Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@clairelp finally I can see that you have a volumiser, not buffer setup. So there should be not extra pumps on the system. The pump built into the Daikin is quite strong, I can't see a bypass (but it's hard to tell with the quality of pictures)
This is what they look like, it maybe in the airing cupboard, do you TRVs on every radiator.
Does the noise stop when doing hot water.???
@clairelp I'd expect the primary pipes - which is the ones that connect your heat pump to to the volumiser, to that black and red Esbe valve, and to any manifolds or branching off in your cupboard, to be at least 28mm diameter. From the pictures it looks like they >may< be 22mm? It's hard to tell though.
Apologies - I've forgotten the output of your heat pump..... There's a limit to how many kWhs you can get down each diameter pipe to not go over 0.9 - 1m/s velocity. For 22mm the limit is around 6kW. For 28mm it's more like 10kWh. * Could you please check what the diameter of the pipes going to your volumiser are please? The volumiser is the small gray tank thing in the attic.
Did you then say that each pipe heading off around the house is 10mm? You can get around 1kW down each one of these to not go over 0.9 - 1m/s velocity.
The reason you would want to keep to that velocity limit is it tends to get noisy above it. Also much above 1.5 and it starts to erode the internal of a copper pipe.
As Ken and others thought previously the pipe clips attach the pipe directly to the wood in your attic. An alternative would be to use a clip that goes to the outside of the insulation material. There is a brand called "Primary Pro" that is a favourite with heat pump installers. As you have a cold attic I'd advise consider this a cold space and upgrading the insulation up there - you'll save money in the long run.
Ken's suggestion to check the air vent is a good one too.
*These numbers assume you have glycol in your system, and that the dT of your heat pump is 5. dT means the delta T - it stands for the temperature difference between the hot pipe from the heat pump and the cold one. Delta means "difference" in Latin. As dT increases you can get more and more heat down a pipe within that velocity limit.
Planning your dream house? Book a simple one-to-one consultation to get you on a good path - here.
Hi, we not had chance to get in the loft to look at the valve yet, difficult to go up in loft making noise when children asleep in the evening.
I did look at pressure gauge in cupboard and it about 1.6.
Friday installers are coming so I will keep you posted. We also have installers msc compliance department checking the install following week. Hoping they will have an answer 🤞🙏
the ashp does have anti freeze valves, with it not been below freezing hoping be okay to keep turning off for a couple of nights.
also looking into sound proofing and insulation for the loft.
Hi,
Installers, have turned down the velocity to I think he said 21-22 and was previously 24. Think he said in the bypass valve. And I sorry can’t remember exactly but I think he said like it around 21 and maybe 24 was making too much noise.
At moment, I don’t think I could hear it and running quieter, it’s only just done so I will test it later when doing hot water and have to wait for a cold night.
🤞
They also did some settings on the frost cycle. They said it shouldn’t be coming on when not cold enough and shouldn’t be constantly going. Said there is two defrost settings one I think he said for the pipes and one for actual pump. They said if changes didn’t help they will contact Daikain, as some setting they can’t change.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 348 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 5 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 13 minutes ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 13 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 14 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 14 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 17 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 23 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 23 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago