(@craig1980)
Reputable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

Here you go

20221201 114543
20221201 114549
20221201 114631

 

 

 


   
ReplyQuote
(@craig1980)
Reputable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

Measurements in brackets are on 35 flow temp setting. 

 

20221201 115159

   
ReplyQuote
(@craig1980)
Reputable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

Room temp is slowly climbing. Up to 19 now.


 


   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 4 years ago
Posts: 4427
 

@craig1980

Thanks Craig, now lower the LWT setting to 30C and see what happens to how the system operates.


   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 4 years ago
Posts: 4427
 

Posted by: @craig1980

Room temp is slowly climbing. Up to 19 now.


 

That is to be expected during the testing. What changes have you made to the Field Setting Values?

 


   
ReplyQuote
(@craig1980)
Reputable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

@derek-m none. I've just followed what it said in the video link that I sent then set to 35 now set to 30 and timing shut downs as it has turned on and off.


   
ReplyQuote



(@craig1980)
Reputable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

Right, finished timing. Now back to 8 mins on 20 seconds off again.

Flow temp 28.1 set to 30

Indoor 22.1 

Outdoor 6.5

Room temp 19


   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 4 years ago
Posts: 4427
 

Posted by: @craig1980

Right, finished timing. Now back to 8 mins on 20 seconds off again.

Flow temp 28.1 set to 30

Indoor 22.1 

Outdoor 6.5

Room temp 19

Hi Craig,

I'm afraid that I have run out of suggestions.

There appears to be something fundamentally wrong with your heat pump, and/or how the system has been installed. The only thing that I can see that appears to be incorrect is the Teva_out temperature reading of -50C, which could possibly be due to a faulty or disconnected temperature sensor.

I would suggest that you e-mail Samsung Technical Help and ask them why your system may be operating as it is doing.

In the meantime set your system back onto WC mode and adjust for the required indoor temperature.

 


   
ReplyQuote
(@craig1980)
Reputable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

Okay, many thanks for all of your help. I'll update if I find anything from Samsung. Thanks again. Much appreciated. 


   
ReplyQuote
(@craig1980)
Reputable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

Interestingly, when I put the settings back to WC I get error E121. Upon looking this up in the manual it says 

"Short-or open- circuit error of the room temperature sensor of the zone 1 indoor unit (detected only when the room thermostat is used) Error source - Hydro unit. 


   
ReplyQuote
(@mike-h)
Reputable Member Member
Joined: 4 years ago
Posts: 197
 

Posted by: @hughf

Posted by: @mike-h

Am I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.

 

It doesn't have a buffer, no...

Which set of instructions say that the samsung needs a buffer?

 

@hughf  Please see the topic about Samsung install and buffer tank

https://renewableheatinghub.co.uk/forums/postid/11342

Freedom Heat Pumps claims a buffer tank is required to be within the Samsung warranty, even though the manual implies otherwise and Joule make a pre-plumbed cylinder without a buffer tank.

 


   
ReplyQuote
(@hughf)
Noble Member Member
Joined: 3 years ago
Posts: 489
 

@mike-h Ah yes, good old freedom. I’d trust the instructions from midsummer wholesale personally. I know that GH was always getting 911 errors (low flow) on his early installs, so they probably mandated a buffer to deal with that issue, allowing the primary pump to run at full speed to charge the buffer.

Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote