Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Discussion on buffer tanks and heat pumps
Now my install has been plumbed correctly I've turned my attention to the buffer, backup heater and external circulation pump as I believe these are put in purely out of laziness/lack of expertise of the designers, whereas in fact they are making the install and run far more complicated and expensive with these items installed. Get the customers to pay for these extras and pay again in wasted energy using them, so no reason for designers to worry about doing it properly.
There are some key mentions in the Daikin manual which are flags, and just as key there is zero mention of adding an external (CH Circ) pump to the CH system.
the only mention of a field supply pump is here:
My install has a 50 litre buffer, a Grundfos circulation pump and a Backup Heater. So, according to the specs, with a backup heater the minimum volume of water is just 20 litres, that's about 3 radiators panels/ large towel rails. I have the equivalent of 11 doubles, which is 144 litres plus the pipework. So in no circumstance would the install need a buffer tank. That 50 litre buffer represents about 33% of the total volume of the install, so that's 33% lost efficiency, 33% more expense in bills.
Now I have never seen a design for the system, it will be interesting what the handover pack will include.
I have also done some experiments on the CH Circ pump speed.
Turning it off or up to full speed doesn't affect the flow rate displayed on the unit, which must mean the internal pump is pushing water faster than the external Grundfos.
Turning the Grundfos off negatively impacts the CH flow, all the Rads went cold even though the F&R temps on the Daikin were at 37/35. Which means the buffer was acting as a bypass to the heating system without that extra Grundfos inertia
Turning the Grundfos to the slowest speed restored warmth to the Rads and the flow in and out of the buffer was <0.2C (delta).
At the moment my only interest is getting it through RHI. I'm not going to start messing with the layout as I need that MCS certificate but its something I will deal with later. A simple bypass of the buffer or ripping it out completely are my thoughts.
Giving this further thought, the buffer tank should only ever be in circuit as part of an automatic bypass system in case of end user error closing all the Rad valves.
......and in my case limited to a 20l buffer tank
some good analysis there. Have you thought of a change in career?
Seriously though, it isn't right that customers/users end up having to know more about their heating systems that the so-called experts. Imagine if you had to tell your electrician how to rewire your house.
Kev
- 27 Forums
- 2,744 Topics
- 64.4 K Posts
- 1,131 Online
- 7,148 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@toodles A daily court feast for luncheon would be enou...
By Papahuhu , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks, however that's an answer to a subtly different ...
By JamesPa , 13 hours ago
-
RE: Flushing system, cleaning and inhibitor
Yes, my 50L volumiser uses the two lower ports, so ther...
By Old_Scientist , 16 hours ago
-
I've been thinking about this and can't help but feel t...
By Majordennisbloodnok , 18 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Such elegant symmetry. look at my lumpy bag of...
By Papahuhu , 2 days ago
-
RE: PV and battery long payback - sense check query
Quite probably not, but you can get a 32A relay and a S...
By JamesPa , 2 days ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
@ian-s Look forward to making contact soon! Regards, To...
By Toodles , 2 days ago
-
I don't notice mine defrosting, and most of the time Im...
By JamesPa , 3 days ago
-
RE: Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
Kind of you, @calumm, but it was @f1p who did the heavy...
By Majordennisbloodnok , 3 days ago
-
RE: Electricity price predictions
2. As EV ownershp increases it'll certainly increase de...
By EtchedPixels , 4 days ago
-
I meant to say I cannot register my kit at Energyplus… ...
By Batpred , 4 days ago
-
RE: HomeTherma Is Live: A New Home-Energy Platform Built Around the Homeowner
Signed up!
By bobflux , 5 days ago