Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan 11.2 KW Flow Rate
Hi,
I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.
In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Most of the plumbing to the outdoor unit is 28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?
Thanks.
Posted by: @elabHi,
I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.
In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Most of the plumbing to the outdoor unit is 28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?
Thanks.
The FTC6 manual suggests 14-32 l/min as the acceptable range so 32 would be right at the upper end. My 14kW Ecodan is running at about 24l/min, also well within the acceptable range. The most I have seen it output is 12-13kW so I'm fairly happy and so was the engineer who serviced it. My delta T probably averages nearer 4 than 5.
I would guess your ASHP will never need to deliver 11.2kW constantly in a steady state. It'll do it in bursts when heating the house up, defrosting, heating DHW, etc.
How is the ASHP working otherwise?
Posted by: @elabIn the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Hi @elab
How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?
in your post I can’t see what your current temperature difference (DeltaT) is.
If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature.
As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.
you can check your current flow rate on your main controller screen.
hope this helps.
Posted by: @sunandairPosted by: @elabIn the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Hi @elab
How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?
in your post I can’t see what your current temperature difference (DeltaT) is.
If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature.
As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.
you can check your current flow rate on your main controller screen.
hope this helps.
@sunandair, @elab hasn't been seen on the forum since 1st May so I don't think s/he is worthy of any more attention!
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 134 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 7 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 7 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 7 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 8 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 9 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 10 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 12 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 12 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 14 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 17 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 20 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago