Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan 6kW - is it "cycling", or normal operation?
I'm struggling to understand the "logic" used by the FTC6 to run the compressor and pumps.
Graphs from today, 8 degrees OAT, WC curve target is 40 degrees
Graph shows flow temp and power consumption for the complete setup over a couple of 20 minute cycles.
The first part of each cycle makes sense - compressor starts up, flow temp increases. Compressor runs harder, flow temp increases further. Reaches target temp, compressor backs off a bit.
Flow temp stabilises for a bit, then everything shuts off - including both pumps. Flow temp is steady, because the water isn't moving.
After 2 minutes, the pumps start up, flow temp drops rapidly.
3 minutes later, the compressor starts up again.
I don't understand why everything switches off when the flow temp is stable?
I don't understand why both pumps switch off the instant that the compressor stops?
The reason why the pumps were stopping is because the heating was switching off.
The Evohome controller starts "modulating" the BDR91 boiler relay as all the TRVs get to within 1 degree of target temperature. Since it can only modulate by switching off, it starts cycling every 20 minutes (the minimum number of cycles, set in the system configuration).
After a few minutes, the Evohome boiler relay switches on again, the pumps start running, flow & return temps start to drop, and the compressor switches on.
This wasn't happening before, because it was cold outside, and a couple of rooms weren't getting close to target temperature. Evohome was continuously calling for heat.
Main culprit was the bathroom, losing a lot of heat through the extractor fan ducting. The electrician had removed the baffle flaps, because they fouled the flexible ducting. I've refitted the flaps, modified the ducting, and they now work. Much less heat loss, bathroom gets up to temperature, so now the Evohome is cycling.
Not sure what to do about this?
I guess I could disconnect the boiler relay, and just use the Mitsubishi wireless remote as a the controlling thermostat, and the Evohome as adjustable TRVs (without any "call for heat" function)?
I'd have to find a suitable location for the Mitsubushi wireless remote though - somewhere that it actually has some control over the heatpump, but doesn't switch it off too soon.
@clockworks That all makes perfect sense and highlights that heat pumps don't need external control from on/off boiler thermostats they just hamper performance.
Sounds like moving the wireless thermostat is the correct option for you. Hope it works out for you.
Rather than disconnecting the Evohome boiler relay, I've added a switch across the relay contacts. This way, I can either have it on continuously, or flip it back and give Evohome control.
The boiler relay was just wired up as a "zero volt" thermostat to the FTC6 - closed circuit for heat, open circuit for no heat.
With the switch closed, Evohome will just be controlling a few TRVs as limiters, while the Mitsubishi remote is doing the "call for heat" and controlling the heat pump. Basically the same as if I was just using a few wax TRVs, but programmable.
Now that I'm back in pure WC mode, I don't think the wireless remote will be having any influence, apart from "on or off"?
- 26 Forums
- 2,724 Topics
- 63.8 K Posts
- 668 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Microgeneration Certification Scheme (MCS)
I’ve just spotted that Ian Rippin is leaving MCS as CEO...
By Mars , 32 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
Hi. I have 16 panel solar panels producing about 20k...
By peterackstraw , 5 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 6 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 20 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago