17kw Grant Aerona heat pump not performing
It really sucks Sonix, you've tried to do the right thing and been badly let down. I would be surprised if the plate heat exchanger is badly blocked, to the point the primary flow is seriously restricted. It would have to take a hell of a lot of quite large particulate contamination to do that, or some massive scale build up due to some water quality issue. Grant ASHPs don't have particulate strainers on the inlet return water connection. The magnetic sludge that builds up on ferrite magnet cores is very fine - too fine for particulate strainers, which is why magnets are used. Reverse flushing using various chemical agents should clear it. The brazed plates are stainless steel, but check compatibility of rubber hoses, plastic pump housings and impellers, etc., before chucking aggressive flushing and cleaning chemicals inside it.
My hunch is an issue with the primary circulating pump. It's relatively easy to remove for inspection change out, and a competent plumber could do that. A primary pump replacement is not new monobloc territory cost. You wouldn't change out a combi for a failed circulating pump, so surely it's not unreasonable to expect Grant to hold circulating pumps as a spare part? Even if they don't the pump will be a generic product and you may be able to source a replacement yourself. Grant are stockists of badged up Chofu units, probably with little spare parts holding in the UK. Dare say they'll probably advise changing the whole monobloc for relatively minor component failures which could and should be repairable.
The grant pump isn’t pwm controlled so you could literally fit the cheapest one from toolstation and it would work without error codes.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Grant have now agreed to replace the circulating pump to see if that's that root cause of the issue this week as it's been power flushed twice with fx2 and another stronger chemical already and the water didn't look that dirty according to the heat engineer. He was expecting it to be black and it wasn't that bad he said. The power flush is using a Kamco flush which has a flow of 200lpm. So fingers fingers crossed it's the pump at fault.
@hughf sorry what does pwm controlled mean? The Grant pump is a pretty powerful pump with 12m head I'm told and as it's the only pump we have now it would need to be at least as powerful.
- 26 Forums
- 2,102 Topics
- 46.2 K Posts
- 68 Online
- 3,388 Members
Join Us!
Latest Posts
-
Location of hot water isolation valve on cylinder
I have recently moved to a property with a heat pump an...
By rossowheels , 3 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
From what you say about the radiators upstairs it does ...
By JamesPa , 5 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer pleased you found it!
By JamesPa , 6 hours ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 8 hours ago
-
@heacol, if you're around, can you please provide some ...
By Mars , 11 hours ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 11 hours ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 1 day ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 1 day ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 1 day ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 2 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 2 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 2 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 2 days ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 4 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 4 days ago