Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Fine tuning my Steibel Eltron wpl17 ASHP
Hi All
I've had my ASHP installed now since October and am beginning to understand how it works etcÂ
Â
We are generally happy with the system, we're not cold nor have issues with waterÂ
So I am turning my attention to trying to get the system running as efficiently as possible,Â
The scop so far is 3.64 and seems to now be rising, (the other day it was 3.72 when it was - 1 and a milder day 4.0) I am working this out by dividing heat generated kW with power usage kW (which is what the installer and manufacturer suggests)Â
Usage so far is approx 14kw per day since being fitted on heating, water is fairly negligible overall.
The unit is a steibel eltron wpl17 and does have a weather compensation mode, its curve is set as 1.0 and the system seems to overshoot the temperature, our daytime temp is 19 and it does always go to 20. I was considering dropping the curve to 0.8.
The rads were all new with all new pipework (mainly 22mm with 15mm off shoots) and rads are all stelrad k2.
Heat loss on property is 6112kw.
I can also manually adjust flow rate and kelvin if that helps but I think the complexity of all the settings is where I'm somewhat stumped.
Â
Any ideas? Happy to provide any details needed, manuals etc
Your numbers sound quite good. Is that heat loss at design settings? Where do you live; that makes a difference too?  Similar numbers for me are: about 20kWh/day from October for a 160m2 house with a heat loss at -3C of c.8000kW, heated to about 21C. Do you have averages for a shorter time, say December to date?
I don't know anything about your ASHP but are you controlling it through room thermostats? If you can reduce the flow temperature by adjusting the compensation curve and it still heats your house that's going to be worth a try. I can heat my house with my K2 radiators at 35-40C in all the weather we've had this year so far. Â
I think @Derek-M is looking for you too.
Hi Kev
A few questions to your qs
Heat loss at design? What does that mean? Heat loss was based on u values and done using the mcs calculator by the installer
Live in Suffolk, I think it was done as heating home to 20/21c when it is - 2 outside
I'll check re averages for a shorter period
Controlled by a thermostat in upstairs hallway and a timer for when it calls for heat at 19c and an eco mode for overnight at 15.5c (never really comes on, think twice?)Â
Posted by: @hr_3Hi All
I've had my ASHP installed now since October and am beginning to understand how it works etcÂ
Â
We are generally happy with the system, we're not cold nor have issues with waterÂ
So I am turning my attention to trying to get the system running as efficiently as possible,Â
The scop so far is 3.64 and seems to now be rising, (the other day it was 3.72 when it was - 1 and a milder day 4.0) I am working this out by dividing heat generated kW with power usage kW (which is what the installer and manufacturer suggests)Â
Usage so far is approx 14kw per day since being fitted on heating, water is fairly negligible overall.
The unit is a steibel eltron wpl17 and does have a weather compensation mode, its curve is set as 1.0 and the system seems to overshoot the temperature, our daytime temp is 19 and it does always go to 20. I was considering dropping the curve to 0.8.
The rads were all new with all new pipework (mainly 22mm with 15mm off shoots) and rads are all stelrad k2.
Heat loss on property is 6112kw.
I can also manually adjust flow rate and kelvin if that helps but I think the complexity of all the settings is where I'm somewhat stumped.
Â
Any ideas? Happy to provide any details needed, manuals etc
Hi Hr_3,
As you have suggested, I would recommend changing the weather compensation curve from 1.0 to 0.8. Then use the Comfort Level setting to achieve the desired temperature.
Looking at your operating data I would say that your heat pump appears to be working quite efficiently, and other than the above change I don't think that there is much more that can be improved.
Â
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 2,684 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
I am amazed that there is not something out there to me...
By JamesPa , 1 hour ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 7 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 12 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 2 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 4 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 5 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago