Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
The thermostat is set at 21.5 degrees and the house is being held at 21 and has been for over 24 hours.
Good morning Batalto,
Very useful data.
As a check, try increasing your thermostat setpoint to say 23C and see if the indoor temperature increases. If it does then your system is not fully operating on weather compensation.
You could try make the slope of your weather compensation shallower, by changing the left hand end to 50C @ -10C.
Don't change the slope immediately, increase the thermostat setting and wait several hours or more to see the effect.
@kev-m actually I used LESS power. You can see from below the details of the days.
And of course as soon as I said it, I was wrong. My heating got the house to 21.5, so I've adjusted the weather curve down a tiny bit from 25@20, to 25@18. I'll wait to see the impact. Also yesterday I adjusted the hot water from 55 to 53 and that seems to be fine as well. Its not perfect as ambient is an average of the whole day - It could have been a cold night and a warm day and still average 13 vs 13 all day. However for my needs its close enough to be interesting.
@derek-m It doesnt matter what I set the thermostat to. Originally I had it on 22, but moved it to 21.5 to prevent a boiling house if the experiment went totally wrong. So far my nest app says the heating was being called for "23.5 hours" yesterday. It is showing 21 steady in the house downstairs. I've left upstairs on normal thermostat as its so warm up there anyway its not really ever on. When it does come on, it warms up pretty quickly.
Checked the filter today and it was pretty much totally clean - so I think the gunk is now cleaned out. The system is basically silent now as well, whereas before it made a high pitched noise in the main return pipe. I assume this was just a restricted flow issue.
House seems to be totally fine today, however the temps seem to creep up in the day. Now evening has come it's back to holding at 21. Not sure what to do as it seems to be a solar gain issue. However it wasn't a major issue as it was only 0.5° above target. A stated I've adjusted my curve a little bit. I'll be leaving it alone for the next few days and seeing the impact. However any tweaks will be around the edges.
Current setting 50°@-3° and 25°@18°
room temperature hit 21.5 again today, so trimmed the weather comp at the bottom end a little. Its not exactly sunny, so solar gain should be negligible today. Now the house is up to temperature it'll be interesting to see how it holds. slowly slowly dialling in. Just need a cold snap to see how we are really getting on
we're a tiny bit cooler indoors today on the same flow temps. I think it's because it's damps and misty. Not enough to worry about though. Like you say, this is too easy, we need some proper winter weather.
Ran through the night with a COP of 4.2 - Lost some heat downstairs though, the temperature dropped to 20. So I've adjusted my curve 1 degree upwards; 25 @ 17
Posted by: @bataltoRan through the night with a COP of 4.2 - Lost some heat downstairs though, the temperature dropped to 20. So I've adjusted my curve 1 degree upwards; 25 @ 17
Good morning Batalto,
The wind speed was higher last night in our area, and I have noticed that it appears to have added about 5C to the required water flow temperature.
@derek-m there is a bit of cycling on the system due to the super mild weather (ambient was 13 overnight). However its very wet today, so interesting to see how we get on. The house is well up to temperature now.
@kev-m It'll be a mix of hot water (for the showers), my wife's hair dryer, washing machine going on etc. This measures power in 5 min intervals, so its prone to being a bit spikey. You think 2/3kw for hot water being heated plus a 2kw hair drier and you're getting up there. Interestingly I am still running on battery, so my power is still 5p/kw
SOC = State of charge e.g. %
- 27 Forums
- 2,790 Topics
- 65.9 K Posts
- 4,298 Online
- 7,194 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Cooling/heating with one unit
Long term, it may be more cost effective to get an A2A ...
By Rob of York , 5 minutes ago
-
The video in the link mentions a direction arrow, which...
By Singlespeed , 12 hours ago
-
RE: Renewables & Heat Pumps in the News
Posted by: @editor I think we should make that approa...
By Rob of York , 21 hours ago
-
RE: Does anyone have experience of a smart water meter?
My neighbour received an email from Anglian Water sayin...
By AndrewJ , 22 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Well the military is well known for going green, isn't ...
By Majordennisbloodnok , 23 hours ago
-
RE: Why are ASHP installs so expensive?
I've ripped out over 11kw of storage and panel heaters ...
By Singlespeed , 23 hours ago
-
RE: Safety study for plug in batteries out to tender - looks like Q3 2027 at best before legal
I think it may depend how much of the world is on fire ...
By EtchedPixels , 1 day ago
-
RE: Air-to-Air Heat Pumps & Air Conditioning: UK Heating and Cooling Q&A
I hope it's not the same people who make the awful TV s...
By EtchedPixels , 1 day ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
I found some interesting data about the price of heat p...
By Rob of York , 2 days ago
-
RE: PV and battery long payback - sense check query
Thanks for all the comments. I finally got to the bott...
By DavidB , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
People following this thread who are hoping that plug i...
By JamesPa , 2 days ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
By Singlespeed , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
just had Vaillant over to service the HP and asked abou...
By AdamK , 3 days ago
-
RE: tepeo ZEB UK Support & Info Thread
OK so ZEB is basically a variant on a storage heater, b...
By JamesPa , 4 days ago