Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Daikin problem
Posted by: @togfather@toodles Thank you for this. I will give it a try 🙂
Although this is generally good advice, as @iancalderbank pointed out, you need to get the very low flow rate fixed first in order to get heat into your house.
@togfather the flow rate is crucial. If that stays at 10.7, you will never move enough heat, there is basic physics in the way, the rate of movement of the water is directly related to the rate of the heat movement, it needs to be 20-25l/m at least.
I don't know enough about daikin to know if there could be some setting causing it to be low. If you are able to turn off the backup heater, please see if that makes any difference to the flow rate, if not then something else may be required.
@toodles @chrislay can you help with where are the pump speed settings on a daikin?
regarding your installer and daikin
1. they are just plain wrong about weather comp costing money. the point of weather comp is that it reduces the heat pumps power in proportion to how warm it is outside (or increases it in proportion to how cold, if you like). The times when its mild spent running at lower power , saves you money. (Bit more to it than that, but thats the "in a nutshell")
2. The low flow rate is a clear and obvious demonstrable fault with the system. There is no way they can "debate" whether its large enough. Its not, the system will never move enough heat to warm your house with this low flow rate. You can legitimately keep on calling them back, asking for your money back, until they get this value to where it should be.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank I have just looked in the Daikin Installer’s Manual and I am attaching a screen grab of the relevant part of a page about pump volume. I am confused to say the least! With my sight and having to magnify the image on my iPad, navigating the pages is very awkward. I will try to find HOW to adjust the flow rate but meanwhile, at the bottom of the image is the manual details so that Tog can look it up if not in possession of a printed copy.
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Just found this link for the manual in case it helps you.
Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
I’ve done my best as my sight allows for now, may I suggest Togfather that you look at section 8 on configuration where you will find mention of the back up heater. My system doesn’t have such a heater and therefore, I don’t wish to rootle through the configuration which may not be the same anyway! I’m glad my installers set up my pump correctly, it sounds like your is a real nightmare job and the installer should be putting it right for you - compensation?
Regards, Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
@iancalderbank I don't know if you can set the actual pump speed. As far as I know the controller sets the speed to maintain the delta t. 10.7 is the minimum and the max is about 40. It will then switch the compressor on/off as well. I think the default dt is 7 or 8.
One other thought - did the installer upgrade any pipework? - oil may have been piped with 22mm - that will be too small.
-
Daikin 6kw setup with Dixell controller
9 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
1 year ago
-
Heating Turned Off but Radiators Still Warm
1 year ago
-
How can we prevent our LG heat pump from freezing up in cold weather?
2 years ago
-
Daikin Error Code 7H05
2 years ago
Currently viewing this topic 4 guests.
- 27 Forums
- 2,821 Topics
- 67 K Posts
- 2,462 Online
- 7,240 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Heat Geek heat pump quote: is £8,500 for labour reasonable?
I think much of this looks beyond the real problem whic...
By EtchedPixels , 3 hours ago
-
The portable induction hobs will run at a few hundred w...
By EtchedPixels , 3 hours ago
-
RE: Issues with Samsung heat pump – high running costs and house dropping to 11C overnight
@jamespa Will do, cheers. The plumber who ca...
By JWilliams89 , 3 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@editor ASHP installed 18 months ago, so just starting ...
By IanWilson , 4 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@editor Aira visited this morning for our 2 year servic...
By MikeH , 4 hours ago
-
Britain’s Heat Pump Shitshow has made it to sunny Tener...
By Mars , 11 hours ago
-
RE: LiFePO4 lithium battery fires and explosions
Absolutely. All batteries store energy, and if that ene...
By cathodeRay , 13 hours ago
-
RE: Got two or three heat pump quotes that don’t agree? Post them here.
The worst case part is where the label really fools you...
By mk1234 , 14 hours ago
-
RE: Why don't people choose heat pumps?
That, in a nutshell, is why I think we, in the UK shoul...
By JamesPa , 1 day ago
-
RE: How quickly would you want/expect heat recovery to take from setback?
You may notice that Mars is advertising a book called '...
By JamesPa , 1 day ago
-
Tell us about your heating system
We’ve added a few new fields to member profiles so that...
By Mars , 2 days ago
-
RE: Grant Aerona3 13kw - Buffer Tank - Heating Journey
@toodles Thank you 🙂 I think I'm quiet lucky as the...
By HeyMikey , 2 days ago
-
RE: Buffer tank on a 2 x 14kw Ecodan system
@fosterl2 I'm sure it's over simplified as there'...
By Singlespeed , 2 days ago