Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Daikin Altherma Heating Controls using Onecta Integration via Home Assistant
Ok so likely not setting the world on fire here for revolutionary controls but it may help some, especially here in the UK, where Octopus are installing a lot of these Dainkin units.
so they have 2 modes, LWT which runs and balances temps of a heat curve and ignores internal temps. It’s very efficient but doesn’t balance internal comfort without a lot of tinkering.
Then Madoka mode that uses the internal thermostat and constantly messes about with the heat pump, is not great at efficiency but does do comfort well.
So, behold. LWT with some internal reference for the best of both.
\
alias: Heat Pump - Adjust Heat Curve Offset based on Room Temp
triggers:
- minutes: /30
trigger: time_pattern
conditions: - condition: numeric_state
entity_id: sensor.altherma_heat_pump_climatecontrol_room_temperature
above: 0
actions: - variables:
room_temp: >
{{ states(‘sensor.altherma_heat_pump_climatecontrol_room_temperature’) |
float(21) }}
current_counter: |
{{ states(‘input_number.heat_curve_offset_counter’) | float(0) }} - choose:
- conditions:
- condition: numeric_state
entity_id: sensor.altherma_heat_pump_climatecontrol_room_temperature
above: 21.5 - condition: numeric_state
entity_id: sensor.altherma_heat_pump_climatecontrol_leaving_water_temperature
above: 30
sequence: - variables:
new_value: |
{% set next = current_counter - 1 %} {% if next < -5 %}
-5
{% else %}
{{ next | int }}
{% endif %} - target:
entity_id: input_number.heat_curve_offset_counter
data:
value: “{{ new_value }}”
action: input_number.set_value
- condition: numeric_state
- conditions:
- condition: numeric_state
entity_id: sensor.altherma_heat_pump_climatecontrol_room_temperature
below: 20.5
sequence: - variables:
new_value: |
{% set next = current_counter + 1 %} {% if next > 5 %}
5
{% else %}
{{ next | int }}
{% endif %} - target:
entity_id: input_number.heat_curve_offset_counter
data:
value: “{{ new_value }}”
action: input_number.set_value
- condition: numeric_state
- conditions:
- condition: numeric_state
entity_id: sensor.altherma_heat_pump_climatecontrol_room_temperature
above: 20.5 - condition: numeric_state
entity_id: sensor.altherma_heat_pump_climatecontrol_room_temperature
below: 21.5
sequence: - target:
entity_id: input_number.heat_curve_offset_counter
data:
value: 0
action: input_number.set_value
- condition: numeric_state
- conditions:
- target:
entity_id: climate.heating_leaving_water_offset
data:
temperature: “{{ states(‘input_number.heat_curve_offset_counter’) | int }}”
action: climate.set_temperature
mode: single
\\
This automation will reference the internal thermostat every 30 minutes and then tweak the flow temperature by 1 up or down to help keep the room temp within the ideal mark of 20.5 and 21.5 degrees C.
Its max adjustment is +/- 5 to the flow temperature.
It also needs a helper to track that adjustment value which you can drop into your configuration.yaml
\
input_number:
heat_curve_offset_counter:
name: Heat Curve Offset Counter
min: -5
max: 5
step: 1
mode: box
initial: 0
\\
This has been keeping my house warm now for a good few weeks and stopping the house over heating whilst keeping the heat pump running slow and steady. Give it a look if you’re interested.
- 26 Forums
- 2,677 Topics
- 62.6 K Posts
- 215 Online
- 7,090 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Floor standing brackets for K3 rads
My neighbour is a plumber and said I would need to fit ...
By Singlespeed , 32 minutes ago
-
After an intense recode, I’m pleased to announce that w...
By Mars , 41 minutes ago
-
RE: Heat pump installation quotations
@batpred, @sttpd1917 I agree with what @batpred says...
By JamesPa , 41 minutes ago
-
RE: Harvest Thermal - ASHP with a smart thermal battery
As its using ToU tarrifs then its totally believable so...
By JamesPa , 2 hours ago
-
Why do you want to maintain a specific deltaT? The out...
By JamesPa , 2 hours ago
-
Hopefully this will answer your question. To...
By ASHP-BOBBA , 3 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I would be interested to find out if others do this and...
By ASHP-BOBBA , 3 hours ago
-
Don't you dare. You just carry on as you are; as @batpr...
By Majordennisbloodnok , 5 hours ago
-
RE: Heat pump design review please: 5 kW Vaillant aroTHERM Plus heat pump
@ragtime27 some rooms in our house only have one place ...
By Judith , 5 hours ago
-
RE: Several AC coupled batteries
That is a good point, a manufacturers can stop trading,...
By Batpred , 9 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Hi @hanno - good question. The range of hybrid invert...
By Transparent , 9 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
@transparent the inverter was installed in 2021 and afa...
By Tim441 , 10 hours ago
-
RE: Say hello and introduce yourself
I hope so, @toodles. It's not often that we see a situa...
By Majordennisbloodnok , 13 hours ago
-
RE: Electricity price predictions
Good point, I do expect the bonus of putting my energy ...
By Batpred , 1 day ago