Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@clairelp finally I can see that you have a volumiser, not buffer setup. So there should be not extra pumps on the system. The pump built into the Daikin is quite strong, I can't see a bypass (but it's hard to tell with the quality of pictures)
This is what they look like, it maybe in the airing cupboard, do you TRVs on every radiator.
Does the noise stop when doing hot water.???
@clairelp I'd expect the primary pipes - which is the ones that connect your heat pump to to the volumiser, to that black and red Esbe valve, and to any manifolds or branching off in your cupboard, to be at least 28mm diameter. From the pictures it looks like they >may< be 22mm? It's hard to tell though.
Apologies - I've forgotten the output of your heat pump..... There's a limit to how many kWhs you can get down each diameter pipe to not go over 0.9 - 1m/s velocity. For 22mm the limit is around 6kW. For 28mm it's more like 10kWh. * Could you please check what the diameter of the pipes going to your volumiser are please? The volumiser is the small gray tank thing in the attic.
Did you then say that each pipe heading off around the house is 10mm? You can get around 1kW down each one of these to not go over 0.9 - 1m/s velocity.
The reason you would want to keep to that velocity limit is it tends to get noisy above it. Also much above 1.5 and it starts to erode the internal of a copper pipe.
As Ken and others thought previously the pipe clips attach the pipe directly to the wood in your attic. An alternative would be to use a clip that goes to the outside of the insulation material. There is a brand called "Primary Pro" that is a favourite with heat pump installers. As you have a cold attic I'd advise consider this a cold space and upgrading the insulation up there - you'll save money in the long run.
Ken's suggestion to check the air vent is a good one too.
*These numbers assume you have glycol in your system, and that the dT of your heat pump is 5. dT means the delta T - it stands for the temperature difference between the hot pipe from the heat pump and the cold one. Delta means "difference" in Latin. As dT increases you can get more and more heat down a pipe within that velocity limit.
Planning your dream house? Book a simple one-to-one consultation to get you on a good path - here.
Hi, we not had chance to get in the loft to look at the valve yet, difficult to go up in loft making noise when children asleep in the evening.
I did look at pressure gauge in cupboard and it about 1.6.
Friday installers are coming so I will keep you posted. We also have installers msc compliance department checking the install following week. Hoping they will have an answer 🤞🙏
the ashp does have anti freeze valves, with it not been below freezing hoping be okay to keep turning off for a couple of nights.
also looking into sound proofing and insulation for the loft.
Hi,
Installers, have turned down the velocity to I think he said 21-22 and was previously 24. Think he said in the bypass valve. And I sorry can’t remember exactly but I think he said like it around 21 and maybe 24 was making too much noise.
At moment, I don’t think I could hear it and running quieter, it’s only just done so I will test it later when doing hot water and have to wait for a cold night.
🤞
They also did some settings on the frost cycle. They said it shouldn’t be coming on when not cold enough and shouldn’t be constantly going. Said there is two defrost settings one I think he said for the pipes and one for actual pump. They said if changes didn’t help they will contact Daikain, as some setting they can’t change.
- 26 Forums
- 2,670 Topics
- 62.5 K Posts
- 144 Online
- 7,080 Members
Join Us!
Directory
Degrees of Separation
Latest Posts
-
RE: Load Shift and Lifestyle Shift Complete - our journey has ended, for now
@allyfish Great to read how you managed it. My main ...
By Batpred , 15 minutes ago
-
-
RE: MCS 2.0 - Changes in January 2025
It strike's me that there's various improvements which ...
By Temperature_Gradient , 2 hours ago
-
RE: Daikin ESPAltherma and Home Assistant installation
@majordennisbloodnok The M5StickC turned up...
By Bash , 3 hours ago
-
Hi Everyone, I wanted to share something with you all...
By ASHP-BOBBA , 3 hours ago
-
-
Many messages back and forth later… GOV UK One Login ...
By Toodles , 6 hours ago
-
RE: Say hello and introduce yourself
@will-h, this isn't a dig but we would prefer if anyone...
By Majordennisbloodnok , 8 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
Thanks Tim. That SolarEdge data also shows voltages a...
By Transparent , 11 hours ago
-
RE: Configuring third party dongle for Ecodan local control
A few notable developments: I'm working through addin...
By F1p , 1 day ago
-
RE: Vehicle-to-Home with a Heat Pump: Is the Technology Ready and Which EV Should I Buy?
Vehicle to Grid is the further step and here is the IEA...
By Judith , 1 day ago
-
RE: Renewables & Heat Pumps in the News
Where the grid is heading? Input from Kraken.
By Jeff , 1 day ago
-
RE: Plug and play solar. Thoughts?
@jamespa Yes, unfortunately our policymakers learned...
By Batpred , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
@l8again It seems you did very well. With our HG h...
By Batpred , 2 days ago