Controlling Daikin Altherma via P1P2 and Home Assistant
Are there any fellow Daikin Altherma 3M owners who are using Home Assistant to control their heatpump?
I’ve installed a P1P2MQTT unit connected to HA to give me more control over our Daikin heat pump and to move away from the truly inflexible Daikin Onecta setup.
I’ve tried to set up the Daikin indoor unit so that it doesn’t interfere with HA control but I’m still finding some curious and frustrating results.
For instance, I wanted to set the hot water tank to only heat overnight during our Octopus Go cheap rate tariff, but I’m finding the Daikin hot water seems stubbornly stuck at 50c despite there being no schedule set on the indoor unit, and Eco DHW set to 30c and comfort DHW set to 35c.
if anyone else has tried to use HA to control their Daikin, I’d appreciate any tips for any aspect of the setup.
Our setup is
* Daikin Low Temperature Monobloc 4kW Heat Pump (EDLA04E2V3)
* Daikin Indoor Unit
* Daikin WLAN Adaptor (BRP069A78)
* Daikin 150L Hot Water Tank
* Solar iBoost+
76m² Semi-detached House in North East England
Nissan Leaf 110 kW N-Connecta, 2017 Hyundai IONIQ Premium SE PHEV
Podpoint EV charger
Daikin Altherma 3M ASHP (EDLA04E2V3)
Daikin WLAN Adaptor (BRP069A78)
Daikin 150L Hot Water Tank
Solar iBoost
P1P2 and Home Assistant
SolaX X1 Hybrid Series inverter
2 × SolaX Triple Power 5.8 kWh Batteries
1 × EcoFlow Stream Ultra X 3.8 kWh, 1 × EcoFlow Stream Ultra 1.92 kWh, 2 × EcoFlow Stream AC 1.92 kWh batteries
12 × 365 W solar panels (roof), 1 × 380 W, 1 × 400 W, 1 × 200 W, 2 × 100 W solar panels (garden)
I haven’t got a Daikin but I have been having some fun with MQTT on another thread. If anyone else can cover off the normal Daikin control stuff I’m happy to help fill in the MQTT and HA bits.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@majordennisbloodnok Thank you!
My biggest head scratcher right now is I have the below automation (and similar) setup for overnight hot water, but the Daikin unit completely ignores it and heats DHW to 50c whenever it wants.
---
alias: Daikin DHW - Start Off Peak Heating (50C)
mode: single
triggers:
- at: "00:30:00"
trigger: time
conditions:
- condition: time
weekday:
- mon
- tue
- wed
- thu
- fri
- sat
actions:
- target:
entity_id: climate.bridge0_dhw_dhw_setpoint
data:
hvac_mode: heat
action: climate.set_hvac_mode
- delay: "00:00:02"
- target:
entity_id: climate.bridge0_dhw_dhw_setpoint
data:
temperature: 52
action: climate.set_temperature
- data:
name: Daikin DHW
message: "Off-peak start: DHW ON, target 52°C"
entity_id: climate.bridge0_dhw_dhw_setpoint
action: logbook.log
76m² Semi-detached House in North East England
Nissan Leaf 110 kW N-Connecta, 2017 Hyundai IONIQ Premium SE PHEV
Podpoint EV charger
Daikin Altherma 3M ASHP (EDLA04E2V3)
Daikin WLAN Adaptor (BRP069A78)
Daikin 150L Hot Water Tank
Solar iBoost
P1P2 and Home Assistant
SolaX X1 Hybrid Series inverter
2 × SolaX Triple Power 5.8 kWh Batteries
1 × EcoFlow Stream Ultra X 3.8 kWh, 1 × EcoFlow Stream Ultra 1.92 kWh, 2 × EcoFlow Stream AC 1.92 kWh batteries
12 × 365 W solar panels (roof), 1 × 380 W, 1 × 400 W, 1 × 200 W, 2 × 100 W solar panels (garden)
So to clarify (and rephrase the problem into my own terms - bear of very little brain, here...), you're saying you can't find anywhere in the onboard controls of your heat pump where there's a schedule to heat your DHW and yet it's always staying at 50degC or reheating immediately it drops below that level. Is that correct? Or is it that your automation is trying to get the DHW to 52degC but the heat pump stops at a ceiling of 50degC?
