Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Ecodan 11.2 KW Flow Rate

5 Posts
3 Users
0 Reactions
3,973 Views
 elab
(@elab)
New Member Member
Joined: 3 years ago
Posts: 1
Topic starter   [#958]

Hi,

I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.

In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min

My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.

Most of the plumbing to the outdoor unit is  28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?

Thanks.



   
Quote
(@kev-m)
Noble Member Member
Joined: 5 years ago
Posts: 1276
 

Posted by: @elab

Hi,

I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.

In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min

My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.

Most of the plumbing to the outdoor unit is  28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?

Thanks.

The FTC6 manual suggests 14-32 l/min as the acceptable range so 32 would be right at the upper end.  My 14kW Ecodan is running at about 24l/min, also well within the acceptable range.  The most I have seen it output is 12-13kW so I'm fairly happy and so was the engineer who serviced it. My delta T probably averages nearer 4 than 5.    

I would guess your ASHP will never need to deliver 11.2kW constantly in a steady state.  It'll do it in bursts when heating the house up, defrosting,  heating DHW, etc. 

How is the ASHP working otherwise? 

 

 



   
ReplyQuote
SUNandAIR
(@sunandair)
Honorable Member Member
Joined: 3 years ago
Posts: 569
 

Posted by: @elab

In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min

My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.

 

Hi @elab 

How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?

in your post I can’t see what your current temperature difference (DeltaT) is. 

If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature. 

As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.

you can check your current flow rate on your main controller screen.

hope this helps.

 



   
ReplyQuote



(@kev-m)
Noble Member Member
Joined: 5 years ago
Posts: 1276
 

Posted by: @sunandair

Posted by: @elab

In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min

My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.

 

Hi @elab 

How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?

in your post I can’t see what your current temperature difference (DeltaT) is. 

If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature. 

As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.

you can check your current flow rate on your main controller screen.

hope this helps.

 

@sunandair, @elab hasn't been seen on the forum since 1st May so I don't think s/he is worthy of any more attention! 

 



   
ReplyQuote
SUNandAIR
(@sunandair)
Honorable Member Member
Joined: 3 years ago
Posts: 569
 

Thanks @kev-m 

I was beginning to wonder, when they hadn’t responded to your post. But I thought “you never know”.

thanks for your comment.



   