Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Daikin problem
Posted by: @togfather@toodles Thank you for this. I will give it a try 🙂
Although this is generally good advice, as @iancalderbank pointed out, you need to get the very low flow rate fixed first in order to get heat into your house.
@togfather the flow rate is crucial. If that stays at 10.7, you will never move enough heat, there is basic physics in the way, the rate of movement of the water is directly related to the rate of the heat movement, it needs to be 20-25l/m at least.
I don't know enough about daikin to know if there could be some setting causing it to be low. If you are able to turn off the backup heater, please see if that makes any difference to the flow rate, if not then something else may be required.
@toodles @chrislay can you help with where are the pump speed settings on a daikin?
regarding your installer and daikin
1. they are just plain wrong about weather comp costing money. the point of weather comp is that it reduces the heat pumps power in proportion to how warm it is outside (or increases it in proportion to how cold, if you like). The times when its mild spent running at lower power , saves you money. (Bit more to it than that, but thats the "in a nutshell")
2. The low flow rate is a clear and obvious demonstrable fault with the system. There is no way they can "debate" whether its large enough. Its not, the system will never move enough heat to warm your house with this low flow rate. You can legitimately keep on calling them back, asking for your money back, until they get this value to where it should be.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank I have just looked in the Daikin Installer’s Manual and I am attaching a screen grab of the relevant part of a page about pump volume. I am confused to say the least! With my sight and having to magnify the image on my iPad, navigating the pages is very awkward. I will try to find HOW to adjust the flow rate but meanwhile, at the bottom of the image is the manual details so that Tog can look it up if not in possession of a printed copy.
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Just found this link for the manual in case it helps you.
Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
I’ve done my best as my sight allows for now, may I suggest Togfather that you look at section 8 on configuration where you will find mention of the back up heater. My system doesn’t have such a heater and therefore, I don’t wish to rootle through the configuration which may not be the same anyway! I’m glad my installers set up my pump correctly, it sounds like your is a real nightmare job and the installer should be putting it right for you - compensation?
Regards, Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
@iancalderbank I don't know if you can set the actual pump speed. As far as I know the controller sets the speed to maintain the delta t. 10.7 is the minimum and the max is about 40. It will then switch the compressor on/off as well. I think the default dt is 7 or 8.
One other thought - did the installer upgrade any pipework? - oil may have been piped with 22mm - that will be too small.
-
Daikin 6kw setup with Dixell controller
7 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
11 months ago
-
Heating Turned Off but Radiators Still Warm
11 months ago
-
How can we prevent our LG heat pump from freezing up in cold weather?
2 years ago
-
Daikin Error Code 7H05
2 years ago
Currently viewing this topic 3 guests.
- 27 Forums
- 2,767 Topics
- 65.1 K Posts
- 1,607 Online
- 7,169 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Next steps on my ASHP journey: Radiators and Pipework
If you are considering phasing the project, then I woul...
By GrahamF , 2 hours ago
-
RE: Siting of the external sensor on a heatpump
Of course had the heat source been a heat pump it would...
By JamesPa , 4 hours ago
-
Never assume, it makes an ass of u and me! OK, tha...
By JamesPa , 4 hours ago
-
RE: Recommendations in Ely (Cambs) area for Full setup checks on Nibe HP setup for House.
In fairness all heating has cost a lot to run in recent...
By JamesPa , 6 hours ago
-
RE: Is it the house or the equipment?
@springswood We have two Daikin single split A2A syst...
By Rob of York , 7 hours ago
-
RE: Navigating the World of Refrigerants In Heat Pumps: A Guide for Homeowners
Indeed we are invvestigating AC at present and are havi...
By Toodles , 1 day ago
-
No, but the heat pump must be capable of delivering a S...
By JamesPa , 2 days ago
-
RE: Daikin ESPAltherma and Home Assistant installation
It's laziness lol The PV system is very chatty, meter...
By bobflux , 2 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
R (The R Project for Statistical Computing, I use it wi...
By cathodeRay , 2 days ago
-
RE: Vaillant Arotherm Plus 7KW need a service on it
booked it with Vaillant. will use them until i can find...
By AdamK , 2 days ago
-
RE: Adventures in heat loss calculations
I have seen it stated that the declared calorific value...
By JamesPa , 3 days ago
-
RE: Two heating zones to one zone
@transparent Many thanks. The garage is fairly well ...
By Profzarkov , 3 days ago
-
RE: Vaillant Aurotherm - Heater Wire Position
Ah, good point. I need to check if this was installed i...
By Batpred , 4 days ago
-
@batpred thanks for getting a copy. Appreciate the supp...
By Mars , 4 days ago