Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
The thermostat is set at 21.5 degrees and the house is being held at 21 and has been for over 24 hours.
Good morning Batalto,
Very useful data.
As a check, try increasing your thermostat setpoint to say 23C and see if the indoor temperature increases. If it does then your system is not fully operating on weather compensation.
You could try make the slope of your weather compensation shallower, by changing the left hand end to 50C @ -10C.
Don't change the slope immediately, increase the thermostat setting and wait several hours or more to see the effect.
@kev-m actually I used LESS power. You can see from below the details of the days.
And of course as soon as I said it, I was wrong. My heating got the house to 21.5, so I've adjusted the weather curve down a tiny bit from 25@20, to 25@18. I'll wait to see the impact. Also yesterday I adjusted the hot water from 55 to 53 and that seems to be fine as well. Its not perfect as ambient is an average of the whole day - It could have been a cold night and a warm day and still average 13 vs 13 all day. However for my needs its close enough to be interesting.
@derek-m It doesnt matter what I set the thermostat to. Originally I had it on 22, but moved it to 21.5 to prevent a boiling house if the experiment went totally wrong. So far my nest app says the heating was being called for "23.5 hours" yesterday. It is showing 21 steady in the house downstairs. I've left upstairs on normal thermostat as its so warm up there anyway its not really ever on. When it does come on, it warms up pretty quickly.
Checked the filter today and it was pretty much totally clean - so I think the gunk is now cleaned out. The system is basically silent now as well, whereas before it made a high pitched noise in the main return pipe. I assume this was just a restricted flow issue.
House seems to be totally fine today, however the temps seem to creep up in the day. Now evening has come it's back to holding at 21. Not sure what to do as it seems to be a solar gain issue. However it wasn't a major issue as it was only 0.5° above target. A stated I've adjusted my curve a little bit. I'll be leaving it alone for the next few days and seeing the impact. However any tweaks will be around the edges.
Current setting 50°@-3° and 25°@18°
room temperature hit 21.5 again today, so trimmed the weather comp at the bottom end a little. Its not exactly sunny, so solar gain should be negligible today. Now the house is up to temperature it'll be interesting to see how it holds. slowly slowly dialling in. Just need a cold snap to see how we are really getting on
we're a tiny bit cooler indoors today on the same flow temps. I think it's because it's damps and misty. Not enough to worry about though. Like you say, this is too easy, we need some proper winter weather.
Ran through the night with a COP of 4.2 - Lost some heat downstairs though, the temperature dropped to 20. So I've adjusted my curve 1 degree upwards; 25 @ 17
Posted by: @bataltoRan through the night with a COP of 4.2 - Lost some heat downstairs though, the temperature dropped to 20. So I've adjusted my curve 1 degree upwards; 25 @ 17
Good morning Batalto,
The wind speed was higher last night in our area, and I have noticed that it appears to have added about 5C to the required water flow temperature.
@derek-m there is a bit of cycling on the system due to the super mild weather (ambient was 13 overnight). However its very wet today, so interesting to see how we get on. The house is well up to temperature now.
@kev-m It'll be a mix of hot water (for the showers), my wife's hair dryer, washing machine going on etc. This measures power in 5 min intervals, so its prone to being a bit spikey. You think 2/3kw for hot water being heated plus a 2kw hair drier and you're getting up there. Interestingly I am still running on battery, so my power is still 5p/kw
SOC = State of charge e.g. %
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 589 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
@david999 ... just water, David, or do you add anything...
By colinc , 39 minutes ago
-
RE: Our 10 year old Grant heat pump failed
Since my last post on this topic we've reached a conclu...
By Mike Patrick , 1 hour ago
-
Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
My installation is 4 years old. After about 18 months a...
By seoras , 3 hours ago
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 12 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 13 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 16 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 17 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 17 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 18 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 21 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 21 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago