Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
ASHP choice help - 55C flow temperature required
apologies if others have covered...
is your total heat loss really 43kW? That's huge; the biggest domestic ASHP I've seen is 16kW.
55 degrees is high for any ASHP; most will do it but the COP isn't going to be a lot better than 2, even with the ones touted as HT. I think (don't know for sure) that while these units can do high temperatures, the COP is not necessarily better than 'normal' units. My ASHP (14kW Ecodan) will output 55 degrees all day at -2 but the COP will be around 2. One thing you rightly pointed out is to be careful with defrosts, which will lose you at least 10-15% of capacity below 2-3 degrees ambient. Also be careful with the rated outputs; they are often lower than the badged value at low ambients.
Remember an ASHP can only output at one LWT at a time. If the upstairs doesn't need 55 degrees LWT then you might be better with one for the downstairs and another for everything else. If your heat loss really is 43kW you're going to need multiple (or commercial grade) ASHPs anyway.
Finally, I don't know much about ufh but you do have to make sure it can emit enough heat at the flow rates an ASHP needs, which are normally higher than gas/oil systems.
Hi – I have a 16kW Daikin HT ASHP – system details below – which we’ve been running since August 2020. We have a combination of UFH and radiators. The system we have can only be used with a basic Daikin controller which gives no information on consumption or COP. I’ve managed by a process of elimination to work out consumption data and to date the heating consumption (not incl. DHW) is as below. Heating has been off since the start of April, and I’ve used this past winter’s figures for this next winter:
During 2021 and early 2022 we were using the system as if it was a gas boiler, doing everything wrong – room stats and zoning, running at high temperatures (there’s a blending valve on the UFH), no weather comp. It coped and was happy producing LWTs up to 70 or so for the radiators (!) but was obviously very thirsty in terms of consumption. This past winter with the help of the folks on this forum I’ve corrected these errors and obviously seen a big difference in consumption. I’m not actually running the HT capabilities of the system now but the house is quite comfortable; we possibly didn’t need a HT system but that’s what was recommended and we are just trying to run it as efficiently as possible.
I realise this doesn’t help much with the topic specifically but just wanted to add some insight into my Daikin HT journey particularly in respect of consumption. I’m more than happy to answer any queries about our experiences with the Daikin HT system.
System details:
- An outside unit - Daikin ERRQ016AAV1
- An inside unit - Daikin EKHBRD016ADV17
- A 500L thermal store - Daikin EKHWP500PB (no immersion heater installed)
- A very basic Daikin controller EKRUAHTB
- Manufacturer stated COP’s are 2.11 at -7, 3.01 at 2, 4.26 at 7, and 4.67 at 12C
- We have a 6.1kWp PV installation with 20 SW-facing panels and a SolarEdge SE6000H 6kw inverter, which produces around 8MWh pa, 3MWh of which goes back to the grid
Many thanks for the helpful responses.
@marzipan71 I'm still struggling to get figures out of Daikan. It's mystifying to me that suppliers aren't more transparant as to the key performance parameters of their products. Do you know what the LWT is for those COP figures?
@kev-m apologies - that heat loss figure was not quite right. The total heat loss in the rooms we use (!) is 18,000. But 5 of those are bedrooms, which are in practice scarcely heated, and even then only for a short time in the morning and evening.
For anyone interested, this is the result of my researches to date:
I am slightly surprised that there isn't a closer relationship between these COPs and the MCS SCOP figures, but of course they only cover a small part of the device characterisitics.
My current plan (it changes daily) is to go with a pair of Arotherm Plus 7kW pumps - one dedicated to the UFH and the other for rads around the house. I will post separately about my slightly eccentric DHW plans, because it would be great to get some input on those.
Stiebel Eltron WPLA07 7kW ASHP. 26 x 400W PV. 10kW Sunsynk 3-phase inverter. 6 x 4.8kWh Pylontech US5000C batteries.
@wintergreen here's what I have - apologies if it's too small to read. I was left two sheets by the installers - with completely different COP figures for the same pieces of kit! First file has the figures I quoted above. Agree about difficulty getting data - I have no way of monitoring COP via my controller as other users are able to do with their kit.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 288 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 2 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 16 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 16 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 19 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago