Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Daikin Altherma Heating Controls using Onecta Integration via Home Assistant
Ok so likely not setting the world on fire here for revolutionary controls but it may help some, especially here in the UK, where Octopus are installing a lot of these Dainkin units.
so they have 2 modes, LWT which runs and balances temps of a heat curve and ignores internal temps. It’s very efficient but doesn’t balance internal comfort without a lot of tinkering.
Then Madoka mode that uses the internal thermostat and constantly messes about with the heat pump, is not great at efficiency but does do comfort well.
So, behold. LWT with some internal reference for the best of both.
\
alias: Heat Pump - Adjust Heat Curve Offset based on Room Temp
triggers:
- minutes: /30
trigger: time_pattern
conditions: - condition: numeric_state
entity_id: sensor.altherma_heat_pump_climatecontrol_room_temperature
above: 0
actions: - variables:
room_temp: >
{{ states(‘sensor.altherma_heat_pump_climatecontrol_room_temperature’) |
float(21) }}
current_counter: |
{{ states(‘input_number.heat_curve_offset_counter’) | float(0) }} - choose:
- conditions:
- condition: numeric_state
entity_id: sensor.altherma_heat_pump_climatecontrol_room_temperature
above: 21.5 - condition: numeric_state
entity_id: sensor.altherma_heat_pump_climatecontrol_leaving_water_temperature
above: 30
sequence: - variables:
new_value: |
{% set next = current_counter - 1 %} {% if next < -5 %}
-5
{% else %}
{{ next | int }}
{% endif %} - target:
entity_id: input_number.heat_curve_offset_counter
data:
value: “{{ new_value }}”
action: input_number.set_value
- condition: numeric_state
- conditions:
- condition: numeric_state
entity_id: sensor.altherma_heat_pump_climatecontrol_room_temperature
below: 20.5
sequence: - variables:
new_value: |
{% set next = current_counter + 1 %} {% if next > 5 %}
5
{% else %}
{{ next | int }}
{% endif %} - target:
entity_id: input_number.heat_curve_offset_counter
data:
value: “{{ new_value }}”
action: input_number.set_value
- condition: numeric_state
- conditions:
- condition: numeric_state
entity_id: sensor.altherma_heat_pump_climatecontrol_room_temperature
above: 20.5 - condition: numeric_state
entity_id: sensor.altherma_heat_pump_climatecontrol_room_temperature
below: 21.5
sequence: - target:
entity_id: input_number.heat_curve_offset_counter
data:
value: 0
action: input_number.set_value
- condition: numeric_state
- conditions:
- target:
entity_id: climate.heating_leaving_water_offset
data:
temperature: “{{ states(‘input_number.heat_curve_offset_counter’) | int }}”
action: climate.set_temperature
mode: single
\\
This automation will reference the internal thermostat every 30 minutes and then tweak the flow temperature by 1 up or down to help keep the room temp within the ideal mark of 20.5 and 21.5 degrees C.
Its max adjustment is +/- 5 to the flow temperature.
It also needs a helper to track that adjustment value which you can drop into your configuration.yaml
\
input_number:
heat_curve_offset_counter:
name: Heat Curve Offset Counter
min: -5
max: 5
step: 1
mode: box
initial: 0
\\
This has been keeping my house warm now for a good few weeks and stopping the house over heating whilst keeping the heat pump running slow and steady. Give it a look if you’re interested.
- 26 Forums
- 2,727 Topics
- 64 K Posts
- 2,142 Online
- 7,131 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
Trading Standards. You can buy all this stuff eas...
By dansus , 19 minutes ago
-
Cleaning solar panels with a hosepipe
The question is, is it legal for a householder to clean...
By JamesPa , 2 hours ago
-
if you have a midea the warranty will be with Midea i g...
By Graham Hendra , 4 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
..... Post deleted, but website won't let me!
By JamesPa , 4 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
I was told that installer doesn’t get to see the system...
By L8Again , 7 hours ago
-
@trebor12345 If you select the Change Rate Plan button,...
By Toodles , 11 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
@majordennisbloodnok Well, I can use such terms as HMRC...
By Toodles , 1 day ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
I'd picked up that there was a leak coming from around ...
By Sheriff Fatman , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
Great info. Thank you. Regards Pete
By peterackstraw , 2 days ago
-
-
RE: Microgeneration Certification Scheme (MCS)
@jamespa A cynical view but, I fear that it is a fair ...
By Toodles , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 5 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 5 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 5 days ago