Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Fine tuning my Steibel Eltron wpl17 ASHP
Hi All
I've had my ASHP installed now since October and am beginning to understand how it works etc
We are generally happy with the system, we're not cold nor have issues with water
So I am turning my attention to trying to get the system running as efficiently as possible,
The scop so far is 3.64 and seems to now be rising, (the other day it was 3.72 when it was - 1 and a milder day 4.0) I am working this out by dividing heat generated kW with power usage kW (which is what the installer and manufacturer suggests)
Usage so far is approx 14kw per day since being fitted on heating, water is fairly negligible overall.
The unit is a steibel eltron wpl17 and does have a weather compensation mode, its curve is set as 1.0 and the system seems to overshoot the temperature, our daytime temp is 19 and it does always go to 20. I was considering dropping the curve to 0.8.
The rads were all new with all new pipework (mainly 22mm with 15mm off shoots) and rads are all stelrad k2.
Heat loss on property is 6112kw.
I can also manually adjust flow rate and kelvin if that helps but I think the complexity of all the settings is where I'm somewhat stumped.
Any ideas? Happy to provide any details needed, manuals etc
Your numbers sound quite good. Is that heat loss at design settings? Where do you live; that makes a difference too? Similar numbers for me are: about 20kWh/day from October for a 160m2 house with a heat loss at -3C of c.8000kW, heated to about 21C. Do you have averages for a shorter time, say December to date?
I don't know anything about your ASHP but are you controlling it through room thermostats? If you can reduce the flow temperature by adjusting the compensation curve and it still heats your house that's going to be worth a try. I can heat my house with my K2 radiators at 35-40C in all the weather we've had this year so far.
I think @Derek-M is looking for you too.
Hi Kev
A few questions to your qs
Heat loss at design? What does that mean? Heat loss was based on u values and done using the mcs calculator by the installer
Live in Suffolk, I think it was done as heating home to 20/21c when it is - 2 outside
I'll check re averages for a shorter period
Controlled by a thermostat in upstairs hallway and a timer for when it calls for heat at 19c and an eco mode for overnight at 15.5c (never really comes on, think twice?)
Posted by: @hr_3Hi All
I've had my ASHP installed now since October and am beginning to understand how it works etc
We are generally happy with the system, we're not cold nor have issues with water
So I am turning my attention to trying to get the system running as efficiently as possible,
The scop so far is 3.64 and seems to now be rising, (the other day it was 3.72 when it was - 1 and a milder day 4.0) I am working this out by dividing heat generated kW with power usage kW (which is what the installer and manufacturer suggests)
Usage so far is approx 14kw per day since being fitted on heating, water is fairly negligible overall.
The unit is a steibel eltron wpl17 and does have a weather compensation mode, its curve is set as 1.0 and the system seems to overshoot the temperature, our daytime temp is 19 and it does always go to 20. I was considering dropping the curve to 0.8.
The rads were all new with all new pipework (mainly 22mm with 15mm off shoots) and rads are all stelrad k2.
Heat loss on property is 6112kw.
I can also manually adjust flow rate and kelvin if that helps but I think the complexity of all the settings is where I'm somewhat stumped.
Any ideas? Happy to provide any details needed, manuals etc
Hi Hr_3,
As you have suggested, I would recommend changing the weather compensation curve from 1.0 to 0.8. Then use the Comfort Level setting to achieve the desired temperature.
Looking at your operating data I would say that your heat pump appears to be working quite efficiently, and other than the above change I don't think that there is much more that can be improved.
- 27 Forums
- 2,775 Topics
- 65.4 K Posts
- 2,964 Online
- 7,180 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
Yes, and I would suggest likely to get worse with more ...
By Batpred , 5 hours ago
-
RE: Electricity price predictions
This topic seems more suitable for this thread... I a...
By Batpred , 5 hours ago
-
RE: Why are ASHP installs so expensive?
It is clearly difficult to say, there must be cases whe...
By Batpred , 5 hours ago
-
RE: Who's your electricity provider and what's your tariff?
Hi all, I'm new to this game having spent the last 25...
By gz00 , 6 hours ago
-
RE: Panasonic Free Multi Z and Etherea Internal units.
@dgclimatecontrol Thank you for that information and re...
By Toodles , 10 hours ago
-
RE: My Kronoterm Adapt 0312 ASHP is finally installed!
@editor It was serendipitous really. Both my wife and I...
By tomasmcguinness , 15 hours ago
-
@mrkfm, I'd also suggest that whenever you're ready, st...
By Mars , 1 day ago
-
RE: Are you planning to use a wood burner to supplement your central heating this winter?
I use my stove daily for backup and comfort. Definitely...
By Margarethomas , 1 day ago
-
@rob-of-york Thanks. I wish I'd started on this site as...
By mrkfm , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@downfield I just checked this morning and OE just r...
By Papahuhu , 2 days ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
Thanks Will. I'll probably be a week or so before get...
By Singlespeed , 2 days ago
-
RE: Cooling using an air to water heat pump
From experience this summer, a single-split A2A unit on...
By Rob of York , 2 days ago
-
Analysis of the economics of switching to an A2W ASHP compared to other heat sources
This post aims to analyse the economics of installing, ...
By Rob of York , 3 days ago
-
RE: Cooling with air to water heat pumps
@editor does that mean you have to have two separate ex...
By mrkfm , 4 days ago