Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Controlling Daikin Altherma via P1P2 and Home Assistant
Are there any fellow Daikin Altherma 3M owners who are using Home Assistant to control their heatpump?
I’ve installed a P1P2MQTT unit connected to HA to give me more control over our Daikin heat pump and to move away from the truly inflexible Daikin Onecta setup.
I’ve tried to set up the Daikin indoor unit so that it doesn’t interfere with HA control but I’m still finding some curious and frustrating results.
For instance, I wanted to set the hot water tank to only heat overnight during our Octopus Go cheap rate tariff, but I’m finding the Daikin hot water seems stubbornly stuck at 50c despite there being no schedule set on the indoor unit, and Eco DHW set to 30c and comfort DHW set to 35c.
if anyone else has tried to use HA to control their Daikin, I’d appreciate any tips for any aspect of the setup.
Our setup is
* Daikin Low Temperature Monobloc 4kW Heat Pump (EDLA04E2V3)
* Daikin Indoor Unit
* Daikin WLAN Adaptor (BRP069A78)
* Daikin 150L Hot Water Tank
* Solar iBoost+
76m² Semi-detached House in North East England
Nissan Leaf 110 kW N-Connecta, 2017 Hyundai IONIQ Premium SE PHEV
Podpoint EV charger
Daikin Altherma 3M ASHP (EDLA04E2V3)
Daikin WLAN Adaptor (BRP069A78)
Daikin 150L Hot Water Tank
Solar iBoost
P1P2 and Home Assistant
SolaX X1 Hybrid Series inverter
2 × SolaX Triple Power 5.8 kWh Batteries
1 × EcoFlow Stream Ultra X 3.8 kWh, 1 × EcoFlow Stream Ultra 1.92 kWh, 2 × EcoFlow Stream AC 1.92 kWh batteries
12 × 365 W solar panels (roof), 1 × 380 W, 1 × 400 W, 1 × 200 W, 2 × 100 W solar panels (garden)
I haven’t got a Daikin but I have been having some fun with MQTT on another thread. If anyone else can cover off the normal Daikin control stuff I’m happy to help fill in the MQTT and HA bits.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@majordennisbloodnok Thank you!
My biggest head scratcher right now is I have the below automation (and similar) setup for overnight hot water, but the Daikin unit completely ignores it and heats DHW to 50c whenever it wants.
---
alias: Daikin DHW - Start Off Peak Heating (50C)
mode: single
triggers:
- at: "00:30:00"
trigger: time
conditions:
- condition: time
weekday:
- mon
- tue
- wed
- thu
- fri
- sat
actions:
- target:
entity_id: climate.bridge0_dhw_dhw_setpoint
data:
hvac_mode: heat
action: climate.set_hvac_mode
- delay: "00:00:02"
- target:
entity_id: climate.bridge0_dhw_dhw_setpoint
data:
temperature: 52
action: climate.set_temperature
- data:
name: Daikin DHW
message: "Off-peak start: DHW ON, target 52°C"
entity_id: climate.bridge0_dhw_dhw_setpoint
action: logbook.log
76m² Semi-detached House in North East England
Nissan Leaf 110 kW N-Connecta, 2017 Hyundai IONIQ Premium SE PHEV
Podpoint EV charger
Daikin Altherma 3M ASHP (EDLA04E2V3)
Daikin WLAN Adaptor (BRP069A78)
Daikin 150L Hot Water Tank
Solar iBoost
P1P2 and Home Assistant
SolaX X1 Hybrid Series inverter
2 × SolaX Triple Power 5.8 kWh Batteries
1 × EcoFlow Stream Ultra X 3.8 kWh, 1 × EcoFlow Stream Ultra 1.92 kWh, 2 × EcoFlow Stream AC 1.92 kWh batteries
12 × 365 W solar panels (roof), 1 × 380 W, 1 × 400 W, 1 × 200 W, 2 × 100 W solar panels (garden)
So to clarify (and rephrase the problem into my own terms - bear of very little brain, here...), you're saying you can't find anywhere in the onboard controls of your heat pump where there's a schedule to heat your DHW and yet it's always staying at 50degC or reheating immediately it drops below that level. Is that correct? Or is it that your automation is trying to get the DHW to 52degC but the heat pump stops at a ceiling of 50degC?