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@majordennisbloodnok That’s correct. I can’t find anywhere in the heat pump controls that should be preventing Home Assistant from scheduling a 52c heat of the DHW.
Interestingly, in the installer settings on the Indoor Unit, there is a screen that shows 50c as you go into the setup. But it is greyed out and can’t be changed. That leads me to believe there may be a hidden Daikin setting I’m not aware of!
76m² Semi-detached House in North East England
Nissan Leaf 110 kW N-Connecta, 2017 Hyundai IONIQ Premium SE PHEV
Podpoint EV charger
Daikin Altherma 3M ASHP (EDLA04E2V3)
Daikin WLAN Adaptor (BRP069A78)
Daikin 150L Hot Water Tank
Solar iBoost
P1P2 and Home Assistant
SolaX X1 Hybrid Series inverter
2 × SolaX Triple Power 5.8 kWh Batteries
1 × EcoFlow Stream Ultra X 3.8 kWh, 1 × EcoFlow Stream Ultra 1.92 kWh, 2 × EcoFlow Stream AC 1.92 kWh batteries
12 × 365 W solar panels (roof), 1 × 380 W, 1 × 400 W, 1 × 200 W, 2 × 100 W solar panels (garden)
@weoleyric, apologies for the delay in response.
Given your last post, I'm still not clear whether you're having trouble finding where the DHW max temperature can be changed or whether you're having trouble finding how to change ANY of the DHW settings/schedule - in both cases, within the Daikin in-house controller. As a result, I'm trying to get hold of a forum member who's familiar with their way around the settings of your in-house controller so we can burrow into the settings and see what's going on.
Once we're clearer about what your heat pump is actually configured to do within its own settings, that's when I'd like to look at Home Assistant and see if you can do what you want by manually changing settings in HA. That'll prove that the MQTT communication is working properly. Once we've done that, that's when we can look at the automation and see if anything needs to be changed. First step, though, is to ignore anything outside the Daikin settings so we can simplify the problem.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@weoleyric Oh Dear, I don’t think I am going to be of much help here as my DHW is handled totally separately using a Sunamp Thermino ePC 210 unit.
Nevertheless, my heat pump is the 8 kW version of the Daikin EDLA08 monobloc with the MMI controller. Main control has been placed in the hands of the Homely Smart Controller though. @majordennisbloodnok wondered if I may be able to help - but I doubt I’ll be of any use to you here. Have you accessed the MMI settings that the installer uses? By setting up at installer level by using the code 5678 rather than the usual user level, you will have access to far more parameters. As I say, I don’t use the DHW settings on the MMI but you should be able to shuffle through the options for water heating and find the adjustments there. This may mean going down four or five level of submenu so take a packed lunch with you! Do you have the installer’s manual as this will show the route to you - though as manuals go, it is not the best example of clarity I’m afraid! Regards and Good Luck, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
On the contrary, @toodles, that’s a lot of help. I’d never have known about the code for the installer’s menu. Thanks.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 187 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
@simonf I’ll ask the installers to get them out. What k...
By AdamK , 5 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
Thanks for all the help/comments. I completely agree w...
By JamesPa , 8 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
I doubt that matters, ToU tariffs are for the benefit o...
By JamesPa , 13 hours ago
-
RE: Free Ecoheat Heat Pump Install
@deltona Yes older houses are problematic like that, bu...
By bontwoody , 16 hours ago
-
RE: Radiator sizing sanity check
As I mentioned early on the cost of supplying and fitti...
By JamesPa , 18 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
I hadn't spotted that there were two pumps in the UFH (...
By JamesPa , 20 hours ago
-
RE: Setback savings - fact or fiction?
Never assume it makes an ass of u and me! You need the...
By JamesPa , 20 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Before I answer your specific questions just one more t...
By JamesPa , 20 hours ago
-
RE: Electricity price predictions
Great point, one of the key ones in my chat with Octopu...
By Batpred , 1 day ago
-
RE: Running from backup generaor in powercut?
Definitely and professionals sometimes miss it. I had...
By Batpred , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 1 day ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 1 day ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 2 days ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 2 days ago
-
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 2 days ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 2 days ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
@ecobaker Thanks for this. I've had it in both slots. ...
By andbeck , 2 days ago