Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
9kW Grant Aerona
Hi Mike,
Thanks for the reply. There is no problem with the delay in replying, I realise that people are busy, it is when they don't have the common courtesy to reply that I find annoying.
I am pleased to hear that you are becoming more confident when making adjustments to the controller, it can be quite traumatic the first time. I still remember the first time I made adjustments to the control systems for a 500MW generating unit, when it was in full operation.
A further problem is that most end users, and it would appear many of the installers, don't fully understand the terminology, and what adjustments may be necessary, and how to make them.
It may be useful if I explain the data that you collected.
00 Circulating water return temperature - as the name suggests, this is the temperature of the water coming back from the heat emitters. So the water coming back to the heat pump is at a temperature of 32C.
01 Compressor operating frequency - this is a measure of how fast the compressor is running. As I am no doubt your are aware, the mains frequency is 50Hz, so the compressor is running at just over 1.5 times the speed at which it would be operating, if it were fed from a mains supply directly. It may be useful to record the frequency when the compressor is running at full speed, so you can gauge how hard the compressor is working.
02 Discharge temperature - I do believe that this is the temperature of the refrigerant gas coming out of the compressor on its way to the condenser.
03 Power consumption - this is self explanatory.
04 Fan control number of rotation - this is the speed of the fan in rpm, which, like the compressor, can also be varied.
05 Defrost temperature - I presume there is a sensor within the ASHP that decides when the unit needs to operate the defrost cycle.
06 Outdoor air temperature - this is self explanatory.
07 Water pump control number of rotation - this is the speed of the pump in rpm, which, like the compressor, can also be varied.
08 Suction temperature - this is the temperature of the refrigerant gas coming out of the evaporator on its way to the inlet of the compressor.
09 Circulating water flow temperature - as the name suggests, this is the temperature of the water going out to the heat emitters. So the water coming out from the heat pump is at a temperature of 39C.
Looking at the above data, at an ambient air temperature of 4C, a water flow temperature of 39C seems a little on the high side, but of more concern is the fact that a 9kW ASHP is drawing 2.8kW of electrical energy, which would indicate that the unit is working near its maximum output or that the COP is quite low.
What is the total floor area of your home? Do you have any heat loss calculations or what is the level of insulation? What are the type and size of all the heat emitters?
I would suggest that you try raising the setting of one of the thermostats by 1C again, and seeing if the temperature in that room still increases. This would indicate that the weather compensation requires further adjustment to lower the water flow temperature.
It would also be useful to record further sets of data at different ambient air temperatures, to quantify how the system is responding.
I will leave you to carryout the above as time permits, and will be here to assist, as necessary, in the future.
Â
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 1,597 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
I am amazed that there is not something out there to me...
By JamesPa , 3 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 9 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 14 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 2 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 4 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 5 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago