can you systematically discover the optimal setup for your system?
Any suggestions welcome, and thanks.
If you find out,let me know!.
From my limited knowledge, weather compensation is a good thing. When it 13 degrees outside, my flow temps are high 30s (radiators) and it warms the house nicely. That's got to be better than 50 for a heat pump. I have only just got MMSP installed and it's not quite all working yet. Can you see the detailed data logs from yours? It's quite interesting to see how the energy consumption varies over time when the system starts up, etc.
I thought the MCS COP was the manufacturers standard rating (at a set flow temp, air temp, lab conditions), a bit like the mpg figures you see for cars. My real COP is similar to yours, maybe slightly higher.
Which heat pump/MMSP do you have?
Mitsubishi Ecodan 14Kw R32 with the MelCloud MMSP. I had 4 months of incorrect metering as they had been wired up incorrectly, registering energy output only, not consumption. So my first 4 months show a SCOP of 6500 🙂
That's interesting; same ASHP and MMSP but mine isn't registering energy output, only consumption. I'm trying to get the supplier back to fix it. Does yours monitor energy consumed from the ASHP and the Immersion/ancillaries separately? Mine doesn't and I think it should.
Posted by: @kev-mPosted by: @markcPosted by: @kev-mPosted by: @markcSo you have had your ASHP installed and the installer has spent 2 minutes running you through the controls, which you promptly forget as soon as they leave the property.
A quick YouTube search refreshes your memory and you realise there are so many options for controlling your system. Internal thermostats, weather compensation curves, flow temps. But which one is the most efficient for your setup and how can you find that out.
I did start logging weekly performance data from the MMSP (Metering and Monitoring Service Package), changing room temperatures one week, flow temperatures the next but quickly realised that a simple comparison between weeks wasn't enough as outside temperatures were not the same.
I did have a quick look at compensation curves but was left unclear as to whether this was relevant to UK usage.
I currently only have 8 months of data. My MCS certificate stated a SCOP of 3.52. Not sure if that was the min, mean or max performance I should expect but it's currently bubbling around between 2.7 and 3.0. (October average outside temp is 13ºC, internal set to 22º with a flow temp of 50º)
So that is the subject of this topic. How can you systematically discover the optimal setup for your system?
Any suggestions welcome, and thanks.
If you find out,let me know!.
From my limited knowledge, weather compensation is a good thing. When it 13 degrees outside, my flow temps are high 30s (radiators) and it warms the house nicely. That's got to be better than 50 for a heat pump. I have only just got MMSP installed and it's not quite all working yet. Can you see the detailed data logs from yours? It's quite interesting to see how the energy consumption varies over time when the system starts up, etc.
I thought the MCS COP was the manufacturers standard rating (at a set flow temp, air temp, lab conditions), a bit like the mpg figures you see for cars. My real COP is similar to yours, maybe slightly higher.
Which heat pump/MMSP do you have?
Mitsubishi Ecodan 14Kw R32 with the MelCloud MMSP. I had 4 months of incorrect metering as they had been wired up incorrectly, registering energy output only, not consumption. So my first 4 months show a SCOP of 6500 🙂
That's interesting; same ASHP and MMSP but mine isn't registering energy output, only consumption. I'm trying to get the supplier back to fix it. Does yours monitor energy consumed from the ASHP and the Immersion/ancillaries separately? Mine doesn't and I think it should.
It will be a simple wire in the wrong place but you need someone who knows what they are doing to fix it. No, it just measures DHW and Heating as two inputs/outputs.
We have the DHW set to be on 24/7 and maintain 50º with a 5º drop to trigger a reheat. From my understanding the only time the immersion would be used is if you drain the tank and need more hot water quickly, so manually turn the DHW heating on or when the legionella cycle runs.
I have a 250l tank and have never totally drained it of hot water.
Posted by: @markcSo you have had your ASHP installed and the installer has spent 2 minutes running you through the controls, which you promptly forget as soon as they leave the property.
A quick YouTube search refreshes your memory and you realise there are so many options for controlling your system. Internal thermostats, weather compensation curves, flow temps. But which one is the most efficient for your setup and how can you find that out.
I did start logging weekly performance data from the MMSP (Metering and Monitoring Service Package), changing room temperatures one week, flow temperatures the next but quickly realised that a simple comparison between weeks wasn't enough as outside temperatures were not the same.
I did have a quick look at compensation curves but was left unclear as to whether this was relevant to UK usage.
I currently only have 8 months of data. My MCS certificate stated a SCOP of 3.52. Not sure if that was the min, mean or max performance I should expect but it's currently bubbling around between 2.7 and 3.0. (October average outside temp is 13ºC, internal set to 22º with a flow temp of 50º)
So that is the subject of this topic. How can you systematically discover the optimal setup for your system?
Any suggestions welcome, and thanks.
Markc, I am sorry to say but with a flow temperature of 50 deg C at this time of year, I hope you have a very big pocket because your bill is going to be very high. It appears that your system has been very poorly designed and set up and certinly, with a predicted SCOP of 3.52, not designed for performance but for low installation cost. The flow temperature should be in the high 20's at this time of year.
SCOP is the anual average performance or total heat produced by the machine divided by the electricity used. At this time of year you should be runnig at above 5. Here is a picture from one of my installations.
@heacol, I had no idea the flow temperature should be so low (20C) in November. We're currently running at 35C (manually set) at it feels about right - COP at just over 3 for later September to today.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor Mars, your unit had a co of 3, My customers had a COP of 5. He has used nearly halve the electricity you have to do the same job, that will be the same for every month of the year. His house has no thermostats and the house is treated as a single zone with TRV's the bedroom radiators to reduce the temperatures there. The heat pimp controlls the temperature in the living areas, all living areas and batherooms are kept at the same temperatures. It is contrary to the normal thinking, but it works.
@heacol, does you customer have very good/excellent insulation?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @heacol@editor Low flow temperatures = low bills. It realy is that simple.
Fabric first to achieve low flow temperatures I guess. Our insulation is good to very good, but we still leak some heat. Getting better though.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor No, it is a 1930's ex council house with cavity wall insulation, double galzing installed about 20 years ago and 250 mm of rockwool in the loft.
A standard off the shelf ex-councill house.
You are correct, it should always be fabrick first, however it is not always necessary or economical.
Your house is your house, some are leaky and others are passive, it is not always possable or make economical sence to make a leaky solid stone house in to a passive pouse. What does make economical sence is to replce a bad fossel fuel system with a reneawble low carbon heating system that is cheaper to run and provides a better living enviroment.
If you have to play with your system there is something wrong. Initially there should be some tweeking but after that, it should just work without any intervention. If your flow temperature is high, is is caused by one of 2 things:- firstly, there are too many levels of controwl, "too many chefs spoil the broth", this is easy to fix, just remove them and allow the heat pump to do it's job. The second is your emmitters are too small or you are not giving then mime to react. Please remember that 80% of a radiator's output is through convection, the lower the flow temperature the longer the convections takes to work (up to 4 hours).
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
4 weeks ago
-
Running my new Nibe ASHP efficiently
4 months ago
-
Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
9 months ago
-
Ecodan consuming 100kwh per day in new build!!!
10 months ago
-
Help with understanding my Mitsubishi Ecodan air source heat pump
1 year ago
Currently viewing this topic 2 guests.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 724 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 1 hour ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 9 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 10 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 13 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 14 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 14 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 15 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 18 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 18 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 23 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago