Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @markc@derek-m Thanks for your comment Derek. Unfortunately I was replying to a post way back on page 6 but the forum software doesn't seem to collate threads. I didn't make it clear that my post was about DHW.
Hi Mark,
You could switch your pump on and off by means of a Pipe Clamp Thermostat, which could be installed at a suitable location on the pipework. When the temperature falls below the desired setting it would switch the pump on until the temperature exceeds the desired value. If you were to mount the thermostat on the return pipe, it would ensure that all the water in the pipework is up to temperature.
Posted by: @derek-mPosted by: @markc@derek-m Thanks for your comment Derek. Unfortunately I was replying to a post way back on page 6 but the forum software doesn't seem to collate threads. I didn't make it clear that my post was about DHW.
Hi Mark,
You could switch your pump on and off by means of a Pipe Clamp Thermostat, which could be installed at a suitable location on the pipework. When the temperature falls below the desired setting it would switch the pump on until the temperature exceeds the desired value. If you were to mount the thermostat on the return pipe, it would ensure that all the water in the pipework is up to temperature.
Now that could be a great solution for @george as well. Thanks.
@markc Thanks Mark,
I try to be helpful whenever possible.
As an afterthought to help conserve energy, you could retain the timer in the circuit, so that the water in the pipework is only kept hot during the time of day when it will be required.
Hi all,
We have an Ecodan 14Kw ASHP - House is 2 storey 286m2
We have underfloor heating downstairs and oversized radiators upstairs.
We have thermostats all over!
Issues
It’s using 18-22 thousand KWh annually and it’s costing us a fortune
The house doesn’t really feel warm
The heat pump is situated at the rear of the house but seems very noisy - not sure if this is normal - hadn’t really thought about the noise when it was installed - stupidly
Any suggestions welcome
@caroline2000 Hi Caroline,
Welcome to the forum.
ASHP's are noisiest when they are working hardest, which would also be when they are using most energy. Has your heat pump always been noisy or is it only recently that you have noticed an increase in noise level?
How long has your ASHP been installed and has it always used this amount of energy?
Do you have the heat loss calculations for your home?
Is there plenty of room around your ASHP for the cold air coming out to dissipate into the atmosphere? If the cold air coming out is drawn back into the heat pump, this will reduce the efficiency and increase the noise level.
If you can answer these questions it may lead to further questions to try to locate the root cause of your problem.
Posted by: @caroline2000Hi all,
We have an Ecodan 14Kw ASHP - House is 2 storey 286m2
We have underfloor heating downstairs and oversized radiators upstairs.
We have thermostats all over!
Issues
It’s using 18-22 thousand KWh annually and it’s costing us a fortune
The house doesn’t really feel warm
The heat pump is situated at the rear of the house but seems very noisy - not sure if this is normal - hadn’t really thought about the noise when it was installed - stupidly
Any suggestions welcome
Hi @caroline2000,
Excessive energy usage, house not warm and noisy I think that all sound wrong.
I too have an Ecodan 14Kw pump servicing around 240m2, UFH downstairs and rads up so not too dissimilar to yours. As Derek suggests, performance is linked to many factors but I'd be happy to share some details on setup/performance stats with you so you have a better idea on what you should be expecting.
Also, your location in the UK will have an impact with regards to outside temperatures.
There is an Ecodan review in the reviews section which is also a similar sized property to yours which gives details on their annual energy usage that should also give you a ballpark of what you should be expecting.
Thanks, it was fitted around May 2019.
i think there’s enough space around it (or so we were told)...it’s to the rest of the house on a side wall (in a corner) - there’s at least a foot behind it and 3foot to the left.....completely open with no instructions to the right and front.
Its the heating that is eating the energy.......when the heating isn’t on the bills are low
I think it’s always been noisy.......and energy consumption was the same during winter 2019 and 2020 (slightly better in 2020 as we tweaked the temperature and thermostats)
Are you heating your water tank 24/7 or have you set the ASHP to heat the tank at intervals during the day?
We found that was costing us a lot and has improved once I took the advice from the people in here, and set the tank to be heated at points during the day.
For what it’s worth, our UFH costs loads in comparison to any other of our electrical devices. We turned it on for the first time in 8/9 months or so this week, and watched the smart reader turn red.
Posted by: @caroline2000Hi all,
We have an Ecodan 14Kw ASHP - House is 2 storey 286m2
We have underfloor heating downstairs and oversized radiators upstairs.
We have thermostats all over!
Issues
It’s using 18-22 thousand KWh annually and it’s costing us a fortune
The house doesn’t really feel warm
The heat pump is situated at the rear of the house but seems very noisy - not sure if this is normal - hadn’t really thought about the noise when it was installed - stupidly
Any suggestions welcome
That's quite a big house. Ours is about half that size and we have the same ASHP. Having said that, if your ASHP is working properly with a COP of 2-3, that's a huge amount of energy to be using. What temperature are your thermostats set to? And your flow temps - are you using weather compensation?
Ours is quite noisy when it's working hard, e.g. to heat the house on a cold morning. But after that it's very quiet, sometimes barely audible standing a few metres away.
@caroline2000 Your high energy bills are mor than likly caused by your thermostats. The heat pump is running flat out all the time and not modulating, the equilivance is, driving a car at 70 miles per hour in third gear down the moterway, you cannot expect good performance.
Try turn all your thermostats up full and controwl the house temperature with the weather compensation on the heat pump only and treat your house as a whole. It will work well with your under floor.The heat pump will work 24-7 but at a very low speed, it will be very quiet and efficient using a lot less electricity.
However, if you have pumps and blending valves on your manifolds, you stand little chance of having reasonable heating bills, the system has been poorly designed and probably will not give you good performance.
Thanks for this - I think we’re probably doomed then!
Biggest regret of the house renovation - the pump and underfloor heating in general.....but it looks like we’re stuck with it so will try some of all the suggestions - once I get a chance to sit down and read the ‘War & Peace’ level instructions.....
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
3 weeks ago
-
Rodents! A word of warning for heat pump owners
1 month ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
2 months ago
-
Running my new Nibe ASHP efficiently
2 months ago
-
Weather compensation- why you should use it
2 months ago
Currently viewing this topic 1 guest.
- 27 Forums
- 2,539 Topics
- 59.1 K Posts
- 303 Online
- 6,818 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Balancing is a long process and its possible to mess th...
By JamesPa , 2 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 3 hours ago
-
Thanks everyone for the help, Havenwise now diasbled. q...
By Boycey , 5 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli Depending on whether you can get an EV tariff, I...
By ChandyKris , 6 hours ago
-
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 7 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 7 hours ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 8 hours ago
-
@Mars at the time of writing heating oil is £1.28 / ltr...
By TechnoGeek , 9 hours ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 11 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 11 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
The setup for this is a Samsung Modbus card. Connected ...
By antonical , 13 hours ago
-
RE: Forum updates, announcements & issues
@davidalgarve, if the emails are more than roughly a mo...
By Mars , 14 hours ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 14 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 15 hours ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
The answer was in two parts in my reply, the second par...
By RobS , 1 day ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 1 day ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
Loss assessments can be a very serious case of GIGO. I...
By JamesPa , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Just bizarre. This is our data. I really don't...
By antonical , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW review
I think you said its an 11.2kW model and your house is ...
By JamesPa , 2 days ago