Posted by: @markc@derek-m Thanks for your comment Derek. Unfortunately I was replying to a post way back on page 6 but the forum software doesn't seem to collate threads. I didn't make it clear that my post was about DHW.
Hi Mark,
You could switch your pump on and off by means of a Pipe Clamp Thermostat, which could be installed at a suitable location on the pipework. When the temperature falls below the desired setting it would switch the pump on until the temperature exceeds the desired value. If you were to mount the thermostat on the return pipe, it would ensure that all the water in the pipework is up to temperature.
Posted by: @derek-mPosted by: @markc@derek-m Thanks for your comment Derek. Unfortunately I was replying to a post way back on page 6 but the forum software doesn't seem to collate threads. I didn't make it clear that my post was about DHW.
Hi Mark,
You could switch your pump on and off by means of a Pipe Clamp Thermostat, which could be installed at a suitable location on the pipework. When the temperature falls below the desired setting it would switch the pump on until the temperature exceeds the desired value. If you were to mount the thermostat on the return pipe, it would ensure that all the water in the pipework is up to temperature.
Now that could be a great solution for @george as well. Thanks.
@markc Thanks Mark,
I try to be helpful whenever possible.
As an afterthought to help conserve energy, you could retain the timer in the circuit, so that the water in the pipework is only kept hot during the time of day when it will be required.
Hi all,
We have an Ecodan 14Kw ASHP - House is 2 storey 286m2
We have underfloor heating downstairs and oversized radiators upstairs.
We have thermostats all over!
Issues
It’s using 18-22 thousand KWh annually and it’s costing us a fortune
The house doesn’t really feel warm
The heat pump is situated at the rear of the house but seems very noisy - not sure if this is normal - hadn’t really thought about the noise when it was installed - stupidly
Any suggestions welcome
@caroline2000 Hi Caroline,
Welcome to the forum.
ASHP's are noisiest when they are working hardest, which would also be when they are using most energy. Has your heat pump always been noisy or is it only recently that you have noticed an increase in noise level?
How long has your ASHP been installed and has it always used this amount of energy?
Do you have the heat loss calculations for your home?
Is there plenty of room around your ASHP for the cold air coming out to dissipate into the atmosphere? If the cold air coming out is drawn back into the heat pump, this will reduce the efficiency and increase the noise level.
If you can answer these questions it may lead to further questions to try to locate the root cause of your problem.
Posted by: @caroline2000Hi all,
We have an Ecodan 14Kw ASHP - House is 2 storey 286m2
We have underfloor heating downstairs and oversized radiators upstairs.
We have thermostats all over!
Issues
It’s using 18-22 thousand KWh annually and it’s costing us a fortune
The house doesn’t really feel warm
The heat pump is situated at the rear of the house but seems very noisy - not sure if this is normal - hadn’t really thought about the noise when it was installed - stupidly
Any suggestions welcome
Hi @caroline2000,
Excessive energy usage, house not warm and noisy I think that all sound wrong.
I too have an Ecodan 14Kw pump servicing around 240m2, UFH downstairs and rads up so not too dissimilar to yours. As Derek suggests, performance is linked to many factors but I'd be happy to share some details on setup/performance stats with you so you have a better idea on what you should be expecting.
Also, your location in the UK will have an impact with regards to outside temperatures.
There is an Ecodan review in the reviews section which is also a similar sized property to yours which gives details on their annual energy usage that should also give you a ballpark of what you should be expecting.
Thanks, it was fitted around May 2019.
i think there’s enough space around it (or so we were told)...it’s to the rest of the house on a side wall (in a corner) - there’s at least a foot behind it and 3foot to the left.....completely open with no instructions to the right and front.
Its the heating that is eating the energy.......when the heating isn’t on the bills are low
I think it’s always been noisy.......and energy consumption was the same during winter 2019 and 2020 (slightly better in 2020 as we tweaked the temperature and thermostats)
Are you heating your water tank 24/7 or have you set the ASHP to heat the tank at intervals during the day?
We found that was costing us a lot and has improved once I took the advice from the people in here, and set the tank to be heated at points during the day.
For what it’s worth, our UFH costs loads in comparison to any other of our electrical devices. We turned it on for the first time in 8/9 months or so this week, and watched the smart reader turn red.
Posted by: @caroline2000Hi all,
We have an Ecodan 14Kw ASHP - House is 2 storey 286m2
We have underfloor heating downstairs and oversized radiators upstairs.
We have thermostats all over!
Issues
It’s using 18-22 thousand KWh annually and it’s costing us a fortune
The house doesn’t really feel warm
The heat pump is situated at the rear of the house but seems very noisy - not sure if this is normal - hadn’t really thought about the noise when it was installed - stupidly
Any suggestions welcome
That's quite a big house. Ours is about half that size and we have the same ASHP. Having said that, if your ASHP is working properly with a COP of 2-3, that's a huge amount of energy to be using. What temperature are your thermostats set to? And your flow temps - are you using weather compensation?
Ours is quite noisy when it's working hard, e.g. to heat the house on a cold morning. But after that it's very quiet, sometimes barely audible standing a few metres away.
@caroline2000 Your high energy bills are mor than likly caused by your thermostats. The heat pump is running flat out all the time and not modulating, the equilivance is, driving a car at 70 miles per hour in third gear down the moterway, you cannot expect good performance.
Try turn all your thermostats up full and controwl the house temperature with the weather compensation on the heat pump only and treat your house as a whole. It will work well with your under floor.The heat pump will work 24-7 but at a very low speed, it will be very quiet and efficient using a lot less electricity.
However, if you have pumps and blending valves on your manifolds, you stand little chance of having reasonable heating bills, the system has been poorly designed and probably will not give you good performance.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Thanks for this - I think we’re probably doomed then!
Biggest regret of the house renovation - the pump and underfloor heating in general.....but it looks like we’re stuck with it so will try some of all the suggestions - once I get a chance to sit down and read the ‘War & Peace’ level instructions.....
-
Rodents! A word of warning for heat pump owners
7 days ago
-
Surface mount or bury primaries for heat pump installation?
2 months ago
-
UFH and ASHPs
4 months ago
-
Installing your own ASHP - DIY
5 months ago
-
ASHP install contract and BUS grant money
6 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 23 Online
- 5,736 Members
Podcast Picks
Latest Posts
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Is that heat loss, or maximum output of the ASHP? Unde...
By Scalextrix , 14 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan Fully agree with you. It shouldn't be the homeo...
By HCas , 15 hours ago
-
RE: Solar Thermal DHW and ASHP
@judith That makes sense to me! If I was in @alex_n '...
By HCas , 16 hours ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
Good unit. And the 10 kW is the same as the 12 kW I ...
By HCas , 16 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 19 hours ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 21 hours ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 1 day ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Just done your survey!
By Judith , 1 day ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@cleardene-ashp just thinking about your issues here. Y...
By Judith , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@cathoderay OK let's wait and see, it sounds an interes...
By Tasos , 2 days ago
-
RE: What is the Heat Geek Guarantee?
@judith, I’m with you on Heat Geek, but there really do...
By Mars , 2 days ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 3 days ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 4 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 4 days ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 4 days ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 4 days ago