Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
17kw Grant Aerona heat pump not performing
It really sucks Sonix, you've tried to do the right thing and been badly let down. I would be surprised if the plate heat exchanger is badly blocked, to the point the primary flow is seriously restricted. It would have to take a hell of a lot of quite large particulate contamination to do that, or some massive scale build up due to some water quality issue. Grant ASHPs don't have particulate strainers on the inlet return water connection. The magnetic sludge that builds up on ferrite magnet cores is very fine - too fine for particulate strainers, which is why magnets are used. Reverse flushing using various chemical agents should clear it. The brazed plates are stainless steel, but check compatibility of rubber hoses, plastic pump housings and impellers, etc., before chucking aggressive flushing and cleaning chemicals inside it.
My hunch is an issue with the primary circulating pump. It's relatively easy to remove for inspection change out, and a competent plumber could do that. A primary pump replacement is not new monobloc territory cost. You wouldn't change out a combi for a failed circulating pump, so surely it's not unreasonable to expect Grant to hold circulating pumps as a spare part? Even if they don't the pump will be a generic product and you may be able to source a replacement yourself. Grant are stockists of badged up Chofu units, probably with little spare parts holding in the UK. Dare say they'll probably advise changing the whole monobloc for relatively minor component failures which could and should be repairable.
The grant pump isn’t pwm controlled so you could literally fit the cheapest one from toolstation and it would work without error codes.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Grant have now agreed to replace the circulating pump to see if that's that root cause of the issue this week as it's been power flushed twice with fx2 and another stronger chemical already and the water didn't look that dirty according to the heat engineer. He was expecting it to be black and it wasn't that bad he said. The power flush is using a Kamco flush which has a flow of 200lpm. So fingers fingers crossed it's the pump at fault.
@hughf sorry what does pwm controlled mean? The Grant pump is a pretty powerful pump with 12m head I'm told and as it's the only pump we have now it would need to be at least as powerful.
- 27 Forums
- 2,753 Topics
- 64.7 K Posts
- 1,288 Online
- 7,158 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Glass lined Cylinder for private water supply
This has turned into a fascinating little rabbit hole. ...
By Mars , 6 hours ago
-
RE: Adventures in heat loss calculations
yes and no. apparently HG’s AI was automatically assumi...
By Batpred , 6 hours ago
-
RE: Switch suitable to change between two inverter CT's
Last winter my battery ,32KWh, could run the house com...
By Jancold , 7 hours ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@rob-of-york Thank you for that, whilst familiar with t...
By kilgorexv , 7 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Agree with Major. And even if I was very happy with ...
By Batpred , 8 hours ago
-
RE: Is the "divide by 2900" rule still valid?
There is another estimator that you could use, a formul...
By Rob of York , 11 hours ago
-
RE: To re-pipe or not to re-pipe? Moving from oil boiler to air source heat pump.
@penval, really useful update. After all the discussion...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu I prefer to look at it simplistically. We d...
By Old_Scientist , 3 days ago
-
RE: Questions about A2A for heating as well as cooling
@rob-of-york I would concur with the underfloor insulat...
By Toodles , 4 days ago
-
RE: New Vaillant Arotherm controls link to existing thermostats ; wired vs wireless
Nothing attached! I have rads but UFH makes the case ...
By JamesPa , 4 days ago
-
RE: Cooling with air to water heat pumps
Passive cooling should always be the first call. Keep ...
By JamesPa , 4 days ago
-
RE: Do I add Air Con or MVHR to existing A2W ASHP?
@rob-of-york Thank you, I’m thinking along these same l...
By Toodles , 5 days ago
-
@Mars Good questions! The downstairs unit did the maj...
By Rob of York , 5 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@dave, I think @jamespa has probably identified the mos...
By Mars , 5 days ago