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@majordennisbloodnok That’s correct. I can’t find anywhere in the heat pump controls that should be preventing Home Assistant from scheduling a 52c heat of the DHW.
Interestingly, in the installer settings on the Indoor Unit, there is a screen that shows 50c as you go into the setup. But it is greyed out and can’t be changed. That leads me to believe there may be a hidden Daikin setting I’m not aware of!
76m² Semi-detached House in North East England
Nissan Leaf 110 kW N-Connecta, 2017 Hyundai IONIQ Premium SE PHEV
Podpoint EV charger
Daikin Altherma 3M ASHP (EDLA04E2V3)
Daikin WLAN Adaptor (BRP069A78)
Daikin 150L Hot Water Tank
Solar iBoost
P1P2 and Home Assistant
SolaX X1 Hybrid Series inverter
2 × SolaX Triple Power 5.8 kWh Batteries
1 × EcoFlow Stream Ultra X 3.8 kWh, 1 × EcoFlow Stream Ultra 1.92 kWh, 2 × EcoFlow Stream AC 1.92 kWh batteries
12 × 365 W solar panels (roof), 1 × 380 W, 1 × 400 W, 1 × 200 W, 2 × 100 W solar panels (garden)
@weoleyric, apologies for the delay in response.
Given your last post, I'm still not clear whether you're having trouble finding where the DHW max temperature can be changed or whether you're having trouble finding how to change ANY of the DHW settings/schedule - in both cases, within the Daikin in-house controller. As a result, I'm trying to get hold of a forum member who's familiar with their way around the settings of your in-house controller so we can burrow into the settings and see what's going on.
Once we're clearer about what your heat pump is actually configured to do within its own settings, that's when I'd like to look at Home Assistant and see if you can do what you want by manually changing settings in HA. That'll prove that the MQTT communication is working properly. Once we've done that, that's when we can look at the automation and see if anything needs to be changed. First step, though, is to ignore anything outside the Daikin settings so we can simplify the problem.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@weoleyric Oh Dear, I don’t think I am going to be of much help here as my DHW is handled totally separately using a Sunamp Thermino ePC 210 unit.
Nevertheless, my heat pump is the 8 kW version of the Daikin EDLA08 monobloc with the MMI controller. Main control has been placed in the hands of the Homely Smart Controller though. @majordennisbloodnok wondered if I may be able to help - but I doubt I’ll be of any use to you here. Have you accessed the MMI settings that the installer uses? By setting up at installer level by using the code 5678 rather than the usual user level, you will have access to far more parameters. As I say, I don’t use the DHW settings on the MMI but you should be able to shuffle through the options for water heating and find the adjustments there. This may mean going down four or five level of submenu so take a packed lunch with you! Do you have the installer’s manual as this will show the route to you - though as manuals go, it is not the best example of clarity I’m afraid! Regards and Good Luck, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
On the contrary, @toodles, that’s a lot of help. I’d never have known about the code for the installer’s menu. Thanks.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
- 27 Forums
- 2,539 Topics
- 59.1 K Posts
- 561 Online
- 6,818 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Balancing is a long process and its possible to mess th...
By JamesPa , 1 hour ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 2 hours ago
-
Thanks everyone for the help, Havenwise now diasbled. q...
By Boycey , 4 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli Depending on whether you can get an EV tariff, I...
By ChandyKris , 5 hours ago
-
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 7 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 7 hours ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 8 hours ago
-
@Mars at the time of writing heating oil is £1.28 / ltr...
By TechnoGeek , 8 hours ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 11 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 11 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
The setup for this is a Samsung Modbus card. Connected ...
By antonical , 12 hours ago
-
RE: Forum updates, announcements & issues
@davidalgarve, if the emails are more than roughly a mo...
By Mars , 13 hours ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 13 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 14 hours ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
The answer was in two parts in my reply, the second par...
By RobS , 1 day ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 1 day ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
Loss assessments can be a very serious case of GIGO. I...
By JamesPa , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Just bizarre. This is our data. I really don't...
By antonical , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW review
I think you said its an 11.2kW model and your house is ...
By JamesPa , 2 days ago